2017-03-05 Thread very Cool
pressure [cid:95457595-a5eb-4fc6-92f2-ac17fbb95287] From: Sprinklerforum on behalf of Matthew J Willis Sent: Saturday, March 4, 2017 5:14 PM To: Forum Subject: Re: Size of main service - dry parking garage - 290 is at the system. How long is the main? How

Re: Size of main service - dry parking garage -

2017-03-04 Thread Matthew J Willis
290 is at the system. How long is the main? How many offsets, etc. There is normally a 25℅ increase or even more, due to build back. If there are no inside hoses, then the house demand is on the underground. It will not be flowing thru the 4". Matt Sent from my Verizon 4G LTE Droid On Mar 4, 201

Re: Size of main service - dry parking garage -

2017-03-04 Thread very Cool
The dry system required flow based on the calc is approximately 290 GPM and required pressure is 90 PSI. But I am not sure how to add the hose allowance to find its impact on required pressure. P.S. The building does not have a required for a standpipe and none will be used. Thanks for helping

Re: Size of main service - dry parking garage -

2017-03-04 Thread Matthew J Willis
And what were the results? You have solved for velocity. That is kind of a lesser concern than available water, and amount required for system. The only way to answer your question is to perform a full hydraulic analysis using Elite. R/Matt Sent from my Verizon 4G LTE Droid On Mar 4, 2017 2:35

Re: Size of main service - dry parking garage -

2017-03-04 Thread very Cool
Elite On Mar 4, 2017, at 4:32 PM, Matthew J Willis mailto:ma...@rapidfireinc.com>> wrote: I'll ask this question, what hydraulic calculation software are you using? Matt Sent from my Verizon 4G LTE Droid On Mar 4, 2017 2:28 PM, very Cool mailto:egengin...@hotmail.com>> wrote: Thanks for your

Re: Size of main service - dry parking garage -

2017-03-04 Thread Matthew J Willis
I'll ask this question, what hydraulic calculation software are you using? Matt Sent from my Verizon 4G LTE Droid On Mar 4, 2017 2:28 PM, very Cool wrote: Thanks for your response Art. The hydrant test shows 130 psi at 500 GPM The parking is on ground level and the pipes wound the 10' above the

Re: Size of main service - dry parking garage -

2017-03-04 Thread very Cool
Thanks for your response Art. The hydrant test shows 130 psi at 500 GPM The parking is on ground level and the pipes wound the 10' above the ground floor The new main will only serve the sprinkler with hose allowance. It does not need to serve fire hydrant. Thanks again On Mar 4, 2017, at 3:

RE: Size of main service - dry parking garage -

2017-03-04 Thread Art Tiroly
>From the information presented the question can’t be answered. To do a hydraulic analysis you need: A water flow test near the point of the connection. Length of the underground fire main from the connection to the riser. Elevation of the dry system highest sprinkler. Is there a fire hydrant s