Agreed, and I can’t really argue with that logic. But if you read
the handbook, the commentary states:
“…The residual pressure criterion of
inklerforum-boun...@lists.firesprinkler.org] On
Behalf Of MFP Design, LLC
Sent: Tuesday, October 24, 2017 2:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Underground Main
Kyle:
Here is the definition per IFC
FIRE-FLOW. The flow rate of a water supply, measured at 20 p
:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of MFP Design, LLC
Sent: Tuesday, October 24, 2017 2:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Underground Main
Kyle:
Here is the definition per IFC
FIRE-FLOW. The flow rate of a water supply, measured at 20 pounds per squ
the "fire fighting" aspect in the definition above
would start.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Kyle.Montgomery
Sent: Tuesday, October 24, 2017 2:19 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Underg
Sent: Tuesday, October 24, 2017 2:19 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Underground Main
Travis,
Good point about doing the work for free. Lately I've been lamenting the
fact that we end up doing a lot of this type of free work in the bid phase,
only
Travis,
Good point about doing the work for free. Lately I've been lamenting the fact
that we end up doing a lot of this type of free work in the bid phase, only to
end up losing the project to a low-ball bidder. I guess that's a risk you have
to take sometimes, but if you've already got a