For a typical breezeway my opinion would be to provide sprinklers. A building
as defined and addressed by the IBC area areas for any use or occupancy. Very
vague and general. Using this may be a bit of a stretch. So my argument would
be that a building is comprised of building area. As
] On Behalf Of Chappell, Carl
Sent: Wednesday, April 06, 2011 4:50 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: IBC and Breezeways
For a typical breezeway my opinion would be to provide sprinklers. A building
as defined and addressed by the IBC area areas for any use or occupancy. Very
vague
You could probably get there in a roundabout way. Such as Section 907.2.12
requires a high rise building to be provided with an automatic fire alarm
system and emergency voice / alarm communication system. The emergency voice /
alarm communication system requires a general alarm or stage
Section 3-1.4 of UFC3-600-1 is for the Total Water Demand for Sprinklered
Occupancies. The total water demand for sprinklered occupancies is equal to
the sum of the domestic/industrial demand plus the sprinkler system(s) water
demand and the hose stream(s) demand. The total demand must be
FM Global does have requirements on the friction loss equations that are to be
used when the velocity exceeds a certain criteria. For FM systems, the use of
Darcy-Weisbach is required if the velocity exceeds 30 ft/s; otherwise
Hazen-Williams is the acceptable method for anything below 30 ft/s.
There is a federal mandate out there that restricts the velocity of the water
at the suction point. This is supposedly due to a kid being drowned by such an
incident. In the past we had to create multiple suction points that tie back
into the single supply pipe to get the velocities down to
Here is a document I found on a quick internet search.
Carl Chappell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Friday, September 24, 2010 7:29 AM
To:
The following two definitions are contained within the FM Data Sheets. As far
as I know, the reasoning behind the 32 fps restriction was that it equates to
the difference between turbulent and laminar flow of fluids (in this case
water) through a piping network. The accuracy of the Hazen
Does anyone have any information regarding the request below? Thanks in
advance.
Carl Chappell
From: Chris Brown [mailto:cbr...@certifiedlifesafety.com]
Sent: Tuesday, March 31, 2009 3:45 PM
To: Chappell, Carl
Subject: CPVC
Carl,
Can you
There are a few design directions the project may go. One option is to
identify it as a separated mixed-use building, which requires fire-rated
separations between occupancy types and incidental use areas. A second
option is non-separated mixed use where the architect / engineer need to
verify
I know that I should be able to find this, but I am having trouble
locating a section in NFPA 13 (2002 or 2007 Editions) that states the
temperature ratings of sprinklers are required to be the same throughout
the protected space unless the items listed in Section 8.3.2.5 apply.
Could someone
Everyone,
As an individual who has performed plan reviews for the company recently
being discussed on this forum (and will be gaining PE licensure this
year), I have to respectfully disagree that all we do is put fluff and
filler in a plan review and get paid by the word or word count. Why
would
Steve,
We like to look at the different manufacturers and have their
engineering department make the engineering judgments when there is not
a known rated assembly. Examples of these are Hilti and 3M.
Carl Chappell
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL
From what we have experienced, the intent of the horizontal exit is to
be supplemental to the stairs and other egress components. However, as
currently done the horizontal exit also acts as an audible zone
boundary. This implies that the notification appliances connected to
the fire alarm system
Martinez CA 94553
925-228-8792
[EMAIL PROTECTED]
- Original Message
From: Chappell, Carl [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Friday, February 1, 2008 2:46:36 PM
Subject: RE: Sprinkler Zones for Horizontal Exit Building
From what we have experienced, the intent
What we deal with here in Las Vegas are the local amendments to the
codes and NFPA 13. When a ceiling height is between 25 and 50 feet
above the floor below quick-response sprinklers with a minimum K-factor
of 11.2 is required. Once a ceiling height exceeds 50 feet a fire
protection engineer has
I have a question for the group. If you have an object in the
horizontal plane below the ceiling sprinklers (adhering to the 18-inch
clearance requirement) that is less than 48-inches wide, what is the
general practice of spacing between these objects? Is it a separation
distance of equal to or
I believe part of the answer lies in whether or not this space is a true
atrium. If it meets the definition of an atrium then the fuel loading
on the floor of the space is limited to low hazard uses and only
approved materials and decorations. There is an exception within the
code, that
Rod,
There are some changes to the 2006 IBC sprinkler requirements. They
mainly relate to telecommunications buildings. Otherwise the code is
essentially the same as the 2003 IBC. In regards to your high-rise, the
basic rules are the same. However, I would check to see if the
jurisdiction also
Ed,
Here in Vegas we do things that may not be done elsewhere. The
International Building Code requires a minimum headroom be maintained
throughout the stair and landing. The minimum headroom is 80 inches.
If you keep the control valve above this height (allowing that you have
the space needed)