RE: Indoor Storage Tanks of Combustible Liquids

2022-02-23 Thread Ken Haney via Sprinklerforum
I would look in NFPA 30. Ken Haney Certified Engineering Tech Haney Fire Protection, Inc. 610.217.0347 hane...@rcn.com From: James Crawford via Sprinklerforum Sent: Wednesday, February 23, 2022 1:18 PM To: Sprinklerforum@lists.firesprinkler.org Cc: James Crawford Subject: Indoor Storage Tanks of

RE: Indoor Storage Tanks of Combustible Liquids

2022-02-23 Thread tstone52--- via Sprinklerforum
Message- From: Sprinklerforum On Behalf Of James Crawford via Sprinklerforum Sent: Wednesday, February 23, 2022 1:18 PM To: sprinklerforum@lists.firesprinkler.org Cc: James Crawford Subject: Indoor Storage Tanks of Combustible Liquids I am hoping someone can help me out, I cannot seem to

Indoor Storage Tanks of Combustible Liquids

2022-02-23 Thread James Crawford via Sprinklerforum
I am hoping someone can help me out, I cannot seem to find any protection schemes for the storage of class IIIB combustible liquids in small storage tanks (more than 660 gal but less than 3700 gallons) Could not find anything in NFPA of FM, or did I just miss it, could someone point me in the

RE: IBC 903.3.5.2 Secondary Water Supply From Swimming Pool & Storage Tanks

2016-11-13 Thread Tom Duross
12, 2016 6:09 PM To: Mike Brown ; sprinklerforum@lists.firesprinkler.org Subject: Re: IBC 903.3.5.2 Secondary Water Supply From Swimming Pool & Storage Tanks We have done these where the secondary supply is piped into the suction side of the pump. That keeps it all automatic. Separate

Re: IBC 903.3.5.2 Secondary Water Supply From Swimming Pool & Storage Tanks

2016-11-12 Thread Travis Mack
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of Mike Brown > Sent: Saturday, November 12, 2016 12:28 PM > To: sprinklerforum@lists.firesprinkler.org > Subject: IBC 903.3.5.2 Secondary Water Supply From Swimming Pool & Storage > Tanks > > I am

Re: IBC 903.3.5.2 Secondary Water Supply From Swimming Pool & Storage Tanks

2016-11-12 Thread Mike Brown
Pool & Storage Tanks   I am working on project that falls in the seismic classification requiring a secondary water supply per section 903.3.5.2. The bid documents showed using the swimming pool and two additional storage tanks to meet the required sprinkler demand. The tanks and the swimming

RE: IBC 903.3.5.2 Secondary Water Supply From Swimming Pool & Storage Tanks

2016-11-12 Thread Steve Leyton
Subject: IBC 903.3.5.2 Secondary Water Supply From Swimming Pool & Storage Tanks I am working on project that falls in the seismic classification requiring a secondary water supply per section 903.3.5.2. The bid documents showed using the swimming pool and two additional storage tanks to meet

IBC 903.3.5.2 Secondary Water Supply From Swimming Pool & Storage Tanks

2016-11-12 Thread Mike Brown
I am working on project that falls in the seismic classification requiring a secondary water supply per section 903.3.5.2. The bid documents showed using the swimming pool and two additional storage tanks to meet the required sprinkler demand. The tanks and the swimming pool are shown to be

Re: Storage Tanks

2016-07-25 Thread Roland Huggins
start with Examples of commodity classifications: plastic containers larger than 5 Gal. The classification is triggered by the wall thickness if greater 1/4 inch, it’s Group A plastic. It does get a bit tricky when you have 6000 gal flowing out once breached (after all a breached water tank ex

RE: Storage Tanks

2016-07-25 Thread James Crawford
...@phaserfire.ca From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matt Grise Sent: Monday, July 25, 2016 10:44 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Storage Tanks What is the nature of the facility? Is it likely that they would never

RE: Storage Tanks

2016-07-25 Thread Matt Grise
7 ph 913.888.0618 f 913.526.7443 cell www. AFPsprink.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of James Crawford Sent: Monday, July 25, 2016 12:41 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Storage Tanks This is always my concern,

RE: Storage Tanks

2016-07-25 Thread James Crawford
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Monday, July 25, 2016 10:36 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Storage Tanks How about when that tank is empty? Now a giant plastic tank in the room

Re: Storage Tanks

2016-07-25 Thread Todd Williams
Is it always filled or would it occasionally be empty? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2] On Mon, Jul 25, 2016 at 1:33 PM, James Crawford wr

RE: Storage Tanks

2016-07-25 Thread Craig.Prahl
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of James Crawford Sent: Monday, July 25, 2016 1:34 PM To: sprinklerforum@lists.firesprinkler.org Subject: Storage Tanks [EXTERNAL] I must be missing it, so I am hoping someone can point me in the right direction 16' high 6000 gal plastic tank f

Storage Tanks

2016-07-25 Thread James Crawford
I must be missing it, so I am hoping someone can point me in the right direction 16' high 6000 gal plastic tank filled with non-combustible liquids, what do you use for sprinkler protection? Is it class 1 commodity on the floor to 16'? Thank you James Crawford Phaser Fire Pro

RE: Storage Tanks

2015-11-23 Thread Craig.Prahl
s are sitting there empty. NFPA doesn't really address plastic storage tanks storing non-flammable liquids but there is some text in the FM Global Data sheets dealing with storage commodities. Craig L. Prahl Fire Protection Group Lead/SME CH2MHILL Lockwood Greene 1500 International Drive Spart

Re: Storage Tanks

2015-11-20 Thread Todd Williams
lerforum@lists.firesprinkler.org Subject: Re: Storage Tanks Roland, if you have ever seen me on regular coffee, you would understand decaf. If it is s pvc tank, is it full 24/7 or is it empty at some point? Different hazards. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-

RE: Storage Tanks

2015-11-20 Thread Steve Leyton
From: Todd Williams Date: 11/20/2015 3:56 PM (GMT-08:00) To: sprinklerforum@lists.firesprinkler.org Subject: Re: Storage Tanks Roland, if you have ever seen me on regular coffee, you would understand decaf. If it is s pvc tank, is it full 24/7 or is it empty at some point? Different hazards

RE: Storage Tanks

2015-11-20 Thread James Crawford
r 20, 2015 3:52 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Storage Tanks First off I have to say it’s just wrong to decaffeinate coffee What exactly do you mean protect? A tank full of water (even with beans) poses what kind of risk? Confused Roland Huggins, PE - VP E

Re: Storage Tanks

2015-11-20 Thread Todd Williams
Roland, if you have ever seen me on regular coffee, you would understand decaf. If it is s pvc tank, is it full 24/7 or is it empty at some point? Different hazards. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic

Re: Storage Tanks

2015-11-20 Thread Roland Huggins
First off I have to say it’s just wrong to decaffeinate coffee What exactly do you mean protect? A tank full of water (even with beans) poses what kind of risk? Confused Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX ht

Re: Storage Tanks

2015-11-20 Thread Todd Williams
What is the tank made of? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2] On Fri, Nov 20, 2015 at 6:44 PM, sprinklerforum@lists.firesprinkler.org wrote

Storage Tanks

2015-11-20 Thread James Crawford
Looking for input as I have not come across this before. Looking for a protection scheme to protect a 65' tall storage tank filled with water and coffee beans (decaffeinating) Just not sure what code would cover this. Thank you James Crawford Phaser Fire Protection Ltd. Pho

RE: fabric storage tanks

2014-05-07 Thread Rod DiBona
, May 07, 2014 8:23 AM To: sprinklerforum@lists.firesprinkler.org Subject: fabric storage tanks I have a client that needs to replace a 50 gallon fabric storage tank. Does anyone know a company that makes large tanks. We may not need this large as I will probably have to evaluate the systems

fabric storage tanks

2014-05-07 Thread Todd - Work
I have a client that needs to replace a 50 gallon fabric storage tank. Does anyone know a company that makes large tanks. We may not need this large as I will probably have to evaluate the systems based on current use. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.

RE: Pump supplying water storage tanks

2011-10-07 Thread Byron Weisz - Cen-Cal Fire Systems
. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Justin Reid Sent: Friday, October 07, 2011 6:56 AM To: sprinklerforum@firesprinkler.org Subject: Re: Pump supplying water storage tanks As long as the tank is holding

Re: Pump supplying water storage tanks

2011-10-07 Thread Justin Reid
As long as the tank is holding all of the demand water that is needed then it should not be required to be a fire pump. Justin Reid On Thu, Oct 6, 2011 at 6:45 PM, Sharon Alves wrote: > Does a pump that supplies water from a well to water storage tanks need to > be a fire pump? > &g

RE: Pump supplying water storage tanks

2011-10-07 Thread Craig.Prahl
, 2011, 6:45:29 PM, you wrote: > Does a pump that supplies water from a well to water storage tanks need to > be a fire pump? > > Thank you, > > SHARON ALVES > Senior Fire Sprinkler Designer > > LP Consulting Engineers, Inc. > Mechanical - Electric

RE: Pump supplying water storage tanks

2011-10-06 Thread Sharon Alves
supplying water storage tanks What is the application 13 13d 13r? Sent on the SprintR Now Network from my BlackBerryR -Original Message- From: "Sharon Alves" Sender: sprinklerforum-boun...@firesprinkler.org Date: Thu, 6 Oct 2011 15:45:29 To: Reply-To: sprinklerforum@firesprinkler.o

RE: Pump supplying water storage tanks

2011-10-06 Thread Sharon Alves
, October 06, 2011 4:18 PM To: Sharon Alves Subject: Re: Pump supplying water storage tanks Hello Sharon, I have done 2 systems with the tank refilled from a well and the well driller just put in a standard well pump and controller. It was not considered part of the Fire Sprinkler System until it got to

Re: Pump supplying water storage tanks

2011-10-06 Thread cabralmike
ying water storage tanks Does a pump that supplies water from a well to water storage tanks need to be a fire pump? Thank you, SHARON ALVES Senior Fire Sprinkler Designer LP Consulting Engineers, Inc. Mechanical - Electrical - Plumbing Engineers - Fire Protection 1663 Eureka Road

Re: Pump supplying water storage tanks

2011-10-06 Thread Charles Thurston
hat supplies water from a well to water storage tanks need to > be a fire pump? > > Thank you, > > SHARON ALVES > Senior Fire Sprinkler Designer > > LP Consulting Engineers, Inc. > Mechanical - Electrical - Plumbing Engineers - Fire Protection > 1663 E

Pump supplying water storage tanks

2011-10-06 Thread Sharon Alves
Does a pump that supplies water from a well to water storage tanks need to be a fire pump? Thank you, SHARON ALVES Senior Fire Sprinkler Designer LP Consulting Engineers, Inc. Mechanical - Electrical - Plumbing Engineers - Fire Protection 1663 Eureka Road Roseville, CA 95661 P

RE: Type of pump for UG storage tanks

2010-10-11 Thread Thom
] On Behalf Of Brad Sent: Monday, October 11, 2010 11:33 AM To: sprinklerforum@firesprinkler.org; 'Charles Thurston' Subject: RE: Type of pump for UG storage tanks Thom, if it were vertical turbines we were talking about, we would not be talking, and nobody would feel hurt, unqualified,

RE: Type of pump for UG storage tanks

2010-10-11 Thread Steve Leyton
L. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Monday, October 11, 2010 11:10 AM To: sprinklerforum@firesprinkler.org Subject: RE: Type of pump for UG storage tanks Yes, it will take

RE: Type of pump for UG storage tanks

2010-10-11 Thread George Church
forum-boun...@firesprinkler.org] On Behalf Of Ralphy Henderson Sent: Friday, October 08, 2010 1:14 PM To: sprinklerforum@firesprinkler.org Subject: Type of pump for UG storage tanks Hello, I have a GC that installed a poly-tank underground in anticipation of a future sprinkler system and pump. The

RE: Type of pump for UG storage tanks

2010-10-11 Thread Brad
--Original Message- From: Thom [mailto:tmcma...@firetechinc.com] Sent: Monday, October 11, 2010 11:17 AM To: sprinklerforum@firesprinkler.org; 'Charles Thurston' Subject: RE: Type of pump for UG storage tanks Seems to me that NFPA 20 does say not to do this! NFPA 20, 2007, 7.3.5.2.2 T

RE: Type of pump for UG storage tanks

2010-10-11 Thread George Church
010 12:17 PM To: sprinklerforum@firesprinkler.org; 'Charles Thurston' Subject: RE: Type of pump for UG storage tanks Seems to me that NFPA 20 does say not to do this! NFPA 20, 2007, 7.3.5.2.2 This valve shall also admit air to the column to dissipate the vacuum upon stopping of the pump. Your s

RE: Type of pump for UG storage tanks

2010-10-11 Thread Thom
-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Charles Thurston Sent: Monday, October 11, 2010 8:37 AM To: George Church Subject: Re: Type of pump for UG storage tanks Hello George, I was just commenting on 2 of the systems I have seen out here. Seems to m

Re: Type of pump for UG storage tanks

2010-10-11 Thread Charles Thurston
onday, October 11, 2010 8:26 AM > To: sprinklerforum@firesprinkler.org; 'Coastal' > Subject: RE: Type of pump for UG storage tanks > Thanks, this is great! Why not post it to the Forum? I think it would help > Ralph B- the original poster. If you do not want to, can I? > -

Re: Type of pump for UG storage tanks

2010-10-11 Thread Ron Greenman
Original Message- > From: sprinklerforum-boun...@firesprinkler.org > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad > Sent: Monday, October 11, 2010 8:26 AM > To: sprinklerforum@firesprinkler.org; 'Coastal' > Subject: RE: Type of pump for UG storage

RE: Type of pump for UG storage tanks

2010-10-11 Thread George Church
;Coastal' Subject: RE: Type of pump for UG storage tanks Thanks, this is great! Why not post it to the Forum? I think it would help Ralph B- the original poster. If you do not want to, can I? -Original Message- From: Coastal [mailto:coastalf...@sc.rr.com] Sent: Sunday, October 10, 2010

RE: Type of pump for UG storage tanks

2010-10-11 Thread Brad
rom: George Church [mailto:for...@ptd.net] > Sent: Friday, October 08, 2010 3:03 PM > To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com > Subject: RE: Type of pump for UG storage tanks > ??? > Unless the tank ws installed upside down, you'd don't have positive

Re: Type of pump for UG storage tanks

2010-10-10 Thread Coastal
essage- > From: George Church [mailto:for...@ptd.net] > Sent: Friday, October 08, 2010 3:03 PM > To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com > Subject: RE: Type of pump for UG storage tanks > ??? > Unless the tank ws installed upside down, you'd don't ha

RE: Type of pump for UG storage tanks

2010-10-10 Thread Brad
riday, October 08, 2010 3:03 PM To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com Subject: RE: Type of pump for UG storage tanks ??? Unless the tank ws installed upside down, you'd don't have positive suction head above the waterline. I don't have an equation to support it, but

Re: Type of pump for UG storage tanks

2010-10-08 Thread Ken
ks for the info everyone! -RB --- On Fri, 10/8/10, George Church wrote: From: George Church Subject: RE: Type of pump for UG storage tanks To: sprinklerforum@firesprinkler.org Date: Friday, October 8, 2010, 10:36 PM The reason you don't see a detail for an up over and down suction pipe is becaus

RE: Type of pump for UG storage tanks

2010-10-08 Thread Ralphy Henderson
r the info everyone! -RB --- On Fri, 10/8/10, George Church wrote: From: George Church Subject: RE: Type of pump for UG storage tanks To: sprinklerforum@firesprinkler.org Date: Friday, October 8, 2010, 10:36 PM The reason you don't see a detail for an up over and down suction pipe is beca

RE: Type of pump for UG storage tanks

2010-10-08 Thread Thom
Type of pump for UG storage tanks I've done this on a small remote residential system. The tank was about 8' below the suction flange, so we but a check valve at the tank connection (2- 2500 gal underground rain water storage tanks) put a tee in the suction flange and 4' of riser pi

RE: Type of pump for UG storage tanks

2010-10-08 Thread George Church
sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Mak Sent: Friday, October 08, 2010 6:07 PM To: sprinklerforum Subject: Re: Type of pump for UG storage tanks The only "rules" I've ever seen for a suction lift scenario, (except via vertical turbine pumps) is an LPC tech

Re: Type of pump for UG storage tanks

2010-10-08 Thread Jamie.seidl
I've done this on a small remote residential system. The tank was about 8' below the suction flange, so we but a check valve at the tank connection (2- 2500 gal underground rain water storage tanks) put a tee in the suction flange and 4' of riser pipe and a globe valve to &quo

Re: Type of pump for UG storage tanks

2010-10-08 Thread Ron Greenman
- Original Message - > From: Ron Greenman [rongreen...@gmail.com] > Sent: 08/10/2010 02:47 PM MST > To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com > Subject: Re: Type of pump for UG storage tanks > > > > No syphon thing when you're losing the pri

Re: Type of pump for UG storage tanks

2010-10-08 Thread Chris Mak
Chris Mak Aon Sprinkler Certification Via Blackberry Cell +64-274-344-058 - Original Message - From: Ron Greenman [rongreen...@gmail.com] Sent: 08/10/2010 02:47 PM MST To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com Subject: Re: Type of pump for UG storage tanks No syphon th

Re: Type of pump for UG storage tanks

2010-10-08 Thread Ron Greenman
#x27;; 'bcasterl...@fsc-inc.com' > Subject: RE: Type of pump for UG storage tanks > > I don't think you get to count the 14.7 psi of the atmosphere in your net > positive suction head calculations. When you discharge back into the > atmosphere, you lose that pressure a

RE: Type of pump for UG storage tanks

2010-10-08 Thread Ralphy Henderson
If I understand correctly these things have to be installed directly over the tank right? I see in NFPA #20 they have some sort of water pit thingy. Is that necessary or can you stick this over a poly tank buried in the ground? Thx, ___ Sprin

RE: Type of pump for UG storage tanks

2010-10-08 Thread Brad
- From: Matt Grise [mailto:m...@afpsprink.com] Sent: Friday, October 08, 2010 3:06 PM To: 'sprinklerforum@firesprinkler.org'; 'bcasterl...@fsc-inc.com' Subject: RE: Type of pump for UG storage tanks I don't think you get to count the 14.7 psi of the atmospher

RE: Type of pump for UG storage tanks

2010-10-08 Thread Matt Grise
t: Friday, October 08, 2010 3:03 PM To: 'George Church'; sprinklerforum@firesprinkler.org Subject: RE: Type of pump for UG storage tanks Definitely talk to a pump rep, but say the suction flange is 8' above tank water level. Might be best to rise up out of the tank to about 15' ab

RE: Type of pump for UG storage tanks

2010-10-08 Thread Brad
essure down. 34-8=26 ft*.433= 10 psi POSITIVE. (it works the same way a siphon does) -Original Message- From: George Church [mailto:for...@ptd.net] Sent: Friday, October 08, 2010 3:03 PM To: sprinklerforum@firesprinkler.org; bcasterl...@fsc-inc.com Subject: RE: Type of pump for U

RE: Type of pump for UG storage tanks

2010-10-08 Thread George Church
elly if there is one, or- well, punt. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Sent: Friday, October 08, 2010 1:43 PM To: sprinklerforum@firesprinkler.org Subject: RE: Type of pump for UG storage

RE: Type of pump for UG storage tanks

2010-10-08 Thread Brad
riday, October 08, 2010 12:14 PM To: sprinklerforum@firesprinkler.org Subject: Type of pump for UG storage tanks Hello, I have a GC that installed a poly-tank underground in anticipation of a future sprinkler system and pump. The pump will be installed above ground at a higher elevation than the

Type of pump for UG storage tanks

2010-10-08 Thread Ralphy Henderson
Hello, I have a GC that installed a poly-tank underground in anticipation of a future sprinkler system and pump. The pump will be installed above ground at a higher elevation than the tanks. Will this require a vertical turbine pump to be able to draw from an underground tank? I've never seen t

RE: Refill time for Underground non-pressurized water storage tanks

2010-08-20 Thread George Church
--Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of G. Tim Stone Sent: Friday, August 20, 2010 7:16 AM To: sprinklerforum@firesprinkler.org Subject: RE: Refill time for Underground non-pressurized water storage tanks Geor

RE: Refill time for Underground non-pressurized water storage tanks

2010-08-20 Thread G. Tim Stone
er.org [mailto:sprinklerforum- > boun...@firesprinkler.org] On Behalf Of George Church > Sent: Thursday, August 19, 2010 7:11 PM > To: sprinklerforum@firesprinkler.org > Cc: bch...@nfpa.org > Subject: RE: Refill time for Underground non-pressurized water storage > tanks > > NFPA 22-2008

RE: Refill time for Underground non-pressurized water storage tanks

2010-08-19 Thread George Church
nklerforum@firesprinkler.org Subject: Refill time for Underground non-pressurized water storage tanks Forum, Is there a time requirement for replenishing an underground storage tank? I have look and cannot find it. I did find an 8 hour requirement for pressure tanks. Thank you. Regards, G. Tim Stone

Refill time for Underground non-pressurized water storage tanks

2010-08-19 Thread G. Tim Stone
Forum, Is there a time requirement for replenishing an underground storage tank? I have look and cannot find it. I did find an 8 hour requirement for pressure tanks. Thank you. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protect