;This loft is OH2.5", etc.
:)
Brad
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of bcasterl...@fsc-inc.com
Sent: Friday, March 16, 2018 8:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: [EXTERNAL] RE: Existing 3/4&q
resprinkler.org] On Behalf Of
cw bamford
Sent: Friday, March 16, 2018 4:39 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: [EXTERNAL] RE: Existing 3/4" outlets
"the right Sprinkler Head for the right job"
in a Hallway of a hotel or apartment building most AHJ's will acc
nklerforum-boun...@lists.firesprinkler.org] On
Behalf Of cw bamford
Sent: Friday, March 16, 2018 4:39 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: [EXTERNAL] RE: Existing 3/4" outlets
"the right Sprinkler Head for the right job"
in a Hallway of a hotel or apar
ncies, but that residential heads
> may only be used in residential occupancies?
>
> -Kyle M
>
> -Original Message-
> From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] On Behalf Of bcasterl...@fsc-inc.com
> Sent: Friday, March 16, 2018 11
y be used in residential occupancies?
-Kyle M
-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
bcasterl...@fsc-inc.com
Sent: Friday, March 16, 2018 11:17 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: [EXTER
:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of bcasterl...@fsc-inc.com
Sent: Friday, March 16, 2018 11:17 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: [EXTERNAL] RE: Existing 3/4" outlets
Kyle, if there is even a whiff of Residential about the occupancy the listed
res should be used beca
: sprinklerforum@lists.firesprinkler.org
Cc: Dewayne Martinez <dmarti...@total-mechanical.com>
Subject: [EXTERNAL] RE: Existing 3/4" outlets
That’s a thought.The problem is the original shell with 3/4"
uprights with a pipe centerline of 12" below deck. No residential
uprights in 3
AL] RE: Existing 3/4" outlets
That’s a thought.The problem is the original shell with 3/4" uprights with
a pipe centerline of 12" below deck. No residential uprights in 3/4"
and I thought residential pendant heads are not listed to be installed exposed?
Dewayne Martinez
Fire
Dewayne Martinez <dmarti...@total-mechanical.com>
Date: 03/16/2018 12:47 PM
Subject: RE: Existing 3/4" outlets
Sent by:"Sprinklerforum"
<sprinklerforum-boun...@lists.firesprinkler.org>
BE ADVISED - This email originated outside EMCOR.
That’s
B Morey
Sent: Friday, March 16, 2018 9:57 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Existing 3/4" outlets
You say bushing, I say sprinkler head extension less than 2" per 6.4.8?
Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh
25 / fax 260.487.7991
email mmo...@shambaugh.com
From: Dewayne Martinez <dmarti...@total-mechanical.com>
To: sprinklerforum@lists.firesprinkler.org
Cc: Dewayne Martinez <dmarti...@total-mechanical.com>
Date: 03/15/2018 06:43 PM
Subject: Existing 3/4" outlets
Sent
nkler.org
Cc: Dewayne Martinez <dmarti...@total-mechanical.com>
Subject: Existing 3/4" outlets
I have a project that was originally designed as a OH II space that
will now be turned into a light hazard residential exposed “loft”
space. The existing ¾” K8.0 sprinklers over discharge li
ewayne Martinez
Sent: Thursday, March 15, 2018 5:42 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dewayne Martinez <dmarti...@total-mechanical.com>
Subject: Existing 3/4" outlets
I have a project that was originally designed as a OH II space that will now be
turned into a light h
-inc.com
Sent: Thursday, March 15, 2018 5:43 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Existing 3/4" outlets
Does anyone make res heads with 3/4 npt?
If so just replace the heads and let it overflow!
The Standards only spell out minimums.
Brad.
Quoting Dewayne Martinez &l
Does anyone make res heads with 3/4 npt?
If so just replace the heads and let it overflow!
The Standards only spell out minimums.
Brad.
Quoting Dewayne Martinez :
I have a project that was originally designed as a OH II space that will
now be turned into a
I have a project that was originally designed as a OH II space that will
now be turned into a light hazard residential exposed “loft” space. The
existing ¾” K8.0 sprinklers over discharge like crazy. Can I bush the
3/4'” outlets down to ½” to use K5.6 sprinklers? If not any suggestions?