RE: IBC and Breezeways

2011-04-06 Thread Chappell, Carl
For a typical breezeway my opinion would be to provide sprinklers. A building as defined and addressed by the IBC area areas for any use or occupancy. Very vague and general. Using this may be a bit of a stretch. So my argument would be that a building is comprised of building area. As

RE: IBC and Breezeways

2011-04-06 Thread Chappell, Carl
] On Behalf Of Chappell, Carl Sent: Wednesday, April 06, 2011 4:50 PM To: sprinklerforum@firesprinkler.org Subject: RE: IBC and Breezeways For a typical breezeway my opinion would be to provide sprinklers. A building as defined and addressed by the IBC area areas for any use or occupancy. Very vague

RE: Hydraulic Calcs

2011-01-18 Thread Chappell, Carl
You could probably get there in a roundabout way. Such as Section 907.2.12 requires a high rise building to be provided with an automatic fire alarm system and emergency voice / alarm communication system. The emergency voice / alarm communication system requires a general alarm or stage

RE: UFC 3-600-1 Fire Flow

2011-01-18 Thread Chappell, Carl
Section 3-1.4 of UFC3-600-1 is for the Total Water Demand for Sprinklered Occupancies. The total water demand for sprinklered occupancies is equal to the sum of the domestic/industrial demand plus the sprinkler system(s) water demand and the hose stream(s) demand. The total demand must be

RE: USACE Velocity

2010-12-29 Thread Chappell, Carl
FM Global does have requirements on the friction loss equations that are to be used when the velocity exceeds a certain criteria. For FM systems, the use of Darcy-Weisbach is required if the velocity exceeds 30 ft/s; otherwise Hazen-Williams is the acceptable method for anything below 30 ft/s.

RE: Pool as a water source

2010-09-24 Thread Chappell, Carl
There is a federal mandate out there that restricts the velocity of the water at the suction point. This is supposedly due to a kid being drowned by such an incident. In the past we had to create multiple suction points that tie back into the single supply pipe to get the velocities down to

RE: Pool as a water source

2010-09-24 Thread Chappell, Carl
Here is a document I found on a quick internet search. Carl Chappell -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise Sent: Friday, September 24, 2010 7:29 AM To:

RE: limits on velocity

2010-06-25 Thread Chappell, Carl
The following two definitions are contained within the FM Data Sheets. As far as I know, the reasoning behind the 32 fps restriction was that it equates to the difference between turbulent and laminar flow of fluids (in this case water) through a piping network. The accuracy of the Hazen

FW: CPVC

2009-03-31 Thread Chappell, Carl
Does anyone have any information regarding the request below? Thanks in advance. Carl Chappell From: Chris Brown [mailto:cbr...@certifiedlifesafety.com] Sent: Tuesday, March 31, 2009 3:45 PM To: Chappell, Carl Subject: CPVC Carl, Can you

RE: Mixed-Use Code Question

2009-03-13 Thread Chappell, Carl
There are a few design directions the project may go. One option is to identify it as a separated mixed-use building, which requires fire-rated separations between occupancy types and incidental use areas. A second option is non-separated mixed use where the architect / engineer need to verify

Temperature Ratings

2009-03-06 Thread Chappell, Carl
I know that I should be able to find this, but I am having trouble locating a section in NFPA 13 (2002 or 2007 Editions) that states the temperature ratings of sprinklers are required to be the same throughout the protected space unless the items listed in Section 8.3.2.5 apply. Could someone

PE Peer Review

2009-02-26 Thread Chappell, Carl
Everyone, As an individual who has performed plan reviews for the company recently being discussed on this forum (and will be gaining PE licensure this year), I have to respectfully disagree that all we do is put fluff and filler in a plan review and get paid by the word or word count. Why would

RE: Fire stop assemblies

2008-03-03 Thread Chappell, Carl
Steve, We like to look at the different manufacturers and have their engineering department make the engineering judgments when there is not a known rated assembly. Examples of these are Hilti and 3M. Carl Chappell -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL

RE: Sprinkler Zones for Horizontal Exit Building

2008-02-01 Thread Chappell, Carl
From what we have experienced, the intent of the horizontal exit is to be supplemental to the stairs and other egress components. However, as currently done the horizontal exit also acts as an audible zone boundary. This implies that the notification appliances connected to the fire alarm system

RE: Sprinkler Zones for Horizontal Exit Building

2008-02-01 Thread Chappell, Carl
Martinez CA 94553 925-228-8792 [EMAIL PROTECTED] - Original Message From: Chappell, Carl [EMAIL PROTECTED] To: sprinklerforum@firesprinkler.org Sent: Friday, February 1, 2008 2:46:36 PM Subject: RE: Sprinkler Zones for Horizontal Exit Building From what we have experienced, the intent

RE: Max Ceiling Heights

2008-01-29 Thread Chappell, Carl
What we deal with here in Las Vegas are the local amendments to the codes and NFPA 13. When a ceiling height is between 25 and 50 feet above the floor below quick-response sprinklers with a minimum K-factor of 11.2 is required. Once a ceiling height exceeds 50 feet a fire protection engineer has

Spray Pattern Obstructions

2008-01-02 Thread Chappell, Carl
I have a question for the group. If you have an object in the horizontal plane below the ceiling sprinklers (adhering to the 18-inch clearance requirement) that is less than 48-inches wide, what is the general practice of spacing between these objects? Is it a separation distance of equal to or

RE: Atrium

2007-12-27 Thread Chappell, Carl
I believe part of the answer lies in whether or not this space is a true atrium. If it meets the definition of an atrium then the fuel loading on the floor of the space is limited to low hazard uses and only approved materials and decorations. There is an exception within the code, that

RE: 2006 IBC changes

2007-12-19 Thread Chappell, Carl
Rod, There are some changes to the 2006 IBC sprinkler requirements. They mainly relate to telecommunications buildings. Otherwise the code is essentially the same as the 2003 IBC. In regards to your high-rise, the basic rules are the same. However, I would check to see if the jurisdiction also

RE: Floor control valve heights

2007-01-29 Thread Chappell, Carl
Ed, Here in Vegas we do things that may not be done elsewhere. The International Building Code requires a minimum headroom be maintained throughout the stair and landing. The minimum headroom is 80 inches. If you keep the control valve above this height (allowing that you have the space needed)