RE: FDC Placard

2019-01-04 Thread Tom Duross
and one for the hydraulic design summary (i.e. the “calc card”) per 6.8. I think the FDC placard should state the required inlet pressure in order to make the minimum residual at the most remote outlets per the standard used as a basis of design (pre-1993), but I would VERIFY THAT WITH SERVING FIRE

RE: FDC Placard

2019-01-04 Thread Steve Leyton
There are two signs referenced in NFPA 14 (2016) and methinks they’re being confused here. There’s a sign at the FDC stating the required pressure prescribed by 6.4.5.2.2 and one for the hydraulic design summary (i.e. the “calc card”) per 6.8. I think the FDC placard should state

Re: FDC Placard

2019-01-04 Thread Phillips, Mark
) To: sprinklerforum@lists.firesprinkler.org Subject: FDC Placard Trying this one more time, original never posted.. Did a 5 year Standpipe test on an older (1986) system with its own Fire Pump. Older ’83 BOCA (MA supplements, 14-1976): 500(1st) + 250 (2nd) plus 250 (for sprinklers). 1000 gpm Fire Pump

FDC Placard

2019-01-04 Thread Tom Duross
Trying this one more time, original never posted.. Did a 5 year Standpipe test on an older (1986) system with its own Fire Pump. Older ’83 BOCA (MA supplements, 14-1976): 500(1st) + 250 (2nd) plus 250 (for sprinklers). 1000 gpm Fire Pump in Basement. Owner is asking me to provide a new