Re: Nipple Extenders

2008-05-09 Thread Charles Thurston
Hello Mike,

We have used AA x AA Male/Female extensions where both sizes are the same.
I have seen them in  1/2 3/4 1 lengths.

Thursday, May 8, 2008, 5:21:16 PM, you wrote:

 Quick (I hope) question.

  

 I don?t recall seeing this thread before. Are ½? x 1?  male female nipple
 extenders allowed to be used at the sprinkler/reducer coupling interface
 when you have cut the drop a smidgen too short and can?t get back above the
 hard ceiling to pull it out?

  

  Mike Wisneski



  

  3898 Leeds Avenue

  North Charleston, SC 29405

  Phone: 843-767-3080

  Cell: 843-200-5710

  Fax: 843-767-5596

  Email : [EMAIL PROTECTED]

  Web   :
 file:///C:\Documents%20and%20Settings\User\Application%20Data\Microsoft\Sig
 natures\www.pyebarkerfiresafety.com www.pyebarkerfiresafety.com

  

 This e-mail, including attachments, may include  confidential and /or
 proprietary information, and may be used only by the person or entity to
 which it is addressed. If the reader of this e-mail is not the intended
 recipient or his or her authorized agent, the reader is hereby notified that
 any dissemination, distribution or copying of this e-mail is prohibited. If
 you have received this e-mail in error, please notify the sender by replying
 to this message and delete this e-mail immediately

  




-- 
Best regards,
 Charles Thurstonmailto:[EMAIL PROTECTED]
  Coastal Fire Protection

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


SxL rule

2008-05-09 Thread Dewayne Martinez
I have recently had a disagreement with a AHJ on how to determine the
protection area of coverage for a sprinkler.
In my situation, we have an OH II area which has extended coverage
sprinklers (14x14) and one standard throw sprinkler.
The distance between the extended and standard sprinkler is 12 ft.  I
was taught that since we are proving the EC sprinkler at 14x14, you
would take 7ft off the distance between the sprinklers and use 5ft as
the one of distances (x2=10ft) to determine the area of coverage for the
standard sprinkler.  He states that per NFPA, you would use the distance
between the sprinklers (ie:12ft).
We are going 13ft between sprinklers the other dimension so using my way
we are at 130sq ft but his way we are 156sq ft.
Which way is right?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Nipple Extenders

2008-05-09 Thread Mike Brown (TECH- GVL)

United Brass makes a 1/2 by 1/2 male by female and a 3/4 x 3/4 male by 
female extender.  These can be used to extend a drop that is cut too short.  
AFSA in the past had a BEST PRACTICE written about the use of these.  There 
is some argument that these should not be used but they can be helpful.  There 
is also a company that makes a cast iron version of the same thing and they are 
a little longer than the brass ones.  I was always more comfortable using the 
brass extender nipples.  You can contact AFSA or go on their website to see if 
you can find the article in the archives'.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Wisneski
Sent: Thursday, May 08, 2008 5:21 PM
To: sprinklerforum@firesprinkler.org
Subject: Nipple Extenders

Quick (I hope) question.



I don't recall seeing this thread before. Are ½ x 1  male female nipple
extenders allowed to be used at the sprinkler/reducer coupling interface
when you have cut the drop a smidgen too short and can't get back above the
hard ceiling to pull it out?



 Mike Wisneski





 3898 Leeds Avenue

 North Charleston, SC 29405

 Phone: 843-767-3080

 Cell: 843-200-5710

 Fax: 843-767-5596

 Email : [EMAIL PROTECTED]

 Web   :
file:///C:\Documents%20and%20Settings\User\Application%20Data\Microsoft\Sig
natures\www.pyebarkerfiresafety.com www.pyebarkerfiresafety.com



This e-mail, including attachments, may include  confidential and /or
proprietary information, and may be used only by the person or entity to
which it is addressed. If the reader of this e-mail is not the intended
recipient or his or her authorized agent, the reader is hereby notified that
any dissemination, distribution or copying of this e-mail is prohibited. If
you have received this e-mail in error, please notify the sender by replying
to this message and delete this e-mail immediately



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Change in static pressure

2008-05-09 Thread Dewayne Martinez
I have a job site which is 10ft higher than the water supply.  A gauge
on the water supply hydrant reads 55 PSI static pressure while two
gauges on the system riser after the BFP read 37 PSI?  The total
elevation change between the system gauges and the supply gauge is about
17ft.  Why would there be a 18 PSI difference between the gauges when
elevation only accounts for 7.36 PSI? 
I confirmed with the city that there are no shut valves.  Any thoughts? 
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Change in static pressure

2008-05-09 Thread art
Gage calibration is my 1st thought. Check all the gages or use your own
calibrated gages.

Art
ATCO/Tiroly

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, May 09, 2008 1:55 PM
To: sprinklerforum@firesprinkler.org
Subject: Change in static pressure

I have a job site which is 10ft higher than the water supply.  A gauge
on the water supply hydrant reads 55 PSI static pressure while two
gauges on the system riser after the BFP read 37 PSI?  The total
elevation change between the system gauges and the supply gauge is about
17ft.  Why would there be a 18 PSI difference between the gauges when
elevation only accounts for 7.36 PSI? 
I confirmed with the city that there are no shut valves.  Any thoughts? 
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Change in static pressure

2008-05-09 Thread Russell
Perhaps there is trapped thermal pressure or surge pressure on the system
side of the BFP.

Russell R

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, May 09, 2008 1:55 PM
To: sprinklerforum@firesprinkler.org
Subject: Change in static pressure

I have a job site which is 10ft higher than the water supply.  A gauge
on the water supply hydrant reads 55 PSI static pressure while two
gauges on the system riser after the BFP read 37 PSI?  The total
elevation change between the system gauges and the supply gauge is about
17ft.  Why would there be a 18 PSI difference between the gauges when
elevation only accounts for 7.36 PSI? 
I confirmed with the city that there are no shut valves.  Any thoughts? 
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.11/1422 - Release Date: 5/8/2008
5:24 PM
 

No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.11/1422 - Release Date: 5/8/2008
5:24 PM
 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Change in static pressure

2008-05-09 Thread Paul Pinigis
Look at the cut sheet on the BFP.  Some BFPs require a significant
amount of pressure to open at very low flows.  For example, an 12 Ames
2000SS requires almost 6 psi to operate at very low flow so it can sit
there all day with an upstream pressure nearly 6 psi higher than the
system side pressure.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, May 09, 2008 1:55 PM
To: sprinklerforum@firesprinkler.org
Subject: Change in static pressure

I have a job site which is 10ft higher than the water supply.  A gauge
on the water supply hydrant reads 55 PSI static pressure while two
gauges on the system riser after the BFP read 37 PSI?  The total
elevation change between the system gauges and the supply gauge is about
17ft.  Why would there be a 18 PSI difference between the gauges when
elevation only accounts for 7.36 PSI? 
I confirmed with the city that there are no shut valves.  Any thoughts? 
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Change in static pressure

2008-05-09 Thread Todd Williams - FPDC

Dwayne,

Were the pressures read on the gauges on the hydrant and the BFP at 
the same time? Was any water flowing when these were read? We had a 
situation recently where we had differing pressures and what we found 
out was that the city had a 30 psi fluctuation in the street they did 
not know about.


Todd


At 01:54 PM 5/9/2008, you wrote:

I have a job site which is 10ft higher than the water supply.  A gauge
on the water supply hydrant reads 55 PSI static pressure while two
gauges on the system riser after the BFP read 37 PSI?  The total
elevation change between the system gauges and the supply gauge is about
17ft.  Why would there be a 18 PSI difference between the gauges when
elevation only accounts for 7.36 PSI?
I confirmed with the city that there are no shut valves.  Any thoughts?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
___

Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Change in static pressure

2008-05-09 Thread Dewayne Martinez
No, they were not read at the same time.  The gauges on the BFP were
read last night and the hydrant information was read this morning by the
city water department.  This is starting to make sense now. The fire
department said that the water tower is refilled at night so this might
account for the missing PSI.  I will go back out to the job in the
morning to check the gauges again to see what they read then.
Thanks,
Dewayne   

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Friday, May 09, 2008 1:33 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Change in static pressure

Dwayne,

Were the pressures read on the gauges on the hydrant and the BFP at the
same time? Was any water flowing when these were read? We had a
situation recently where we had differing pressures and what we found
out was that the city had a 30 psi fluctuation in the street they did
not know about.

Todd


At 01:54 PM 5/9/2008, you wrote:
I have a job site which is 10ft higher than the water supply.  A gauge 
on the water supply hydrant reads 55 PSI static pressure while two 
gauges on the system riser after the BFP read 37 PSI?  The total 
elevation change between the system gauges and the supply gauge is 
about 17ft.  Why would there be a 18 PSI difference between the gauges 
when elevation only accounts for 7.36 PSI?
I confirmed with the city that there are no shut valves.  Any thoughts?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email 
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Change in static pressure

2008-05-09 Thread Dewayne Martinez
Thanks,
I will look into the cut sheet.  The fitter preformed an alarm test so
only a small amount of water was flown. 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, May 09, 2008 1:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Change in static pressure

Look at the cut sheet on the BFP.  Some BFPs require a significant
amount of pressure to open at very low flows.  For example, an 12 Ames
2000SS requires almost 6 psi to operate at very low flow so it can sit
there all day with an upstream pressure nearly 6 psi higher than the
system side pressure.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, May 09, 2008 1:55 PM
To: sprinklerforum@firesprinkler.org
Subject: Change in static pressure

I have a job site which is 10ft higher than the water supply.  A gauge
on the water supply hydrant reads 55 PSI static pressure while two
gauges on the system riser after the BFP read 37 PSI?  The total
elevation change between the system gauges and the supply gauge is about
17ft.  Why would there be a 18 PSI difference between the gauges when
elevation only accounts for 7.36 PSI? 
I confirmed with the city that there are no shut valves.  Any thoughts? 
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Change in static pressure

2008-05-09 Thread Ron Greenman
The BFP should trap the highest pressure on the system side so that
the up and down fluctuations will happen on the supply side. This will
read the same as the two gages on an alarm check valve when it is
acting as the only system/supply check. The water tower seems the
culprit. The elevation difference accounts for 7.4 psi. The remaining
10.6 psi could be the tank if the before refill/after refill elevation
inside the tank is 24.5 feet.



On Fri, May 9, 2008 at 11:59 AM, Dewayne Martinez [EMAIL PROTECTED] wrote:
 Thanks,
 I will look into the cut sheet.  The fitter preformed an alarm test so
 only a small amount of water was flown.

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Paul
 Pinigis
 Sent: Friday, May 09, 2008 1:22 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Change in static pressure

 Look at the cut sheet on the BFP.  Some BFPs require a significant
 amount of pressure to open at very low flows.  For example, an 12 Ames
 2000SS requires almost 6 psi to operate at very low flow so it can sit
 there all day with an upstream pressure nearly 6 psi higher than the
 system side pressure.

 Paul J. Pinigis, P.E.
 Chief Life Safety Engineer

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
 Martinez
 Sent: Friday, May 09, 2008 1:55 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Change in static pressure

 I have a job site which is 10ft higher than the water supply.  A gauge
 on the water supply hydrant reads 55 PSI static pressure while two
 gauges on the system riser after the BFP read 37 PSI?  The total
 elevation change between the system gauges and the supply gauge is about
 17ft.  Why would there be a 18 PSI difference between the gauges when
 elevation only accounts for 7.36 PSI?
 I confirmed with the city that there are no shut valves.  Any thoughts?
 Thanks,
 Dewayne
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
 to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
 to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
at home
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Change in static pressure

2008-05-09 Thread Paul Pinigis
If water was flowed on the system side of the BFP there can be a lower
pressure on the system side vs. the supply side due to the on-off
action of some axial-check BFPs.  This is not the same phenomenon as the
pressure difference across an ACV because the ACV uses a simple
side-hinged check.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Friday, May 09, 2008 3:33 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Change in static pressure

The BFP should trap the highest pressure on the system side so that
the up and down fluctuations will happen on the supply side. This will
read the same as the two gages on an alarm check valve when it is
acting as the only system/supply check. The water tower seems the
culprit. The elevation difference accounts for 7.4 psi. The remaining
10.6 psi could be the tank if the before refill/after refill elevation
inside the tank is 24.5 feet.



On Fri, May 9, 2008 at 11:59 AM, Dewayne Martinez [EMAIL PROTECTED]
wrote:
 Thanks,
 I will look into the cut sheet.  The fitter preformed an alarm test so
 only a small amount of water was flown.

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Paul
 Pinigis
 Sent: Friday, May 09, 2008 1:22 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Change in static pressure

 Look at the cut sheet on the BFP.  Some BFPs require a significant
 amount of pressure to open at very low flows.  For example, an 12
Ames
 2000SS requires almost 6 psi to operate at very low flow so it can sit
 there all day with an upstream pressure nearly 6 psi higher than the
 system side pressure.

 Paul J. Pinigis, P.E.
 Chief Life Safety Engineer

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
 Martinez
 Sent: Friday, May 09, 2008 1:55 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Change in static pressure

 I have a job site which is 10ft higher than the water supply.  A gauge
 on the water supply hydrant reads 55 PSI static pressure while two
 gauges on the system riser after the BFP read 37 PSI?  The total
 elevation change between the system gauges and the supply gauge is
about
 17ft.  Why would there be a 18 PSI difference between the gauges when
 elevation only accounts for 7.36 PSI?
 I confirmed with the city that there are no shut valves.  Any
thoughts?
 Thanks,
 Dewayne
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
 to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
 to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
at home
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: SxL rule

2008-05-09 Thread Roland Huggins
The starting point is the explicit guidance that addresses the last  
sprinkler or branch line against a wall.  You apply the longest  
dimension from either side for both S and L.  This places the  
sprinkler in the center of the imaginary rectangle.  The same  
philosophy applies to non-symmetrical layouts within the system.  Yep  
there is a lot of overlap but it provides a consistent methodology.


Roland

On May 9, 2008, at 5:30 AM, Dewayne Martinez wrote:


I have recently had a disagreement with a AHJ on how to determine the
protection area of coverage for a sprinkler.
In my situation, we have an OH II area which has extended coverage
sprinklers (14x14) and one standard throw sprinkler.
The distance between the extended and standard sprinkler is 12 ft.  I
was taught that since we are proving the EC sprinkler at 14x14, you
would take 7ft off the distance between the sprinklers and use 5ft as
the one of distances (x2=10ft) to determine the area of coverage for  
the
standard sprinkler.  He states that per NFPA, you would use the  
distance

between the sprinklers (ie:12ft).
We are going 13ft between sprinklers the other dimension so using my  
way

we are at 130sq ft but his way we are 156sq ft.
Which way is right?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Change in static pressure

2008-05-09 Thread Todd Williams - FPDC
If the solution is not evident when you re-check, have the city put a 
pressure recorder on the hydrant. That will show the ups and downs 
over a period of time. In my situation it was 3 tanks that filled at 
random times.




At 02:57 PM 5/9/2008, you wrote:

No, they were not read at the same time.  The gauges on the BFP were
read last night and the hydrant information was read this morning by the
city water department.  This is starting to make sense now. The fire
department said that the water tower is refilled at night so this might
account for the missing PSI.  I will go back out to the job in the
morning to check the gauges again to see what they read then.
Thanks,
Dewayne

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Friday, May 09, 2008 1:33 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Change in static pressure

Dwayne,

Were the pressures read on the gauges on the hydrant and the BFP at the
same time? Was any water flowing when these were read? We had a
situation recently where we had differing pressures and what we found
out was that the city had a 30 psi fluctuation in the street they did
not know about.

Todd


At 01:54 PM 5/9/2008, you wrote:
I have a job site which is 10ft higher than the water supply.  A gauge
on the water supply hydrant reads 55 PSI static pressure while two
gauges on the system riser after the BFP read 37 PSI?  The total
elevation change between the system gauges and the supply gauge is
about 17ft.  Why would there be a 18 PSI difference between the gauges
when elevation only accounts for 7.36 PSI?
I confirmed with the city that there are no shut valves.  Any thoughts?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
___

Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Change in static pressure

2008-05-09 Thread Allan Seidel
My thought is open up the BFP and check for rocks. The one time I've  
seen odd numbers at the BFP it was due to rocks introduced by the  
site plumber altering the incoming service unbeknownst to the fire  
protection contractor who had already installed his stuff.  Using the  
numbers given, 55 at the street is 47.6 at the BFP. The system side  
can drop below 47.6 because at the check valve the check area exposed  
to the street pressure is smaller than the check area exposed to the  
system pressure.  A system pressure smaller than 47.6 will hold the  
check closed against the street because that smaller system pressure  
is acting on a check area larger than the check area the street is  
acting on. This happens twice in a double check. That accounts for  
some of pressure difference. Now add some rocks on the system side in  
the BFP that act in favor of the system side. Maybe that is what is  
going on and maybe not, but keep in mind that all the rest of the  
system in question is just plain pipe and valves. The only unknown  
mechanism involved is what is inside the BFP.


Allan Seidel
St. Louis, MO


On May 9, 2008, at 12:54 PM, Dewayne Martinez wrote:


I have a job site which is 10ft higher than the water supply.  A gauge
on the water supply hydrant reads 55 PSI static pressure while two
gauges on the system riser after the BFP read 37 PSI?  The total
elevation change between the system gauges and the supply gauge is  
about

17ft.  Why would there be a 18 PSI difference between the gauges when
elevation only accounts for 7.36 PSI?
I confirmed with the city that there are no shut valves.  Any  
thoughts?

Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- 
[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)