RE: test header

2013-06-03 Thread Mark A. Sornsin, P.E.
Moreover, the engineer could specify Ron's solution up front. Doesn't help the design-build jobs - but you as the contractor could offer it up front...in such a way that makes you look like you're helping the customer, not just seeking a means to get more money out of them (easy to say...).

RE: test header

2013-06-03 Thread John Denhardt
Mark and Ron - You are so correct. Put the header in and be done. It is less expensive in the long run. John John August Denhardt, P.E., FSFPE Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone

RE: test header

2013-06-03 Thread RFletcher
NFPA 13 and 24 only require the forward flow test. Maybe they could be changed to require a means to forward flow test? Around here most BFP's are installed at the property line so they are not in the FP contractor's scope. Ron F -Original Message- From:

Re: test header

2013-06-03 Thread Ron Greenman
I think we're talking about the 25 test here and this is an ongoing deal. When you find a system without means it is in the owner's interest to pay for installing a header, which can be as little as dropping the system and adding a couple of mech tees and hose valves to the FDC line, plus the cost

Re: test header

2013-06-03 Thread Todd - Work
What exactly is the purpose of a forward flow test on a backflow preventer? This is not required on other check valve devices such as alarm valves, riser checks, water meters, etc. Has there been a history of problems that this seems to solve? Todd G Williams, PE Fire Protection

Re: test header

2013-06-03 Thread Ron Greenman
Yes there has. These checks are designed to be opening and closing regularly and to differing demands. Once they started being required of sprinklers it was found that they didn't always operate as designed (if we were sitting with a bunch of models open I could show you various pinch points where

Re: test header

2013-06-03 Thread George Church
I believe tommy d could fill you in on a lot of local horror stories. Sent from my iPhone On Jun 3, 2013, at 10:24 AM, Todd - Work t...@fpdc.com wrote: What exactly is the purpose of a forward flow test on a backflow preventer? This is not required on other check valve devices such as alarm

Re: required section modulus (it don't get no easier)

2013-06-03 Thread ParsleyConsulting
Brad, Part 1 - Gibberish. Pure and simple. The tables in NFPA 13 didn't reduce the force and distance by half in their calculations. It simply used the formula to calculate the maximum moment at the point of the load for a simple beam, based on the maximum length of various pipe sizes

RE: test header

2013-06-03 Thread Cahill, Christopher
This discussion is about the minority of systems right? Doesn't the 2 main drain take care of most LH and OH? Chris Cahill, PE* Senior Fire Protection Engineer, Aviation Facilities Group Burns McDonnell 8201 Norman Center Drive Bloomington, MN 55437 Phone:  952.656.3652 Fax:  952.229.2923

RE: required section modulus (it don't get no easier)

2013-06-03 Thread Brad Casterline
Ken, Sorry if I touched a nerve or upset you. I am nothing but a designer with a trust issue; I simply do not trust anything in any code or standard until I can explain it to myself like I'm 6 years old. May I send you a spread sheet I made many years ago? It will allow you to quickly calc the

Re: test header

2013-06-03 Thread Roland Huggins
NFPA 13 has stated for a couple of cycles that a means shall be provided to forward flow test the BFP. Look at 8.17.4.6.1. Because Mr Greenman requested it, I'll state it shall be the FLOW portion of system demand. It just says a flow test at system demand. THe annex implies flow by

Re: Fire Pump - Pressue Relief Valve

2013-06-03 Thread Roland Huggins
exactly. NFPA 14 gives a lot of detail on how to accomplish this set-up. Using a relief valve is a big no-no. Dumping a bunch of water every time you do a churn test (weekly for diesel and monthly for electric) is a bad thing that is not allowed by NFPA 20. Roland Huggins, PE - VP

RE: Fire Pump - Pressue Relief Valve

2013-06-03 Thread Sean Roberts
NFPA 14 allow to control separate zones with a pressure reducing valve Thank you, Sean Roberts 4456 Campbell RD, Houston, TX 77041 713-896-9941 Fax 713-896-9945 Cell 713-206-8837 sean.robe...@wsfp.us -Original Message- From: Roland Huggins [mailto:rhugg...@firesprinkler.org] Sent:

RE: Fire Pump - Pressue Relief Valve

2013-06-03 Thread Joe Powell
Thanks guys Joe C. Powell Pruett Ford Associates, Inc. Consulting Engineers 1201 Broad Street, Suite 3A Augusta, GA 30901 Ph: 706-722-3959 Fax:    706-724-5127 Email: jpow...@pruettford.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

Re: Fire Pump - Pressue Relief Valve

2013-06-03 Thread Roland Huggins
There's also a master pressure reducing valve assembly (contains 2 primary PRV's, a smaller PRV to account for lower sprinkler testing flows, a by-pass etc etc) for controlling a larger portion of the building and triggered by having more than 2 hose connections downstream of the BFP. Roland

Re: required section modulus (it don't get no easier)

2013-06-03 Thread ParsleyConsulting
Brad, No, thank you for the offer on the spreadsheet, I have myown, and thanks to some very patient structural engineers on the hanging and bracing committee, and the Eighth Edition of the Manual of Steel Construction, I have all the formulas I could ever need or use. And, because I

RE: test header

2013-06-03 Thread Mark A. Sornsin, P.E.
Chris - the potential design flow for an ordinary hazard, group 2 system is 300 to 400 gpm. Can you get that from your 2 drain? How do you know what rate your 2 in. drain allows? Even if your system is designed to flow light hazard and has a maximum design flow of 125 gpm, how do you measure

RE: required section modulus (it don't get no easier)

2013-06-03 Thread Brad Casterline
my gosh Ken, you appear to be almost as stubborn as i am... i like that! i wrote: section modulus is moment divided by stress. moment is half the force(lb) times half the distance(in). the force is the weight of the water-filled pipe plus 250. the distance is 4ab/a+b. the stress is 15,000. for

Re: test header

2013-06-03 Thread Roland Huggins
you calculate it just like flow from any other orifice open to the exterior. The judgement part comes in for assigning a discharge coefficient and the exact size for a threaded orifice. This issue was the exact topic of an article in the May issue of Sprinkler Age. It can be accessed from

Supervisory valve

2013-06-03 Thread Phong - Indochine Engineering
Dear All, For one floor of a highrise tower, there is normally one supervisory valve for the sprinklers of that floor. Traditionally a supervisory gate valve is used but an UL/FM supervisory butterfly valve is also manufactured at a cheaper price. Does NFPA regulate to use which type of valve

Re: Supervisory valve

2013-06-03 Thread Charles Thurston
Hello Phong, No There are many systems with butterfly (butterball) valves in them. Just as long as it is supervised or locked open. Monday, June 3, 2013, 9:10:36 PM, you wrote: Dear All, For one floor of a highrise tower, there is normally one supervisory valve for the sprinklers of that

RE: Fire Pump - Pressue Relief Valve

2013-06-03 Thread Steve Leyton
Sorry for the late chime in - I'm (theoretically) on vacation and don't have NFPA 20 with me. As already stated, the 20 yields to other standards that may incorporate a fire pump into an approved water supply - 13, 14, 24, etc. Where 20 ends isn't defined, but the discharge control valve