13R pump listing

2012-08-09 Thread Rod DiBona
It is my understanding that any pump used for 13R must be per NFPA 20. It has come to my attention that one of our competitors is using a model made by Talco Fire Systems. www.talcofiresystems.comhttp://www.talcofiresystems.com The salesmen told my estimator that all of the pieces are

RE: 13R pump listing

2012-08-09 Thread G. Tim Stone
- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum- boun...@firesprinkler.org] On Behalf Of Rod DiBona Sent: Thursday, August 09, 2012 3:38 PM To: sprinklerforum@firesprinkler.org Subject: 13R pump listing It is my understanding that any pump used for 13R must be per NFPA

RE: 13R pump listing

2012-08-09 Thread Steve Leyton
: Thursday, August 09, 2012 12:59 PM To: sprinklerforum@firesprinkler.org Subject: RE: 13R pump listing Rod, Read NFPA 13R, (2010 ed.) 9.3 Source, (4) A stored water source with an automatically operated pump. Notice it does not state Fire Pump. 9.4 says that where a fire pump is installed

RE: 13R pump listing

2012-08-09 Thread Matsuda, Richard
inspection dept -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of G. Tim Stone Sent: Thursday, August 09, 2012 2:59 PM To: sprinklerforum@firesprinkler.org Subject: RE: 13R pump listing Rod, Read NFPA 13R, (2010 ed

RE: 13R pump listing

2012-08-09 Thread Steve Leyton
Sent: Thursday, August 09, 2012 1:18 PM To: sprinklerforum@firesprinkler.org Subject: RE: 13R pump listing This is what I thought about the stored water supply...so now I have a question that's bothered me ever since NFPA-13R put in the requirement for a listed fire pump installed per NFPA-20. NFPA

RE: 13R pump listing

2012-08-09 Thread Rod DiBona
...@firesprinkler.org] On Behalf Of Steve Leyton Sent: Thursday, August 09, 2012 2:29 PM To: sprinklerforum@firesprinkler.org Subject: RE: 13R pump listing Correct, as I said in last email and as Tim points out with regard to said pump having to be of a type that is automatically operated. Yes, the pump will have

RE: 13R pump listing

2012-08-09 Thread Tom Duross
...@firesprinkler.org] On Behalf Of Rod DiBona Sent: Thursday, August 09, 2012 5:03 PM To: sprinklerforum@firesprinkler.org Cc: Jared Wilson Subject: RE: 13R pump listing Thank you Steve and Tim for your response. Frustrating to see a manufacturer selling all over the country an unlisted 13R pump

RE: 13R pump listing

2012-08-09 Thread Steve Leyton
Zachary. SML -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross Sent: Thursday, August 09, 2012 2:48 PM To: sprinklerforum@firesprinkler.org Subject: RE: 13R pump listing FWIW- For my money, I'd

Re: 13R pump listing

2012-08-09 Thread George Church
To: sprinklerforum@firesprinkler.org Subject: RE: 13R pump listing Correct, as I said in last email and as Tim points out with regard to said pump having to be of a type that is automatically operated. Yes, the pump will have to be sized for both domestic and fire sprinkler demands, whichever

RE: 13R pump listing

2012-08-09 Thread Rod DiBona
@firesprinkler.org Subject: Re: 13R pump listing Rod, Go back and read Tim's citation. 2007 is our PA adopted version. In it, no reason non-22 tanks store FP water to unlisted pump from Lowes to 13R system with no connection to domestic. Don't have to like it, can change it in a later edition, but until PA