RE: [EXTERNAL] RE: Sprinklerforum Digest, Vol 83, Issue 6

2020-02-27 Thread Anthony C via Sprinklerforum
: RE: [EXTERNAL] RE: Sprinklerforum Digest, Vol 83, Issue 6 You can't use that head on a pre-action system, can you? -Kyle M -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Anthony C via Sprinklerforum Sent: Thursday, February 27

RE: Misc. Storage

2020-01-30 Thread Anthony C via Sprinklerforum
Gentlemen Another thing to look at is the height of the building above the storage, this height wasn’t mentioned in the original post and may not be an issue but should be looked at, See NFPA 13-12.1.3.4 Clearance to ceiling. Specific to your commodity would be section 12.1.3.4.4 -12.1.3.4.5

RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Anthony C via Sprinklerforum
The only reference to clearance is for structural members NFPA 13 – 2016 edition: 9.3.4.9 The installed horizontal and upward vertical clearance between horizontal sprinkler piping and structural members not penetrated or used, collectively or independently, to support the piping shall be

RE: [EXTERNAL] RE: Panel Construction

2019-12-20 Thread Anthony C via Sprinklerforum
Here is what NFPA 13 -2019 edition states: 3.3.41.2* Unobstructed Construction. Construction where beams, trusses, or other members do not impede heat flow or water distribution in a manner that materially affects the ability of sprinklers to control or suppress a fire. Unobstruc‐ ted

RE: [EXTERNAL] RE: Panel Construction

2019-12-20 Thread Anthony C via Sprinklerforum
Did you all notice what the appendix to 3.7.1 Definition of Panel construction. A.3.7.1 Obstructed Construction. The following examples of obstructed construction are provided to assist the user in determining the type of construction feature: (4) Panel Construction. The term panel