It is my understanding that any pump used for 13R must be per NFPA 20. It has
come to my attention that one of our competitors is using a model made by Talco
Fire Systems. www.talcofiresystems.comhttp://www.talcofiresystems.com
The salesmen told my estimator that all of the pieces are
-
From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
boun...@firesprinkler.org] On Behalf Of Rod DiBona
Sent: Thursday, August 09, 2012 3:38 PM
To: sprinklerforum@firesprinkler.org
Subject: 13R pump listing
It is my understanding that any pump used for 13R must be per NFPA
: Thursday, August 09, 2012 12:59 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R pump listing
Rod,
Read NFPA 13R, (2010 ed.) 9.3 Source, (4) A stored water source with an
automatically operated pump. Notice it does not state Fire Pump.
9.4 says that where a fire pump is installed
inspection dept
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of G. Tim
Stone
Sent: Thursday, August 09, 2012 2:59 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R pump listing
Rod,
Read NFPA 13R, (2010 ed
Sent: Thursday, August 09, 2012 1:18 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R pump listing
This is what I thought about the stored water supply...so now I have a
question that's bothered me ever since NFPA-13R put in the requirement
for a listed fire pump installed per NFPA-20.
NFPA
...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, August 09, 2012 2:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R pump listing
Correct, as I said in last email and as Tim points out with regard to
said pump having to be of a type that is automatically operated. Yes,
the pump will have
...@firesprinkler.org] On Behalf Of Rod DiBona
Sent: Thursday, August 09, 2012 5:03 PM
To: sprinklerforum@firesprinkler.org
Cc: Jared Wilson
Subject: RE: 13R pump listing
Thank you Steve and Tim for your response. Frustrating to see a manufacturer
selling all over the country an unlisted 13R pump
Zachary.
SML
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom
Duross
Sent: Thursday, August 09, 2012 2:48 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R pump listing
FWIW- For my money, I'd
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R pump listing
Correct, as I said in last email and as Tim points out with regard to
said pump having to be of a type that is automatically operated. Yes,
the pump will have to be sized for both domestic and fire sprinkler
demands, whichever
@firesprinkler.org
Subject: Re: 13R pump listing
Rod,
Go back and read Tim's citation. 2007 is our PA adopted version. In it, no
reason non-22 tanks store FP water to unlisted pump from Lowes to 13R system
with no connection to domestic. Don't have to like it, can change it in a later
edition, but until PA