Re: air pockets and false alarms (aka: Statistics)

2009-03-22 Thread bverhei


All: 

I hope I am not misunderstanding the question. 

1. Do wet systems using a pressure switch without integral retard installed at 
the top of a retard chamber generate unwanted alarms? 

The answer is definitely yes. 

The problem in the city I work for seems largely associated with systems with 
large internal volume. Flow switches and pressure switches as described both 
seem to have problems. But that may be result that the city I work in is 
characterized with distribution centers. Many have 0.39 gpm/sf over 5,600 sf. 
systems. Depending on the decade of installation, large tree, looped, or 
gridded systems. 

It also characterized by a large area without residences. Instead of many small 
water uses turn on and off, a fewer bigger industrial users turn water on and 
off. Use peaks in summers. Highest use is not 0500 to 0700 or 1700 to 1900 hrs. 
as most people, or at least me, guessed. Highest use is as 0200-0300 hrs. This 
non-intuitive use is landscaping irrigation sprinklers coming on. During this 
time another use that turns water on and off is parking lot washers. 

The pressures switches at top of retard chambers seem allowed by code; often 
within a few months of installation it is obvious they are problematic, and an 
alternative is used. Given the cost that is entailed by everyone concerned I 
fail to understand why if pressure swiches are to be use on a wet system, an 
integral retard are not always used. It costs to send a fitter out to correct 
the problem. (I always assume this is a call back the spk co. eats. Am I wrong 
- does the owner pay again?) 

2. I've yet to see a prv on dry systems. It was my understanding the dry 
systems leak air, and that seasonally they bleed air excess air in the spring. 
The compressor just runs less. Is installing prv's a regional adaptation? Puget 
Sound is not known for blistering cold or blistering heat. My experience is all 
from here. 

3. I've never seen the 300 psi on wet systems, and I've looked at a lot of 
guages. Those little 175 psi relief valves seem to be the most precise thing 
installed on a system. The bleed right to 175. 

4. Jockey pumps. I want to make sure I am saying the same thing. I think of a 
jockey pump as a small pump of a few gpm in paralel with a big fire pump. The 
small pump runs to prevent the big pump from starting. Its start pressure is 
set above the start pressure for the big pumps controller. They use a real pump 
controller. Where fire pumps and jockey pumps are installed false alarm 
associated with pressure fluctuations are rare. They are usally corrected by 
sending the right person out to adjust controller settings. Most of our fire 
pumps are associated with ESFR pre-K25 heads. 

We have had a few customers who had to install excess pressure pumps at their 
systems. The problem was associated with normal pump runs causing false alarms. 
It also seems more of a problem with pumps serving a number of buidlings in 
industrial/distribution center campuses, as opposed to a just serving a single 
building. 

5. Excess pressure pump. An excess pressure pump is again a small pump. It is 
not required to be listed for fire pump usage. It is normally 120 VAC. It's UL 
listing is just like my table lamp. The listing is for electrical safety, not 
functionality. It pumps from supply side of a (alarm usually) check valve to 
system side. (Please install the system connection above the flow switch.) They 
do not use a real fire pump controller. They maintain pressure in the system 
above that expected from pressure surges in the system. I've usually seen ~20 
psi above observed system gauge prior to installation of pump. 

If the question is false alarms in wet sprinkler systems excess pressure pumps 
are a definitive solution. 

Once an excess pressure switch is installed our experience is that any further 
false alarms are associated with human communication difficulties, lightning 
activity Any thing but pressure fluctations. 

Yours, 

Bruce Verhei 



- Original Message - 
From: Ed Vining edvinin...@gmail.com 
To: sprinklerforum@firesprinkler.org 
Sent: Friday, March 20, 2009 11:38:15 AM GMT -08:00 US/Canada Pacific 
Subject: Re: air pockets and false alarms (aka: Statistics) 

Yes Jim. Pressure in the retard chamber is relieved through the drain when 
the alarm port is closed. 

On Fri, Mar 20, 2009 at 10:26 AM, jim.robe...@fluor.com wrote: 

 I had not been following the thread because the subject title hasn't 
 changed, but am I correct in assuming this problem does not occur with 
 pressure switches at the top of retard chambers? 
 
 James L.(Jim) Roberts, PE/SET 
 Fluor Corporation 
 100 Fluor Daniel Drive - C104F 
 Greenville, SC 29607 
 864.281.5149 
 864.281.4916(Fax) 
 
 
 
 
 
 Jay Jay Blocker fire_sprinkler...@yahoo.com 
 Sent by: sprinklerforum-boun...@firesprinkler.org 
 03/03/2009 08:09 PM 
 Please respond to sprinklerforum 
 
 To 
 sprinklerforum@firesprinkler.org 
 cc 
 
 Subject 
 Re: 

Re: Excessive system pressure

2009-03-22 Thread bverhei

Bill. 

Please don't do this without a pressure relief on a vessel. Or at least don't 
make the container that is solid use a liquified gas with a low boiling 
pressure. 

One ton Cl2 cylinders use very heavy walls. The ends are arched toward the 
product for security and strength. If you fail to leave a vapor space they 
bulge outward before the plugs fail. Not good. 

Bruce Verhei 


- Original Message - 
From: bill brooks bill.bro...@brooksfpe.com 
To: sprinklerforum@firesprinkler.org 
Sent: Friday, March 20, 2009 2:42:27 PM GMT -08:00 US/Canada Pacific 
Subject: RE: Excessive system pressure 

Rodney, 

You said you aren't hard headed and you understand the principles behind 
the system pressure increases. Here's a chance to prove both. 

1. Two containers of identical volume. One container 50% water, the 
other container 100% water. Each has been sitting in a 50 F room with 
the lid off. In other words the liquid and the containers are at 50F. 
Now make sure the 100% container is topped off and put lids on both. 
Read the pressure gage and satisfy yourself they both read 0. Move 
both containers into a 120 F room and come back when the two systems 
reach 120 F. 

2. Same as above, but remove 10% of the water from the filled container 
before capping and moving. 

When the systems reach 120 F, which container has the higher pressure in 
each of the cases above? 

Bill Brooks 

William N. Brooks, P.E. 
Brooks Fire Protection Engineering Inc. 
372 Wilett Drive 
Severna Park, MD 21146 
410-544-3620 Phone 
410-544-3032 FAX 
412-400-6528 Cell 

___ 
Sprinklerforum mailing list 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
For Technical Assistance, send an email to: techsupp...@firesprinkler.org 

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org 
(Put the word unsubscribe in the subject field) 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Excessive system pressure

2009-03-22 Thread Steve Leyton
Excellent information.  So to summarize, it's agreed by all that excess 
pressure issues are valid and should be dealt with by way of valves or 
accessories designed for that application, such as PRV's.   And alarm test 
connections can be located anywhere downstream of the device they're intended 
to test.  

Steve Leyton
Protection Design  Consulting
San Diego, CA



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Rodney Hamm
Sent: Friday, March 20, 2009 9:13 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Excessive system pressure


I FULLY INTEND THAT THIS WILL BE MY LAST POST REGARDING THIS SUBJECT. I
promise to make a concerted effort to make this statement true. I would also
like to state that you should probably read this entire post if you have not
completely tuned out regarding this subject!


I obtained my Bachelors Degree in Mechanical Engineering and I am also a
FPE; I am fully aware and I understand thermal expansion. A few forum
participants posted data regarding water, but refrained from including any
thermal expansion data for air. My point is that thermal expansion effects
both water and air. The following two paragraphs were copied from the
internet:


Charles's law states that when pressure is kept constant, there is a direct
relationship between volume and temperature. As a gas heats up, its volume
increases, and when it cools down, its volume reduces accordingly. Thus, if
an air mattress is filled in an air-conditioned room, and the mattress is
then taken to the beach on a hot day, the air inside will expand. Depending
on how much its volume increases, the expansion of the hot air could cause
the mattress to pop.


 

That is to say, he discovered that if a container of air were to be sealed
at 0*C, at ordinary atmospheric pressure of 15 pounds per square inch, and
then heated to 100*C but kept at the same volume, the air would now exert a
pressure of about 20 pounds per square inch on the sides of the container.
(Of course, strictly speaking, the container will also have increased in
size, that would lower the effect-but it's a tiny correction, about ½% for
copper, even less for steel and glass.)  Remarkably, if the air were
initially at a pressure of thirty pounds per square inch at 0*C, on heating
to 100*C the pressure would go to about 40 pounds per square inch-so the
percentage increase in pressure was the same for any initial pressure: on
heating through 100*C, the pressure would always increase by about 33%.

 

Water on the other hand: On heating from 0*C through 30*C, the pressure will
stay essentially constant, while heating from 30*C through 100*C, the
pressure will increase by about 4%. Check out the thermal expansion
properties of air and water if you think I am wrong. Web site:
http://www.engineeringtoolbox.com/water-thermal-properties-d_162.html 

 

In summary, I guess I am simply trying to state that trapped air pockets
will create a more significant pressure increase or decrease in a closed
sprinkler system than water when the temperature changes. 

 

I will absolutely admit that I cannot explain mathematically why we see such
drastic pressure increases in the numerous wet sprinkler systems where we
have identified and resolved these issues (based strictly on Charles's Law,
the pressure increases should not be so extreme), but I can state that the
excessive pressure problem is completely resolved after we bleed off a
significant amount of the trapped air pockets. This is not a theory, this is
absolute real world action with undeniable results. Some systems relieve air
for 20-40 minutes through multiple sprinkler heads (loosened enough to hear
and feel the air escape from the system at the various high points). After
we remove a significant amount of the trapped air, the problem is resolved.
And to address the obvious question, the problem is resolved even without a
175 psi PRV (we do not always provide the 175 psi PRV, but we typically
recommend them for gridded systems; some clients agree to provide them, but
some decide against paying for the 175 psi PRV).

 

I will officially let it go. I have planted a few seeds through this forum
and hopefully caused a few people to think about the subject to some degree.


 

I sincerely hope that I have not caused any animosity or hurt feelings..if
so, PLEASE know that I had no intentions of making anyone feel bad in any
way, shape or form. 

 

I also feel compelled to state that I am really not trying to win an
argumentarguing or an obsession of being right is usually a fruitless
and ultimately negative exercise. That being said, I imagine that I am now
officially branded as argumentative and/or obsessive. I hope this is not
the case, but I am a Big Boy and I can deal with it I guess! Over time, I
sincerely hope everyone on this forum will realize that my overall
intentions are to have a positive impact, learn from 

Re: Excessive system pressure

2009-03-22 Thread Ron Greenman
A single example of very cold from several years ago when I used to
work for a living. An unoccupied section of a warehouse. Wet sprinkle
system. All the branch lines on that side of the riser end in that
space. The heat has been turned off. Several freeze and break due to
freezing. We can assume that there is no air trapped in the new ends
of the broken lines since the ice plugs are keeping the system intact.
There probably is trapped air at the other end and in the frozen end
where branch lines have not broken. I'm called out because the riser
is leaking around the flow  switch. When I get there there is also
water weeping out around all the face plate bolts. The gauge reads
zero. As I'm standing in front of this riser I rap on the gauge a
couple of time and get not wiggle in the needle. I look closer and
the needle is pegged on the back side of the zeroing pin, ergo 300+
psi. Quick little dance to the side and I try to open the main drain
to bleed this sucker off. No chance even though my personal little
hell there is literally frozen over. I finally cracked the main drain
using a Texas Ten (ten-inch pipe wrench with a cheater that extends
the handle to the same leverage as an 18 wrench) on the stem. I felt
like I was in one of those submarine movies where flange bolts are
going to start shooting off. The power ice. So question of the day: If
thermal expansion causes pressure to rise/fluid to expand when heat is
applied and to contract when heat is removed what then causes water to
also expand when it reaches it's freezing point and is this true for
all fluids. This two-part question is worth 50% of your final exam
relative to this thread.

And Rodney, thanks for your final comments. I for one was thinking you
were being more than a little contentious, arrogant and argumentative
(in the negative context of that word), but after stating your intent
throughout the thread all is forgiven. As in all institutions the
Forum has a culture and sometimes it takes a new guy a bit of time to
settle in. John Drucker can probably remember this crazy guy that
entered the alarm forum, pretty much told everyone they were idiots,
and at one point attacked me with a verbal violence I reserve for
Hitler  his ilk because he took some offense at a joking comment I
made to another member thinking I was insulting him. I offered a
left-handed apology which he accepted, missing the sarcasm, and
eventually left the forum. You seem to have gotten the culture here
right, so welcome.

On Sun, Mar 22, 2009 at 10:11 AM, Steve Leyton
st...@protectiondesign.com wrote:
 Excellent information.  So to summarize, it's agreed by all that excess 
 pressure issues are valid and should be dealt with by way of valves or 
 accessories designed for that application, such as PRV's.   And alarm test 
 connections can be located anywhere downstream of the device they're intended 
 to test.

 Steve Leyton
 Protection Design  Consulting
 San Diego, CA



 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Rodney Hamm
 Sent: Friday, March 20, 2009 9:13 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Excessive system pressure


 I FULLY INTEND THAT THIS WILL BE MY LAST POST REGARDING THIS SUBJECT. I
 promise to make a concerted effort to make this statement true. I would also
 like to state that you should probably read this entire post if you have not
 completely tuned out regarding this subject!


 I obtained my Bachelors Degree in Mechanical Engineering and I am also a
 FPE; I am fully aware and I understand thermal expansion. A few forum
 participants posted data regarding water, but refrained from including any
 thermal expansion data for air. My point is that thermal expansion effects
 both water and air. The following two paragraphs were copied from the
 internet:


 Charles's law states that when pressure is kept constant, there is a direct
 relationship between volume and temperature. As a gas heats up, its volume
 increases, and when it cools down, its volume reduces accordingly. Thus, if
 an air mattress is filled in an air-conditioned room, and the mattress is
 then taken to the beach on a hot day, the air inside will expand. Depending
 on how much its volume increases, the expansion of the hot air could cause
 the mattress to pop.




 That is to say, he discovered that if a container of air were to be sealed
 at 0*C, at ordinary atmospheric pressure of 15 pounds per square inch, and
 then heated to 100*C but kept at the same volume, the air would now exert a
 pressure of about 20 pounds per square inch on the sides of the container.
 (Of course, strictly speaking, the container will also have increased in
 size, that would lower the effect-but it's a tiny correction, about ½% for
 copper, even less for steel and glass.)  Remarkably, if the air were
 initially at a pressure of thirty pounds per square inch at 0*C, on heating
 to 100*C the 

Excessive system pressure

2009-03-22 Thread å . . . . . . .
  So question of the day: If
 thermal expansion causes pressure to rise/fluid to expand when heat is
 applied and to contract when heat is removed what then causes water to
 also expand when it reaches it's freezing point and is this true for
 all fluids. This two-part question is worth 50% of your final exam
 relative to this thread.


my guess is---


what causes water to expand when it freezes has to do with the
way the molecular lattice forms in the solid phase.  The little
buggers don't hug so tightly, when they realize they are
stuck with their nearest neighbor from now until...well...until their
personal hell thaws over.


no, it is not true for all fluids.  water being one of the few molecules
that behaves in this way.  If it did not behave in this way, it would be
SHTF time.   we would not be here.
that is because our planet  would have frozen over
long ago.  when liquid water expands to form solid ice, it becomes
less dense than liquid--- which is nice.  nice because it insulates
the water below, so the fish can continue to go about their
business.  if ice were denser than liquid water, ice would sink,
allowing the surface to continue to generate more and more
ice, probably leading to a solid frozen slab of water through its
thickness.   not good for aquatic life, which is not good for
terrestial life, either.

 scot deal
 excelsior fire engineering
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Excessive system pressure

2009-03-22 Thread bverhei

It is hard to remember all the ways that water is a special chemical. 

Bruce Verhei 


no, it is not true for all fluids. water being one of the few molecules 
that behaves in this way. 
scot deal 
excelsior fire engineering 
___ 
Sprinklerforum mailing list 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
For Technical Assistance, send an email to: techsupp...@firesprinkler.org 

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org 
(Put the word unsubscribe in the subject field) 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: air pockets and false alarms (aka: Statistics)

2009-03-22 Thread Rodney Hamm
James,

 

I would have to answer No to your question.

 

In my experience, the problem is typically much more common with retard
chambers which are equipped with pressure switches. I stated this in one of
my previous emails, but you are the first person I have noticed who asked
specifically about retard chambers with pressure switches. The problem
usually shows itself the night after the system has been drained/filled or
tested (i.e. main drain tests or ITC testing) or within a week or two if the
daytime and nighttime temperatures are not drastically different. The false
alarm problem exists if the air pockets are large enough OR if the public
water supply has a normal cycle which results in higher city main pressures
at night than during the day (primarily when they fill the gravity tanks). I
have seen this problem many times at facilities fed by the public water
supply as well as facilities fed by fire pumps with jockey pumps. As the air
pocket volume decreases due to colder temperatures at night, water enters
the system piping. During small fluctuations water enters the system through
the bypass line or ball check in the clapper (if provided) with no false
alarm. During larger pressure fluctuations, the clapper opens slightly to
accommodate the slightly larger water flow rate; usually just enough to fill
the retard chamber and activate the pressure switch (10-25 seconds is
usually all that is needed for most retard chambers). I have noticed these
false alarms are also more common when a cold front moves through which has
rain (I suppose the building temperature drops faster in this situation). 

 

Pressure switches on retard chambers do not have delay settings and
typically activate sooner/quicker than a flow switch set with a 30-60 second
delay. The problem sometimes remains idle after the low temperatures have
allowed enough water to enter the system and the air pockets have been
compressed enough to maintain a system pressure higher than the public water
supply UNTIL the next drastic temperature drop and even colder cold front
moves through. This is when the plant maintenance man closes the alarm line
for good because he knows just enough to realize this action will
permanently resolve the problem (if he did not already do it immediately
following the first false alarm!). Fire alarm system is no longer active,
but the false fire alarm issue is no longer a problem. Am I really the only
person in America who has seen this scenario? If anyone else has experienced
this problem, please send a quick email and let us all know what you did to
resolve the issue.

 

Ant doubters reading this email should probably ask themselves a question.
How many times have you visited a facility and found the alarm line for the
water motor gong closed? This is a fairly good indication they have had
false alarms; if you ask the right people at the facility, they will
probably remember since false fire alarms are very aggravating to them. My
brother is a Lieutenant on a local fire department and they get called on
false fire alarms on a very regular basis.

 

If you encounter this problem and want to be completely sure this is the
culprit, my advice is to place a 5 gallon bucket to catch the water in the
retard chamber drain line. If you have a false alarm and the bucket has
water, this is probably what happened. I usually cover the top of the bucket
with plastic to prevent rain water accumulation. I have done this several
times to prove to my customers that the problem is not with the electronic
components in the alarm system. One customer actually sealed the alarm test
valve, alarm line valve, main drain and ITC to make completely sure nobody
was opening the valves at night; I really liked the idea. In these
instances, the easiest resolution might be to remove the pressure switch and
provide a flow switch which allows for a longer delay depending, of course,
on how long water flows into the system during the false alarm events. I
usually install the flow switch and remove as much air as possible when I
reinstate the system and the problem is exterminated! 

 

Take care,

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

Date: Fri, 20 Mar 2009 13:26:59 -0400

From: jim.robe...@fluor.com

Subject: Re: air pockets and false alarms (aka: Statistics)

To: sprinklerforum@firesprinkler.org

Message-ID:

  ofe5d18c54.116385b3-on8525756f.0044b35b-8525757f.005ff...@fluor.com

Content-Type: text/plain; charset=us-ascii

 

I had not been following the thread because the subject title hasn't
changed, but am I correct in assuming this problem does not occur with
pressure switches at the top of retard chambers?

 

James L.(Jim) Roberts, PE/SET

Fluor Corporation

100 Fluor Daniel Drive - C104F

Greenville, SC 29607

864.281.5149

864.281.4916(Fax)

 

___
Sprinklerforum mailing list

Re: Excessive system pressure

2009-03-22 Thread Trevor Spain
Michael,

Thanks for posting an accurate compression constant for liquid water.  I 
should have known better than to grab something from the internet for a 
quick post (1 part in 5x10^7).  Nothing like being off by a few orders 
of magnitude!  I've since found a decent site on water, if you're 
curious: http://www.lsbu.ac.uk/water/explan2.html

Take care and God bless.

Michael Fitz wrote:
 Rodney,

 I deal with these problems all the time.  The sprinkler system MUST have
 some air in it or an expansion tank otherwise the pressure will jack up to
 high pressures.  We see this problem every time a check valve is installed
 in a domestic water system where there is a water heater downstream.  Cold
 water fills the system and is then heated, say from 50 to 130.  The
 volumetric expansion of water is very high when compared to the linear
 expansion of the copper water pipes (or the steel pipes of a sprinkler
 system) and the water will drain out of the PRV.  If it doesn't have one,
 something breaks as explained below.

 As with most real systems, it can be extremely complicated to exactly model
 and calculate precisely what happens.  Assume that water expands when
 heated, albeit a small amount. This amount is about .000207/degree C at 68F.
 For a 1% change in volume and assuming the factor is constant (it isn't), we
 would need to heat the water 48 degrees C or about 87 F.

 Also assume that water is somewhat compressible.  Table 5.4 of Eshbach's
 Handbook of Engineering Fundamentals, 4th Edition, lists the compressibility
 (K or Beta) of water at 68F as 318,000 PSI where dP=dV*K  This means for a
 1% change in volume, the pressure would go up or down 3,180 PSI.

 IF we assume a completely sealed rigid container full of water, not too
 unlike a sprinkler system, then we just need to equate the thermal expansion
 of water to the compressibility of water.  This way, the change in volume
 cancels out.  In other words, if we heated the water 87F, then the pressure
 would rise 3,180 PSI.  This rough calculation indicates that the pressure
 would theoretically increase about 36 PSI per degree F.

 Now in real life, the pipes also expand because of the temperature rise (2X
 the linear expansion rate) AND because the pressure rise of the water
 stresses the material so it also elastically expands.  If there are any
 gaskets that allow the pipes to move a little in the groove, that changes
 things a little.  So you can see the actual pressure rise is difficult to
 calculate but what happens is that the actual pressure rise in a system is a
 lot less than that rigid container calculation shown above.  This is how we
 select expansion tanks, see
 http://www.watts.com/pro/divisions/watersafety_flowcontrol/learnabout/learna
 bout_thermexpansion.asp  It's a good explanation why it is so very dangerous
 to overfill a propane tank.  The liquid will expand until the tank goes
 hydraulic and then it burps over the PRV with a very little change in
 temperature.

 General rules of thumb:  Water compressibility 318,000 PSI, Glycerin =
 630,000 PSI. Glycerin can exert twice the force assuming the same
 temperature change, another reason to have the right expansion tanks on an
 antifreeze system.

 Air (assuming ideal) P2 = P1*V1/V2.  Halve the volume, double the absolute
 pressure, quite compressible.
   
 P2 = P1*T2/T1  Double the absolute temperature and you double the absolute
 pressure.  As an example, for a temperature rise of air in a rigid container
 from 68F to 98F and a system pressure of 75 PSIA, the pressure would
 increase to 75*(98+460)/(68+460) or 79.3 PSIA.   For those that read gauges,
 essentially from 60 to 64 PSI.

 Hope this clears up why trapped air pockets DON'T cause significant pressure
 increases with temperature and why air free systems dangerously increase
 in pressure with rises in temperature.

 Michael

 Michael M. Fitz, P.E., C.F.I.
 MDE Inc.
 700 S. Industrial Way
 Seattle, WA  98108
 www.MDE.com
 206-321-1804
   

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Southwest Airlines FALSE advertisment

2009-03-22 Thread Coastal
Hello sprinklerforum,

  Has anybody else seen the TV commercial where the guy has something in the 
microwave, The microwave emits a shower of sparks and the sprinklers in the 
room go off? I looked at their website for an email address to write to, but 
all they have is a feedback form... Anybody in Dallas want to track down an 
email address for Gary Kelly ? I called customer service and they said they did 
not have it.

Thanks 

-- 
Best regards,
Charles Thurston
Coastal Fire Protection  mailto:coastalf...@sc.rr.com


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)