RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Matsuda, Richard
110-feet?...woohoo...I don't think I've ever seen anything like this. I'm glad I asked before I stuck my foot in my mouth. I'll have to agree with Todd and change my answer to No, put the 1st level of rack sprinklers at 10-foot as shown in the figure. The storage arrangement is an extreme...and

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Matsuda, Richard
Ron, Let's play devils advocate and go back to the question that I asked in my first response. If your total storage arrangement is 35-feet high, do you design for the total height of 35-feet or only 30-feet high since the lower 5-feet is dead space? I don't understand your note regarding your

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Craig.Prahl
Is this an ASRS system, narrow aisles, automated picker? What are the cartons? Cardboard, 5-sided plastic, etc? Typically in these hi-rise rack systems the bottom tier is inaccessible to the picker so there is no regular storage of commodities, BUT that doesn't mean there is not other

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Jimmy Waite
I don't know if I've seen all of this thread, I just got back today. The first thing that strikes me is that storage is 110 feet, and I'm assuming there are ceiling sprinklers that are even higher. So, not to throw another kink in your operation, but how will stratification of heat work in this

RE: Dry System Valves Air Supply

2009-01-05 Thread Thom McMahon
We blow out at full line open, usually that means 50 to 75 Psi back pressure. When we fill or reset the valve, we use radio's with the valve just cracked at the compressor. Fill usually takes about 2 minutes. We leave the air couplings on the drum drips, but not the insp. Test. Then we're pretty

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Craig.Prahl
Sorry, hit the ENTER --- button too soon Is this an ASRS system, narrow aisles, automated picker? What are the cartons? Cardboard, 5-sided plastic, combustible, non-combustible, encapsulated, etc? Typically in these hi-rise rack systems the bottom tier is inaccessible to the

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Craig.Prahl
Ceiling sprinkler may or may not operate depending on where the fire starts. That's why you have the in-racks and face sprinklers in the racks. The sprinklers closest to ignition should respond and control the fire so those above don't have to. Craig L. Prahl, CET Fire Protection

RE: Sidewall Sprinklers

2009-01-05 Thread Craig.Prahl
Why would anyone want to install a sidewall head exposed in the middle of a room? Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439

RE: Sidewall Sprinklers

2009-01-05 Thread George Church
It's all they had left on the truck? More likely at NIH, the last 20' of the room is wall to wall duct above the ceiling. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent:

RE: another fire - this will be interesting

2009-01-05 Thread Terri Leyton
__ Information from ESET NOD32 Antivirus, version of virus signature database 3739 (20090105) __ The message was checked by ESET NOD32 Antivirus. http://www.eset.com ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman

RE: Sidewall Sprinklers

2009-01-05 Thread Johnson, Duane (NIH/OD/ORS) [C]
Low clearance areas (ie. garage entrance ramp). A sidewall (or extended coverage sidewall at that) would keep your pipe out of the no hang zone where uprights (or extended coverage uprights) won't permit. Inaccessible areas. Rather than paying for scaffolding to get you over furniture/storage,

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Jimmy Waite
Monday has struck again. They way I was reading it was there would ONLY be one level of in-racks. Oops. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Monday, January 05, 2009

RE: Sidewall Sprinklers

2009-01-05 Thread Craig.Prahl
Guess all that would be just peachy if the mfgr listing stated that it's head was listed for such applications. I've often wished for an OH or even EH listed sidewall for similar reasons. But apparently the mfgrs. don't intend for them to be used for more than LH occupancies in most cases.

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Todd Williams
I am skeptical about the idea of a bottom level space being unused in a storage warehouse. At some point, someone will figure out how to use it and then it will be a mess. Stick with the 10 ft above the floor, I would. At 09:51 AM 1/5/2009, you wrote: Ron, My answer is maybe yes...but I'd

1st Level of in-rack sprinklers location

2009-01-05 Thread Fletcher, Ron
Anyone want to take a shot at this? Figure 17.3.4.1.3(d) indicates the first level of sprinklers to be 10 ft. approximately from the floor and is shown above the second cube in the elevation view. If there is a 5 ft. dead space (empty with no storage or other equipment) from the floor to the

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Fletcher, Ron
Rick, Once the storage is over 25 ft. the height really doesn't matter. The roof density is determined by the distance from top level or in-racks to the top of storage and the in-rack requirement is from Figures 17.3.1.2(a) to 17.3.1.2(f) based on a level of sprinklers about every 10 ft. or two

RE: Sidewall Sprinklers

2009-01-05 Thread A.P.Silva
I agree, the codes do not permit installation of sidewalls without a backwall/soffit/beam in any other situation. However, this is something I have often wondered myself. Granted, all closed sprinklers actuated by thermal elements require to be in proximity to a ceiling. The thermal elements in

RE: Sidewall Sprinklers

2009-01-05 Thread George Church
I'm not a PE nor do I play one on TV. But I've seen James' fire videos, so I'm ahead of most plumbing designers:) Caveats aside, I think activation depends on heat banking down from the ceiling, and in order to get a head to throw 24' it has to go off- and that's a long way for heat to go without

RE: Sidewall Sprinklers

2009-01-05 Thread Thom McMahon
Many OH as well as LH HSW heads and even OH Dry HSW heads are available. Reliable has MBEC-14 for those metal frame and purlin buildings, in addition to their other listings for HSW. The availability of the heads is not in question here, it's the installation, and without the wall/soffit behind

RE: Sidewall Sprinklers

2009-01-05 Thread Craig.Prahl
Activation is most likely not the issue but pattern of discharge. At the wall there is no real need for discharge in more than one direction as opposed to a pendent or upright in the middle of a room where you're seeking a 360 degree field of discharge. Same deal for the sidewall under the

Re: 1st Level of in-rack sprinklers location

2009-01-05 Thread Todd Williams
We all know that nothing ever falls out and that stuff never collects in empty spaces under things, does it? At 11:42 AM 1/5/2009, you wrote: If you room for another foot, I'll toss out a thought We have a high level of assurance that stuff will not be located on the floor (that pesky

RE: Movie studio classification

2009-01-05 Thread Steve Leyton
to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 3739 (20090105) __ The message was checked by ESET NOD32 Antivirus. http://www.eset.com

RE: Sidewall Sprinklers

2009-01-05 Thread GAYLE KNOWLES
I think the earlier response is the issue. There is no room to get over to the area to be protected, hence spray the area with the sidewall. I've wanted to do it on several occasions, but just didn't seem right. There are pendant heads protecting the area behind the sidewall. so the

RE: fire pump room requirement

2009-01-05 Thread Steve Leyton
...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 3739 (20090105) __ The message was checked by ESET NOD32

RE: Sidewall Sprinklers

2009-01-05 Thread A.P.Silva
Say you have a room that is 24 feet wide. The first 12 feet is covered with a pendent 6 feet feom the left wall. What is the problem with having a sidewall at the centre of the room facing towards the right wall to cover that part of the room. I know NFPA codes doesn't allow it. But I'd like to

RE: Sidewall Sprinklers

2009-01-05 Thread Craig.Prahl
Wall behind the SW doesn't play a part in the spray pattern. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 craig.pr...@ch2m.com

Re: Sidewall Sprinklers

2009-01-05 Thread Roland Huggins
The only exception to not having a wall, soffit, or beam behind them is when installed UNDER roll-up doors ( as allowed by 8.4.2 (3) Roland On Dec 31, 2008, at 11:37 AM, Dale Wingard wrote: Duane, NFPA 13(2007) 8.7.4.1.2 addresses the location of vertical and horizontal sidewalls in

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Fletcher, Ron
No one gets shot on this forum (I hope), all opinions are appreciated. To play devils advocate though what would you do if the load height were 10 ft. instead of 5? The top of the first tier would be 15 ft. off the floor. I don't agree with the source of ignition would probably be at the floor

Re: 1st Level of in-rack sprinklers location

2009-01-05 Thread Roland Huggins
If you room for another foot, I'll toss out a thought We have a high level of assurance that stuff will not be located on the floor (that pesky automated equipment has little tolerance for variances I assume). Would you not consider that the main issue is having in-racks every other

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Fletcher, Ron
1. 110 ft. storage. 2. Every other level as shown in 17.3.4.1.3(d). 3. Class IV and Group A in cartons. In this case it makes one level of sprinklers difference and in this building it's a lot of sprinklers. Ron Fletcher Aero Automatic Sprinkler 21605 N. Central Ave Phoenix, AZ 85024 P:

RE: another fire - this will be interesting

2009-01-05 Thread Chris Cahill
Dave P. said Once there's a fire in a building there is another completely real life hazard in play - the responding emergency personnel.  Some may enter the building and be very close to harm's way and others may respond and have ancillary functions - traffic control, EMS, crowds etc. As an 18

RE: test

2009-01-05 Thread Tom Duross
You get to roll the hoses. :) 500 gpm on the first and 250 gpm on each of the other three, totaling 1250 gpm. What do I win? At 08:53 AM 1/5/2009, you wrote: 1,2,3,4. ___ Sprinklerforum mailing list

Re: test

2009-01-05 Thread Todd Williams
500 gpm on the first and 250 gpm on each of the other three, totaling 1250 gpm. What do I win? At 08:53 AM 1/5/2009, you wrote: 1,2,3,4. ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical

RE: another fire - this will be interesting

2009-01-05 Thread Chris Cahill
Ron said (I suspect the savings in mains, hydrants, fire stations, apparatus and firefighters is way more than a wash in fully sprinklered, planned communities than the cost of sprinklering schools). Were these savings realized? Last I read which was a long time ago there was very little saved

Electrical Rooms and Archives

2009-01-05 Thread David de Vries
I usually save Forum postings if I expect to need them in the future.  Of course, I thought I knew the rules on dedicated space for electrical equipment well enough that I did not need to save the latest round of discussion on this subject.  Now I have the following comment on a submittal:  

RE: Electrical Rooms and Archives

2009-01-05 Thread Craig.Prahl
Don't have a 2002 but how does the wording compare to the 2008? Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 craig.pr...@ch2m.com

RE: Sidewall Sprinklers

2009-01-05 Thread Thom McMahon
Careful with that all encompassing statement. For Residential Sidewall I believe that the BackWall Wetting to reduce Flash-over is still a very important factor. Additionally I've been told that yes there is a certain percentage of water that does direct back from the standard HSW heads to the

Re: Electrical Rooms and Archives

2009-01-05 Thread Richard Lindner
Try this.. http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: techsupp...@firesprinkler.org To

RE: Sidewall Sprinklers

2009-01-05 Thread Craig.Prahl
Back-wall wetting would be a result of the discharge pattern, the wall is the recipient of the discharge not the creator. And while that may be an issue for residential, it's not for other non-residential applications. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Matsuda, Richard
Ron, My answer is maybe yes...but I'd like to know the full extent of the storage before I agreed. 1. How high is the total storage? The chart is for over 25-feet high. 2. Where are the 2nd and 3rd levels of rack sprinkler located? 3. What is being stored? Not that any of these questions make a

test

2009-01-05 Thread Tom Duross
1,2,3,4. ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: techsupp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org

RE: Sidewall Sprinklers

2009-01-05 Thread Johnson, Duane (NIH/OD/ORS) [C]
Looking at 155°F EC pendents and uprights, 20x20 are standard response and 18x18 (or less) are quick response. In other words, the sprinkler is either 9' away or 10' away from the fire. This leads one to believe that it would be possible to have an exposed HSW listed for a 10' throw for at

RE: Sidewall Sprinklers

2009-01-05 Thread Johnson, Duane (NIH/OD/ORS) [C]
Note for residential sidewalls, the 2007 edition section 8.10.7.1.5.2 permits residential sidewalls to be installed above cabinets up to 12 without pendents below. Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes

RE: Sidewall Sprinklers

2009-01-05 Thread Thom McMahon
All Dandy idea's. Now all you need to do is show that there is enough need for this to have UL and FM develop a standard test for this installation, then convince the MFG's that the demand for this installation is great enough for them to spend 100's of thousands of $ to get the testing and

RE: Sidewall Sprinklers

2009-01-05 Thread Craig.Prahl
Hey just get an AHJ to sign off on the concept, then it's all good! ;) Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439

Re[2]: Sidewall Sprinklers

2009-01-05 Thread Charles Thurston
Hello Craig, I have an AHJ that suggested back to back sidewall heads under a low walkway to get the throw out to each side over the open space between the walkway and the front of the condo unit. The condos connect to the walkway via a bridge to the front door. There is dirt below the open space

RE: Electrical Rooms and Archives

2009-01-05 Thread David de Vries
Looks like the language is identical in the 2008 and 2002 editions.  NFPA 70-2002:  110.26(F)(1)   (b)  Foreign Systems.  The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the

Re: Electrical Rooms and Archives

2009-01-05 Thread David de Vries
Thanks, Richard.  That link worked and I found all postings just as I recalled. Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated 2715 Harrison St. Evanston, IL 60201 Tel: 847-733-0944 Fax: 847-866-6255 --- On Mon, 1/5/09, Richard Lindner rklindner.w...@gmail.com

Re[2]: Sidewall Sprinklers

2009-01-05 Thread Todd Williams
Charles, That sounds like a project that I would get called on. Thanks for handling this one. I would suggest an open head deluge system and with the right lighting, you could get rainbows (sprinkler bows?). Todd At 05:27 PM 1/5/2009, you wrote: Hello Craig, I have an AHJ that suggested

RE: Re[2]: Sidewall Sprinklers

2009-01-05 Thread Thom McMahon
If you think your liability went away when the AHJ signed off on an unlisted installation, think again. Even if you had a P.E. write the letter and the AHJ accepted it you're the installer, and still Liable. Check with your insurance underwriter, they usually have some very fine lawyer's who can

RE: another fire - this will be interesting

2009-01-05 Thread scott mitchell
Well, if the passive people can hire big gun FPE firms to stand up and say one in six sprinkler systems fail to operate in a fire event, then surely we can dangle a plastic carrot in front of a developer or two.    Wouldn't it then behove the developer to follow through with holding the

RE: another fire - this will be interesting

2009-01-05 Thread Rod DiBona
Very good point. It reminds me of gift cards. The stores make a ton of extra money on these cards being bought but not used. Are they to blame? Rod DiBona Rapid Fire -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On

RE: Electrical Rooms and Archives

2009-01-05 Thread John Drucker
David, You are correct. John Drucker Fire Protection Subcode Official Electrical Inspector Borough of Red Bank, NJ -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de Vries Sent: Monday, January 05,