d prudent.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
*From:* Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of
*John Paulsen
*Sent:* Tuesday, July 18, 2017 11:14 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* RE: Calculation require
) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of John Paulsen
Sent: Tuesday, July 18, 2017 11:14 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Calculation requirement when adding sprinklers
No, these heads are being added close to
s Mack; MFP Design, LLC
Sent: Tuesday, July 18, 2017 9:20 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Calculation requirement when adding sprinklers
Well then, I would say it depends. It doesn’t matter if it is not the “remote”
area. Did the alteration create a more demanding area.
.
Crown FSD
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Travis Mack; MFP Design, LLC
Sent: Tuesday, July 18, 2017 12:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Calculation requirement when adding sprinklers
Well then, I would say
ESS**
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of John Paulsen
Sent: Tuesday, July 18, 2017 9:17 AM
To: tm...@mfpdesign.com; sprinklerforum@lists.firesprinkler.org
Subject: RE: Calculation requirement when adding sprinklers
I agree and normally I would do a check
; MFP Design, LLC
Sent: Tuesday, July 18, 2017 12:14 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Calculation requirement when adding sprinklers
I concur with Jeff. With the ease of doing calcs in today’s software, it is
not uncommon for me to run several just to justify to
rg] On
Behalf Of Jeff Normand
Sent: Tuesday, July 18, 2017 9:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Calculation requirement when adding sprinklers
I would want to do a proof calc to satisfy myself and then if someone ask for
it you already have it.
I usually do many pr
Subject: Calculation requirement when adding sprinklers
Hello all!
I feel like I should know the answer to this and at one time I probably did,
but I was just asked if there was a requirement to provide hydraulic
calculations if adding over a certain number of sprinklers to a system. My
off the
I would want to do a proof calc to satisfy myself and then if someone ask
for it you already have it.
I usually do many proof calcs but only submit some of them.
Jeff
On Tue, Jul 18, 2017 at 11:04 AM, John Paulsen wrote:
> Hello all!
>
>
>
> I feel like I should know the answer to this and at
Does adding the new sprinklers create a new remote area?
It depends on how and where the sprinklers were added. If they are being added
to closets and the remote area is over the 1500 sqft (LH, OH) where they would
not impact the hydraulics (can be omitted), then no. If they are ta
Hello all!
I feel like I should know the answer to this and at one time I probably did,
but I was just asked if there was a requirement to provide hydraulic
calculations if adding over a certain number of sprinklers to a system. My
off the cuff answer was no, that unless you were adding sprinkl
11 matches