You might try the contact below for Firematic replacement parts:
Company: 900 Industries, Inc.
Address: 16 Deborah Drive
Sutton, MA 01590
Phone: 508-865-9600
FAX: 508-865-7336
Email: [EMAIL PROTECTED]
Web: www.900 industries.com
Contact: Paul L. McNamara
Mike Cabral
"Sal Izz
No, Firematic is no longer in business.
Salvatore Izzo, P.E.
Manager - Reliable Technical Services
From: [EMAIL PROTECTED] [EMAIL PROTECTED] On Behalf Of douglas hicks [EMAIL
PROTECTED]
Sent: Monday, December 08, 2008 2:15 PM
To: sprinkler board
Subject:
bject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the
is Cinematic still in business? I need a clapper for a Model D 3 inch
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an em
Sorry to correct you George bun tin the south it's "Hey Ya'll, watch this!"
They've already drank the beer hence the reason for the aforementioned
statement, plus they sure wouldn't trust their friend bubba to just hold it.
Sorry I digress.
Craig L. Prahl, CET
Fire Protecti
Watch out for the mfg. areas too. They have a tendency to stack large
quantities of battery cases and some of the other plastic parts in the
manufacturing and assembly areas. So Group A may be present in more places
than just the storage warehouse. Plus once they're filled they are considered
It not blowing itself (and us) up was our primary focus. Didn't leave a lot
of room in our minds for doing the "watch this!" sort of thing of running
out from behind the stone wall and taking a picture as it blows up (In the
Midwest during snowmobile season, and South pretty much anytime, I
underst
Has anyone designed a sprinkler system for a facility that manufactures and
stores batteries on racks. If so what was the design criteria? I'd say OH2
for the manufacturing area and group A plastic storage for the rack area.
Not much info is available yet on the type of batteries. The following
Too bad, that's almost like seeing bigfoot (no offense george).
I've tested a dual drive which is kinda cool to see with the clutches and
whatnot.
Tom
Circa 1990, if I had pics I have no idea where they'd be. Don't recall
taking any.
The monster was abandoned in place, to the best of my memory.
Circa 1990, if I had pics I have no idea where they'd be. Don't recall
taking any.
The monster was abandoned in place, to the best of my memory.
glc
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Monday, December 08, 2008 10:53 AM
To
Joe,
Although NEC 695 does not cover (695.1(B)) jockey pumps they are permitted
to be connected to the fire pump feeder. There are however requirements for
tapping the fire pump feeder. The tap however cannot be taken within the
fire pump controller. The primary overcurrent and feeders shall consi
TECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
__ Information from ESET NOD32 Antivirus, version of virus signature
database 3672 (20081208) __
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
It is stated in the NEC, Article 695.6 (F)
(F) Junction Points. Where wire connectors are used in
the fire pump circuit, the connectors shall be listed. A fire
pump controller or fire pump power transfer switch, where
provided, shall not be used as a junction box to supply
other equipment, includi
Joe,
Try this:
NFPA 70, 2005 edition, 695.6 (F) Junction Points.
"Where wire connectors are used in the fire pump circuit, the connectors shall
be listed. A fire pump controller or fire pump power transfer switch, where
provided, shall not be used as a junction box to supply other equipment
NFPA 20 (1999, Edition) 7-3.4.4
A fire pump controller shall not be used as a junction box to supply other
equipment. Electrical supply conductors for pressure maintenance (jockey or
make-up) pump(s) shall not be connected to the fire pump controller.
David Autry
Plans Examiner
Nebraska State Fi
The fire pump controller can't be used as a junction box for other services.
Not sure where to find it. Ask the controller mfg.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
3300 King Ave
Cleveland, OH 44114
216-621-8899
216-570-7030 cell
-Original Message-
From: [EMAIL
I just had a job site meeting with a electrical contractor. He stated the
engineer wanted to feed the jockey pump controller from the fire pump
controller. Something about a tapping rule or exception. I cautioned against
it, told him to research it first. Can anyone give me a section that prohib
Did you take any pictures ?
John
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Monday, December 08, 2008 9:56 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: This week's discovery
It had been out of service quite some time and
Tyco shows a rebuild kit in their current price book:
_http://tyco-fireproducts.com/TFP_common/TFP_Price_Oct/TFBP_S20_061708.pdf_
(http://tyco-fireproducts.com/TFP_common/TFP_Price_Oct/TFBP_S20_061708.pdf)
Forest Wilson
Cherokee Fire
In a message dated 12/8/2008 10:05:55 A.M. Eastern Stan
Good morning group.
Does anyone know where I can find parts for a Star Model BB exhauster??
Thanks,
Mike Wisneski
3898 Leeds Avenue
North Charleston, SC 29405
Phone: 843-767-3080
Cell: 843-200-5710
Fax: 843-767-5596
Email : [EMAIL PROTECTED]
Web : www.pyebarkerfiresaf
It had been out of service quite some time and wasn't in the best shape.
With all the unknowns facing us in repairing the syeam pump, it was more
prudent to switch to electric.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Saturda