Re: Hydraulic Calculations

2008-11-19 Thread Todd Williams
Eladio, This should be calculated. For one thing, the new arrangement may now be the most hydraulically remote. Assuming that the protection requirements will not change, with 12x14 spacing and 0.1 density, you will be flowing 16.8 gpm per sprinkler. However, with the 6x14 spacing, the

RE: Man made reservoir to be used for fire protection?

2008-11-21 Thread Todd Williams
Shannon, About the only successful arrangement I have seen from a retention pond is a vertical turbine pump in a suction crib. You have to be very careful meeting NPSH of a horizontal pump from a reservoir. There are only two that I know of that work and they have the suction pond up the

Re: Collapsing File Storage System

2008-11-21 Thread Todd Williams
There was a recent thread on this; check the archives. Use concealed sprinklers At 09:08 AM 11/21/2008, you wrote: I need input as to what type/arrangement sprinklers you would use over the top of accordion type filing cabinets like are used in offices, etc. that are on tracks and can be

variable public water supply

2008-11-26 Thread Todd Williams
I did a flow test yesterday where the municipality had recently installed a new variable speed pump at a pumping station. The static pressure was 67 psi. We flowed the hydrant and the pressure dropped to about 45 psi (flow of about 500 gpm). Then the pump kicked in and boosted the pressure

RE: variable public water supply

2008-11-28 Thread Todd Williams
The system is a combination of gravity tanks and pumps. This particular location is close to the highest point in town and pumps are required to much more that flush a low-flow toilet. This was actually the first time hydrant had been flowed since the pump was installed (3 weeks ago), so I'm

RE: variable public water supply

2008-11-29 Thread Todd Williams
] On Behalf Of Todd Williams Sent: Friday, November 28, 2008 10:21 AM To: sprinklerforum@firesprinkler.org Subject: RE: variable public water supply The system is a combination of gravity tanks and pumps. This particular location is close to the highest point in town and pumps are required to much more

A new winner?

2008-12-01 Thread Todd Williams
Did a flow test this morning. Static 94, Residual 16, Flow 369 gpm. The head of the water department was reading the gauge. No plans to investigate (yet). Think they can design a dry system in a wood truss attic on that? Todd G. Williams, PE Fire Protection Design/Consulting Stonington,

Re: Specialized Location Service for Underground Water Mains

2008-12-02 Thread Todd Williams
Most site contractors have a backhoe. If you are dealing with multiple mains, especially if they cross, it could be difficult to find an answer using typical soundings techniques. Maybe someone in the geology department at Rutgers (A UCONN fan recommending Rutgers?) could maybe give you some

Re: Spec's. vs. Drawings

2008-12-04 Thread Todd Williams
I usually send an RFI citing the conflict. At 08:31 AM 12/4/2008, you wrote: Good mornin'. I have always been under the impression that the contract drawings for a project take precedence over the specifications. This was just passed down from my early involvement in the trade and have never

RE: Spec's. vs. Drawings

2008-12-04 Thread Todd Williams
Make that git a Suthin law'er At 02:08 PM 12/4/2008, you wrote: Here is the section I like to include concerning documents and design. It's written for use in the south. Feel free to adjust it for your specific location. I must say that living by these rules has provided countless

RE: This week's discovery

2008-12-06 Thread Todd Williams
No foam, part of 1.5 million sqft of unoccupied manufacturing space. (A few years ago, I did see an 1890s system and 1890s sprinklers with foam stacked to the bottom of the pipe.) The building was actually built in 1935, not 1955 (full scale FIA plan shrunk down to 8.5x11 and too much eye

RE: This week's discovery

2008-12-07 Thread Todd Williams
The last one I saw took about 30 minutes to get up to speed. FM wouldn't give them credit for it. At 12:22 PM 12/7/2008, you wrote: Wow! A steam turbine? I've only seen one before and it's actually out for bid for replacement right now here in MA. Did you take pictures I hope? Tom FGOL

Re: Battery manufacturing and storage

2008-12-09 Thread Todd Williams
Tony, Here is a good link describing the product http://en.wikipedia.org/wiki/Gel_battery#Gel_battery. Check for any chemicals used in the manufacturing before you jump to OH2 conclusions. At 01:24 PM 12/8/2008, you wrote: Has anyone designed a sprinkler system for a facility that

Re: Foam Block Insulation

2008-12-09 Thread Todd Williams
Is this above a ceiling? Did the Fire Marshal sign off on this? If this is not at least somewhat fire retardant, there could be a huge problem. The Station fire spread via foam on the ceiling. What you have is probably better, but could still be a significant problem. See if the Building or

Re: 13R Storage Room in exterior balcony

2008-12-11 Thread Todd Williams
It seems to meet the intent, but.. How is the closet heated? If there is an electric heater in a storage closet, I would be very concerned about that as a potential ignition source. If there is warm air fed from the dwelling, it doesn't meet the standard of no penetrations. Is the balcony

Re: Pipe Installed in concrete

2008-12-16 Thread Todd Williams
Bad and potentially ugly. I have too many scenarios in my head to organize or put down on what could happen. If there is any possibility of building movement, it could ba a horror show. The old WTC used to flex 10 ft in the wind at the top floor (designed in). Just my thoughts... At

RE: Dry Pipe System Dilemmas

2008-12-17 Thread Todd Williams
Assuming no leaks, how many feet would a dry system have to drop before the compressor comes on? Actually, there can be plenty of reasons why DPVs will trip. Craig's and other responses describe a lot of good scenarios, but they are by no means all of them. Just don't necessarily believe what

pipe schedule standpipe

2008-12-23 Thread Todd Williams
I have been asked to evaluate an existing standpipe system in a hospital. There are separate risers and mains that feed a network of 1-1/2 fire hose cabinets (no 2-1/2 valves). There is not sufficient water to supply the system, based on NFPA 14 requirements. Nor have any previous

stimulus

2008-12-23 Thread Todd Williams
Any thoughts about the upcoming stimulus package including anything for Code and/or safety upgrades to public buildings? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 ___ Sprinklerforum

pipe schedule standpipe

2008-12-23 Thread Todd Williams
I have been asked to evaluate an existing standpipe system in a hospital. There are separate risers and mains that feed a network of 1-1/2 fire hose cabinets (no 2-1/2 valves). There is not sufficient water to supply the system, based on NFPA 14 requirements. Nor have any previous

pump suction conundrum

2008-12-24 Thread Todd Williams
I did a hydrant flow test at a location and had a 67 psi static pressure. About 1/2 hour later, I flowed a fire pump taking suction from this line and had a suction pressure at churn (0 flow) of 55 psi. There is no elevation difference and the gauges used were calibrated. I would think they

RE: pump suction conundrum

2008-12-24 Thread Todd Williams
activity drew the narrow standpipe down 28'? Booster station in the area's pump had kicked off? glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Wednesday, December 24, 2008 6:11 AM

Re: pump suction conundrum

2008-12-24 Thread Todd Williams
Shelbyville, IL 62565 Todd Williams wrote: I did a hydrant flow test at a location and had a 67 psi static pressure. About 1/2 hour later, I flowed a fire pump taking suction from this line and had a suction pressure at churn (0 flow) of 55 psi. There is no elevation difference and the gauges used were

Re: HAPPY HOLIDAYS!

2008-12-24 Thread Todd Williams
We may not choose to participate in the recession, but will our clients? (It reminds me of the story of the small town in Turkey. They were told the town was built over a fault line and they could be subject to major earthquakes. The town council unanimously voted to move the fault line.)

Re: HAPPY HOLIDAYS!

2008-12-24 Thread Todd Williams
Oh yea? Ask the people in TN with the sludge problem. At 12:08 PM 12/24/2008, you wrote: Steve, There is no dam recession. They're still all there and full size. Happy Holidays to all. On Wed, Dec 24, 2008 at 8:48 AM, Steve Muncy smu...@firesprinkler.org wrote: The AFSA Staff and Board of

Re: Seismic Bracing CPVC in 13R Applications

2008-12-24 Thread Todd Williams
Were the rods less than 6? At 01:54 PM 12/24/2008, you wrote: Has anybody had the opportunity to seismic brace a 13R cpvc system in platform style construction? Recently a designer in my company submitted plans for a NFPA 13R system built of platform style construction: TJI's for the ceiling

fire pump room requirement

2008-12-26 Thread Todd Williams
Where in the maze of standards is the requirement for a fire pump to be in a separate room? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 ___ Sprinklerforum mailing list

Re: fire pump room requirement

2008-12-26 Thread Todd Williams
Thanks, Forest. CT is still using the 1999 edition and it is in Chapter 2 in that one. The reference helped a lot. At 06:40 PM 12/26/2008, you wrote: 20-5.12.1.1 INSIDE UNITS Forest Wilson Cherokee Fire In a message dated 12/26/2008 6:25:56 P.M. Eastern Standard Time, t...@fpdc.com writes:

Re: Movie studio classification

2008-12-29 Thread Todd Williams
There is a small but active studio in this area that I have done work on. Everybody is pretty much on target. However, there also can be a fair amount of plastics. This particular place has a full scale model of a WWII anti-aircraft gun made of foam, cardboard and paper machet. NFPA 140 should

suction pressure dilemma - part 2

2008-12-29 Thread Todd Williams
I posted a problem about a month ago regarding a situation where the suction pressure at churn of a pump was 12 psi less than the static pressure during a flow test. Both were read at no-flow conditions and there is no elevation difference. I was looking for an explanation, as yet, none has

another fire - this will be interesting

2008-12-31 Thread Todd Williams
http://www.wtnh.com/dpp/news/news_wtnh_Shelton_High_fire_200812301825 Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 ___ Sprinklerforum mailing list

Re: another fire - this will be interesting

2008-12-31 Thread Todd Williams
Sounds like NAHB talking points.. At 04:16 PM 12/31/2008, you wrote: I agree. I had a recent conversation with my father about the residential IBC requirements. His first concern was: The tenant will cause the sprinkler to activate and flood the house if they are at war with the

Re: another fire - this will be interesting

2009-01-01 Thread Todd Williams
the average fire fatalities in US educational facilites for years 2000 - 2005 was zero. maybe because of sprinklers, but maybe because of: ample exits noncombustible construction fire loads are not significant in most public schools, relative to the volume they contain.

RE: another fire - this will be interesting

2009-01-01 Thread Todd Williams
convinced from years of these and other settings that folks just don't finagle with sprinklers. Happy New Year Campers, Tom -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org]on Behalf Of Todd Williams Sent: Wednesday

RE: 1st Level of in-rack sprinklers location

2009-01-05 Thread Todd Williams
I am skeptical about the idea of a bottom level space being unused in a storage warehouse. At some point, someone will figure out how to use it and then it will be a mess. Stick with the 10 ft above the floor, I would. At 09:51 AM 1/5/2009, you wrote: Ron, My answer is maybe yes...but I'd

Re: 1st Level of in-rack sprinklers location

2009-01-05 Thread Todd Williams
We all know that nothing ever falls out and that stuff never collects in empty spaces under things, does it? At 11:42 AM 1/5/2009, you wrote: If you room for another foot, I'll toss out a thought We have a high level of assurance that stuff will not be located on the floor (that pesky

Re: test

2009-01-05 Thread Todd Williams
500 gpm on the first and 250 gpm on each of the other three, totaling 1250 gpm. What do I win? At 08:53 AM 1/5/2009, you wrote: 1,2,3,4. ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical

Re[2]: Sidewall Sprinklers

2009-01-05 Thread Todd Williams
Charles, That sounds like a project that I would get called on. Thanks for handling this one. I would suggest an open head deluge system and with the right lighting, you could get rainbows (sprinkler bows?). Todd At 05:27 PM 1/5/2009, you wrote: Hello Craig, I have an AHJ that suggested

RE: another fire - this will be interesting

2009-01-06 Thread Todd Williams
Not to digress from a digression, but here is an follow up article on the original intent of this post.http://www.nhregister.com/articles/2009/01/06/news/valley/b1-shschoolupgrades.txt. (Alice? You remember Alice? This is a song about Alice.) Todd G. Williams, PE Fire Protection

RE: The Engineering Problem (RE: another fire - this will be interesting)

2009-01-06 Thread Todd Williams
Steve, You make a good point, but I don't see the Contractor's (at least up here) willing to take on incompetent PEs. Most of the smaller shops don't have the time to devote to doing the documentation to file a grievance and what benefit would they gain? It may be good for the industry as a

Re: 13R Tank/Pump Piping

2009-01-07 Thread Todd Williams
Bobby, I'm not sure what there is for specific guidance. What I usually try to do is keep all of the suction pipe the same size (or larger, if distance is an issue) as the pump suction. I also like to valve each tank so if a problem develops, then you can isolate the tank and keep the system

Re: Tracking down dry system leaks

2009-01-07 Thread Todd Williams
Pump wintergreen extract in the system and smell for leaks? Could be a problem in buried pipe, though. At 10:09 AM 1/7/2009, you wrote: Any tips on tracking down leaks that are buried in insulation and enclosed in wall and ceilings? We suspect the system isn't sloped properly and doesn't

RE: another fire - this will be interesting

2009-01-07 Thread Todd Williams
I would like to see equal treatment; the HVAC engineers should show a hatch pattern on the floor plan with a note that says deign ductwork to provide a comfortable environment.. I like it! I may have to use that (with proper credit, of course) at a couple of job meetings. I like to things

RE: Apartment Building

2009-01-08 Thread Todd Williams
I always include hose on that type of system (unless it is an impounded water supply with no connections) At 01:47 AM 1/8/2009, you wrote: Watch out! I don't think you can delete hose allowance for the parkade, as it is included in the design criteria for 13. Anyway, I have always included

RE: Apartment Building

2009-01-08 Thread Todd Williams
you include 750 GPM hose on ESFR? glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Thursday, January 08, 2009 7:07 AM To: sprinklerforum@firesprinkler.org Subject: RE: Apartment Building

RE: Apartment Building

2009-01-08 Thread Todd Williams
The original post was a generic question. We do not know the nature of the construction, how the building is classified under the applicable Codes, nor the rating of the separation between the two occupancies. Does the Code consider it entirely considered a Group R or is it a mix of R and S-1?

Re: FW: The Engineering Problem

2009-01-09 Thread Todd Williams
In MA the plans and calcs are required for building permit, but not necessarily in CT. Dots and lines on an outdated floor plan will suffice for that phase and the rest can come when the mechanical permit is required. Hey, but at least MA has the discipline right on their stamp; I wish all

RE: Apartment Building

2009-01-09 Thread Todd Williams
I may have started or at least participated in that post. One situation I ran into a while back was a two story motel with an open parking area underneath. I believe that the local AHJ allowed 13R above, but wanted the full 13 below. Besides, given the water supply, there was not going to be

RE: Plan rights

2009-01-09 Thread Todd Williams
There is a big difference between public record and drawing ownership. You can check a book out of the library, but it doesn't mean you can sell the movie rights. At 11:33 AM 1/9/2009, you wrote: Yes they are part of a public record, and as such you must provide copies on request. You do

Re: Packaging of explosives

2009-01-12 Thread Todd Williams
Bobby, This is some serious stuff they are playing with. NFPA has several standards that deal with explosion hazards and related materials. Also, if the Gov't has a hand in it (even as a client), then they have their own standards for protecting this stuff. There should be a qualified FPE

Re: piping through joist

2009-01-12 Thread Todd Williams
Travis, Send me your fax number. I have a drawing I created a few years back. Todd At 06:00 PM 1/12/2009, you wrote: Does anyone have a moderately accurate formula for determining the longest length of pipe I can fit in a joist space. The project in question has 24 deep joists at 5' on

RE: Sprinklered vs Sprinkled

2009-01-15 Thread Todd Williams
How about Automatic Sprinklers vs. Fire Sprinklers? At 09:07 AM 1/15/2009, you wrote: Content-class: urn:content-classes:message Content-Type: text/plain; charset=utf-8 Yes, I have heard it many times here in Virginia, and always find it amusing. Paul Pinigis, P.E. Life Safety

RE: Sprinklered vs. Sprinkled

2009-01-15 Thread Todd Williams
We also tend to use 'sprinkler' as a transitive verb (Did you sprinkler the office area?). Neither 'sprinklered' or sprinklering' showed up in any of my dictionary references. Of course, how many times have you heard 'Are you going to sprinkle the office area?' At 11:31 AM 1/15/2009, you

Re: Sprinklered vs. Sprinkled

2009-01-15 Thread Todd Williams
Be judicious in your verbifications. You may find yourself in an untenable verbifunistic situation wherein verbaforms begin to talk on a nounistic rather than a solid verbistian aspect. Said like a true spec writer Todd G. Williams, PE Fire Protection Design/Consulting Stonington,

Re: Boat Storage

2009-01-15 Thread Todd Williams
Russell, I assume you mean rack storage of boats. I have a friend in that is involved with that business and according to him, no. (He asked to to do some consulting on this issue, but when I listed all of the problems and considerations, the offer mysteriously disappeared.) I haven't seen

Re: Firematic

2009-01-15 Thread Todd Williams
I think that is the only Model A data sheet I don't have in my Firematic catalog. Good find. I didn't know that they got much play on the other coast. At 06:15 PM 1/15/2009, you wrote: I was putting our Firetrol pump controller catalog back in its place on the shelf in our library, when I

RE: Boat Storage

2009-01-15 Thread Todd Williams
Does anybody know where I could find a copy of Ken's article? I'd be interested. At 03:53 PM 1/15/2009, you wrote: http://www.mail-archive.com/sprinklerforum@firesprinkler.org/msg04310.html Follow this thread. Thanks Mark. I could not remember where that article was. Russell, I spent alot

Re: Salt Water In Sprinkler System

2009-01-16 Thread Todd Williams
Salt water is a non-potable water source, so all of those rules, such as return bends or dry pendents, would apply. Also, salt water has a different density (64 #/cuft vs. 62.4 #/cuft) so Hazen-Williams does not apply. You should use a program with Darcy-Weisbach. (I designed a system for a

RE: Salt Water In Sprinkler System

2009-01-18 Thread Todd Williams
Tom, If that is the old plant in RI in the upper part of the bay, I did a small job there years ago. Stayed away from the pump, however. (I think it is actually half way between you and me.) When I was with FM, I did a number of pump tests at the mills around Fall River and New Bedford

design criteria for canopies

2009-01-18 Thread Todd Williams
I am working on a hardware store which will have a canopy going across the front and down one side. The canopy itself is non combustible, but there may be product outside for display, so it needs to be sprinklered (8.14.7.4). The product could include a couple of wheelbarrows, bags of ice

RE: ***SPAMTAGPTD: Re: FDC

2009-01-19 Thread Todd Williams
I use it and I'm not an ASCOA guy (but I think I learned it from one). It's also nice to see another former Insomniac Sprinkler Corp guy up an at 'em At 04:49 AM 1/19/2009, you wrote: Nice to see someone else use appurtenances. I thought use of that wsa limited to ASCOA alum. W

Re: Americas Funniest Videos 1-18-09

2009-01-19 Thread Todd Williams
I bet that sucker on page 68 of FPC would do something. At 12:52 PM 1/19/2009, you wrote: What kind of head guard do do you think will stop a bowling ball? --Original Message-- From: Chris Cahill Sender: sprinklerforum-boun...@firesprinkler.org To: sprinklerforum@firesprinkler.org

RE: Re[2]: Old Escutcheons and replacing them

2009-01-20 Thread Todd Williams
Let me play devil's advocate (or be my typical pain in the butt). According to NFPA 13 (2002) 6.2.7.1 Nonmetallic escutcheons shall be listed 6.2.7.2, Escutcheons used with recessed, flush-type or concealed sprinklers shall be part of a listed sprinkler assembly So, If the escutcheon is

Re: 1.2 Leg of Remote Area

2009-01-20 Thread Todd Williams
I'm a little confused by your explanation, but let me try and describe as I see it. In situations with long enough branch lines, 22.4.4.1.1.1 would apply, which is the 1.2X rule. If the branch lines are not sufficiently long to meet the 1.2X rule, then section 22.4.4.1.1.3 would apply. In both

RE: 1.2 Leg of Remote Area

2009-01-21 Thread Todd Williams
If I ever get around to finishing my web site, I am going to have a Rogue's Gallery, but that will be just photos. Maybe someone could do a monthly Top 10 stupid sprinkler tricks At 05:25 AM 1/21/2009, you wrote: But hpw could you resist? LOL Perhaps FPC, Spkr Age, Or SQ should collect war

Re: Hodgman Sprinklers

2009-01-21 Thread Todd Williams
I think they were bought out by Globe many years ago. Also, try www.firespec.com. They were involved at one point. At 05:05 PM 1/21/2009, you wrote: Does anybody know where one can find any information (spec's, data sheets, etc.) on Hodgman sprinklers? Bobby Gillett Sr. Project Manager

RE: Boat Storage

2009-01-21 Thread Todd Williams
And hey if it's properly sprinklered (to an extent) fire protection engineering is a marginal concern. Curious comment. Care to expand on that? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080

water test location

2009-01-23 Thread Todd Williams
I did a flow test a couple of days ago on an underground main that had recently been looped. There is a main that feeds a hydrant and sprinklers to the building at the end of the loop. I flowed the hydrant and read the pressures off the first test port on the backflow preventer (before any

RE: water test location

2009-01-23 Thread Todd Williams
with the contractor. Your scenario is like a dead end main with your gauge on the last hydrant if I am interpreting it correctly. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Friday

RE: water test location

2009-01-23 Thread Todd Williams
Per edition 5 of the American Mutual Insurance Alliance Simplified water supply testing In testing a water system at a sprinklered plant, sometimes we can note the residual pressure from a gauge at the base of the nearest riser. This is not recommended as standard practice, but may be used when

RE: water test location

2009-01-24 Thread Todd Williams
That is exactly how I learned it. I didn't stay at a Holiday Inn Express, but I did sleep in my car in the parking lot. Does that count? At 10:07 PM 1/23/2009, you wrote: When taking the static/residual reading from a sprinkler riser, I think the effective point (the point the calcs should be

RE: Threat to the 2009 IRC

2009-01-26 Thread Todd Williams
and Mark is sticking pins in his PE voodoo dolls. Maybe that explains the pain in my right shoulder Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 ___ Sprinklerforum mailing

Re: Tampa Landmark Saved from Suspected Arson by Sprinklers and Firefighters

2009-01-28 Thread Todd Williams
Steve, they didn't say when it was re-opening. Keep us informed. (That was actually the only response I could come up with that wouldn't get me thrown off the Forum). I like how the article included a Google map so you could get directions. I wonder if this will show up in Success Stories in

Re: Fire Hydrant Butts

2009-01-28 Thread Todd Williams
You can probably get adapters. But be sure to check the thread type. At 02:38 PM 1/28/2009, you wrote: Anyone ever seen a fire hydrant with 2 hose butts rather than the most common 2-1/2? I need a cap in order to perform a flow test. Russell Rewis Brown Automatic Sprinklers, Inc. 107C

Re: AZ Bill - News

2009-01-29 Thread Todd Williams
There are a couple of issues with the CT bill that Terri forwarded to me (such as the referenced subsection does not exist). I will post more when I know more. However, the particular section references energy modifications to existing buildings and says nothing of sprinklers. At 02:27 PM

Re: Strange Request - Book Info.

2009-01-30 Thread Todd Williams
I'm not sure when the first handbook was printed, but Bob Hodnett was the editor. try www.isbndb.com. You might be able to find the numbers in there At 08:49 AM 1/30/2009, you wrote: Good morning all, Strange request here . I'm in the process of backfilling my library with older

Hospital standpipe

2009-02-03 Thread Todd Williams
I am working with local 5-story hospital that has an existing Class II standpipe. If this was being built as a new structure, there would be a Class I or III installed. Is there any reason why the standpipe system would need to be upgraded? (We are doing a water supply upgrade and would need

RE: Hospital standpipe - update

2009-02-03 Thread Todd Williams
...@firesprinkler.org] On Behalf Of Todd Williams Sent: Tuesday, February 03, 2009 1:36 PM To: sprinklerforum@firesprinkler.org Subject: RE: Hospital standpipe - update John, The hospital is in CT and the Codes up here are vague. Update - I walked the whole facility for the first time this morning

RE: Hospital standpipe - update

2009-02-03 Thread Todd Williams
? John Drucker Fire Protection Subcode Official Red Bank, NJ 07701 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Tuesday, February 03, 2009 8:39 AM To: sprinklerforum@firesprinkler.org

quote of the day

2009-02-04 Thread Todd Williams
This comes from a member of the Shelton, CT High School Building Committee in an article on why sprinklers weren't installed as part of the recent renovation. (This was as a result of a well publicized fire around Christmas): Installing sprinklers involves running water pipes through the

RE: quote of the day

2009-02-04 Thread Todd Williams
A pulse.. At 09:26 AM 2/4/2009, you wrote: What are the qualifications to be a member of the building committee ? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Wednesday

MRI

2009-02-04 Thread Todd Williams
Where can I find some information regarding protection of an MRI space? Most of the installations have seen or designed are pre-action systems. I am now looking at one with a regular wet system with a valve and dielectric coupling. Are there any issues with water-filled pipe? Todd G.

Re: MRI

2009-02-04 Thread Todd Williams
...@firesprinkler.org] On Behalf Of Todd Williams Sent: Wednesday, February 04, 2009 9:55 AM To: sprinklerforum@firesprinkler.org Subject: MRI Where can I find some information regarding protection of an MRI space? Most of the installations have seen or designed are pre-action systems. I am now looking

Re: Evedence Room

2009-02-04 Thread Todd Williams
Chris, You need to look at this just like any other storage occupancy. It can also depend on where you are. An Evidence Room in Los Angeles could be very different than one in East Wazoo. Is this for current cases or archival storage? Shelves? Racks? How high? If your storage is less than 12

Re: Evedence Room

2009-02-04 Thread Todd Williams
a seized crack lab is, when placed in an evidence room? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Wednesday, February 04, 2009 4:59 PM To: sprinklerforum@firesprinkler.org

Re: IFC vs NFPA 13 issue

2009-02-05 Thread Todd Williams
Code is regulation; Standard is guideline. Standard can be adopted by Code and modified as the jurisdiction desires At 12:54 PM 2/5/2009, you wrote: dumb, really dumb question, but is not the IFC more of a maintenance code and the IBC the new construction code? if the IFC applies to this

Re: Bedbug Treatment

2009-02-06 Thread Todd Williams
If you read the commentary in the Handbook (NFPA 13-2002) under section 6.1.2.2, that seems to open up the idea of removing and replacing sprinklers in limited applications, to which this might apply. Also, if you remove the sprig/drop/arm over and replace it, but do not touch the sprinkler,

RE: CEILING CLOUDS - AGAIN

2009-02-06 Thread Todd Williams
Steve, I'm not sure I agree. Aside from what the book says, I look at this type of situation and I have a couple issues with it. Sprinklers at the deck are typically uprights directly off a branch line (or perhaps a short sprig). The pendent sprinklers may be fed by swing joints or flexible

Re: remodel and deficiencies in existing system

2009-02-07 Thread Todd Williams
Protection Design Consulting San Diego, CA -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Friday, February 06, 2009 4:29 PM To: sprinklerforum@firesprinkler.org Subject: RE: CEILING CLOUDS

RE: 13R ATTIC Protection

2009-02-09 Thread Todd Williams
Steve, Sprinklering the attic is not always voluntary. Some jurisdictions are requiring it At 11:49 AM 2/9/2009, you wrote: Right - I mean to say that if you VOLUNTARILY sprinkler the attic, as you might to satisfy the draft-stopping and compartmentalization provisions of the building

RE: Information regarding Beijing's The Mandarin Oriental Hotel fire

2009-02-11 Thread Todd Williams
I wonder if they were using bamboo scaffolding. Could cause a fire to spread down At 09:38 AM 2/11/2009, you wrote: Chris, See this video http://www.ireport.com/docs/DOC-210388 In this video (and some others) there is a small fire atop the building. Smitty -Original Message-

Re: Wooden Tanks

2009-02-12 Thread Todd Williams
It comes from barrel making (coopering). I believe croze is the notch cut in the wooden staves to hold the hoops. I think the chime to the top hoop on the barrel. At 02:55 PM 2/12/2009, you wrote: In reviewing chapter 8 of NFPA 22, Water Tanks, there are two terms that I am not familiar

RE: water source heat pumps

2009-02-13 Thread Todd Williams
What is the construction of the space? Are there exposed wood joists? Other combustible loading? Does the hatch allow a person into the space or would all work on the heat pumps have to be reaching through the opening? If it is an unaccessible, N/C space, would 8.14.1.2.2 (2002) apply? At

Re: you be the engineer here

2009-02-13 Thread Todd Williams
It is tough to tell without specifics, but I will throw out an idea. Perhaps some combination of Novec (or something similar) in large equipment cabinets and server rooms and a pre-action system for the entire space. Depending on the height and design of the tower, evacuation may be a

Re: conveyors

2009-02-14 Thread Todd Williams
are not part of a continuous rated shaft how could you justify penetrations through the floors? On Fri, Feb 13, 2009 at 2:06 PM, Todd Williams t...@fpdc.com wrote: What is the construction of the space? Are there exposed wood joists? Other combustible loading? Does the hatch allow a person into the space

Re: leak statistic

2009-02-18 Thread Todd Williams
OK, using algebra, (don't know)/(don't know) = 1. Since the question of how often leaks occur only comes up when a leak occurs and the answer is 1, could this then be the source of the inevitable answer this has never happened before? At 09:51 AM 2/18/2009, you wrote: Do not believe or

Re: Unlisted pumps

2009-02-19 Thread Todd Williams
So if we install a pump in a separate pump house, we don't have to satisfy NFPA 20? Call you competition and tell them you have a job they might be interested in. At 11:19 AM 2/19/2009, you wrote: The owner has two tanks outside the NFPA 13 building, buried in the ground. He wants to

RE: Residential systems in California

2009-02-20 Thread Todd Williams
Are plumbing designers going to start doing hydraulic calculations? At 11:09 AM 2/20/2009, you wrote: Never mind raising eyebrows, how is our industry going to find the thousands of design tech's and literally dozens of thousands of installers necessary to serve this market? Plumbing

Re: Residential systems in California

2009-02-20 Thread Todd Williams
. It's just math, right? Didn't Bernie Madoff say that? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 ___ Sprinklerforum mailing list

RE: Residential systems in California

2009-02-20 Thread Todd Williams
Good luck. The biggest one I can find on the shelf out here is 50' x 100'. At 06:16 PM 2/20/2009, you wrote: I'VE REQUESTD MY 1.6 Billon of TARP, and am just waiting for the check. When it comes I'll buy pie for all of you! Happy weekend! Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge