RE: Horizontal Combustible Concealed Space

2021-01-28 Thread Greg McGahan via Sprinklerforum
Gamble Subject: RE: Horizontal Combustible Concealed Space So, if an attic is constructed with a pitch of less than or equal to 2:12 and the depth of that space is less than or equal to 36" from deck to ceiling, then it becomes a horizontal cc space and MUST be protected with list

RE: Horizontal Combustible Concealed Space

2021-01-28 Thread JD Gamble via Sprinklerforum
ry 28, 2021 7:55 AM To: sprinklerforum@lists.firesprinkler.org Cc: Steve Leyton ; Cary Webber Subject: RE: Horizontal Combustible Concealed Space Or to put it another way, if an attic is constructed so that its configuration meets the conditions of 9.3.2, it MUST be protected with listed CC sprin

RE: Horizontal Combustible Concealed Space

2021-01-28 Thread Steve Leyton via Sprinklerforum
: Cary Webber via Sprinklerforum Date: 1/28/21 6:41 AM (GMT-08:00) To: sprinklerforum@lists.firesprinkler.org Cc: Cary Webber Subject: RE: Horizontal Combustible Concealed Space I think it's fair to say that an attic (agreeing with Taylor S) is at the top, however, an "attic" can be c

RE: Horizontal Combustible Concealed Space

2021-01-28 Thread Cary Webber via Sprinklerforum
SCĀ  29657 Tel: 864-843-5161 -Original Message- From: Sprinklerforum On Behalf Of JD Gamble via Sprinklerforum Sent: Thursday, January 28, 2021 9:37 AM To: sprinklerforum@lists.firesprinkler.org Cc: JD Gamble Subject: RE: Horizontal Combustible Concealed Space CAUTION: This email origi

RE: Horizontal Combustible Concealed Space

2021-01-28 Thread JD Gamble via Sprinklerforum
28, 2021 7:34 AM To: sprinklerforum@lists.firesprinkler.org Cc: Cary Webber Subject: RE: Horizontal Combustible Concealed Space CCS style sprinklers are generally listed to a maximum 2:12 pitch so IMO this is the best indicator of the difference between an attic space and a combustible ceiling sp

RE: Horizontal Combustible Concealed Space

2021-01-28 Thread Taylor Schumacher via Sprinklerforum
Sent: Thursday, January 28, 2021 8:34 AM To: sprinklerforum@lists.firesprinkler.org Cc: Cary Webber Subject: RE: Horizontal Combustible Concealed Space CCS style sprinklers are generally listed to a maximum 2:12 pitch so IMO this is the best indicator of the difference between an attic space

RE: Horizontal Combustible Concealed Space

2021-01-28 Thread Cary Webber via Sprinklerforum
CCS style sprinklers are generally listed to a maximum 2:12 pitch so IMO this is the best indicator of the difference between an attic space and a combustible ceiling space requiring special sprinklers; and yes, by requiring special sprinklers in the horizontal CCS 9.3.2 by default prohibits