Besides a false impression upon building occupants (many of whom don't
notice sprinklers anyway), one must consider false impressions upon first
responders or insurance agents.
On Tue, Apr 12, 2016 at 6:39 AM, Frans Stoop wrote:
> Gentlemen,
>
> Thank you very much.
> I overlooked the phrase NFP
Gentlemen,
Thank you very much.
I overlooked the phrase NFPA 1 and NFPA 101 and the Annexes.
In particular the Annex is very clear.
The IFC does not apply in our country, but I will use the quoted
phrase to emphasize that it is common practice in our profession to
avoid a false impression of s
Eventually, we all run into this construction cart-before-the-horse phasing
situation where you just cannot say no to the client. Once, using the defense
that those observing fire sprinklers who would know what a fire sprinkler looks
like in order to perceive a space as being protected by fire p
on is raised if it is written in the NFPA or FM that
> unconnected sprinklers are not allowed.
> Unfortunately, I can't find it.
> Another suggestion was to put a sign on the door to each room saying
> "Sprinklers not functional".
>
> Met vriendelijke groet/Kind regards,
2-856-5298
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Karen Lesko
Sent: Monday, April 11, 2016 11:18 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Unconnected sprinklers
The Life Safety Code does say &quo
being, to avoid a false suggestion of safety.
Now the question is raised if it is written in the NFPA or FM that
unconnected sprinklers are not allowed.
Unfortunately, I can't find it.
Another suggestion was to put a sign on the door to each room saying
"Sprinklers not functional".
Met v
.
Ed Foster
Fire Marshal
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Frans Stoop
Sent: Monday, April 11, 2016 3:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Unconnected sprinklers
Gentlemen,
Is it written
if it is written in the NFPA or FM that
unconnected sprinklers are not allowed.
Unfortunately, I can't find it.
Another suggestion was to put a sign on the door to each room saying
"Sprinklers not functional".
Met vriendelijke groet/Kind regards,
Frans Stoop
Riskonet B.V.
Sing
the NFPA or FM that
unconnected sprinklers are not allowed.
Unfortunately, I can't find it.
Another suggestion was to put a sign on the door to each room saying
"Sprinklers not functional".
Met vriendelijke groet/Kind regards,
Frans Stoop
Riskonet B.V.
Singel 540, 1017AZ, Amste