There are some exceptions for storage areas that are broken into maybe 500 SF
ax areas being allowed to bbe .05 with resi's, I believe.
eorge L. Church, Jr., CET
owe Sprinkler Systems, Inc.
O Box 407, Middleburg, PA 17842
77-324-ROWE
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
kmick44...@aol.com
Sent: Thursday, September 20, 2012 10:06 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Basements storage in multiple dwellings
thanks G
right now cellar is approx 1200 sf
i'm going to treat it as a separate space use the Rm
Basements that are not used as a dwelling unit in a conforming
residential building are addressed in NFPA 13R, 7.2 Design Criteria -
Outside Dwelling Unit.
The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 13D/13R Technical Committee on
sprinklerforum@firesprinkler.org
Sent: Wed, Sep 19, 2012 11:07 am
Subject: RE: Basements storage in multiple dwellings
Basements that are not used as a dwelling unit in a conforming
esidential building are addressed in NFPA 13R, 7.2 Design Criteria -
utside Dwelling Unit.
The foregoing is my opinion
: Wednesday, September 19, 2012 8:47 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Basements storage in multiple dwellings
Ok
then that leads to nfpa 13 with quick response sprinkler and room design
method @ 0.1 density or could that qualify under the exception
residential fire loading
: Wednesday, September 19, 2012 8:47 AM
o: sprinklerforum@firesprinkler.org
ubject: Re: Basements storage in multiple dwellings
Ok
hen that leads to nfpa 13 with quick response sprinkler and room design
ethod @ 0.1 density or could that qualify under the exception
esidential fire loading of 13R outside