I've been advocating that 13R be rolled into 13D as a special residential
section for years (to an empty room of course) and I'll do the same for 13D
as soon as the concept of sprinklers in SFDs becomes a more or less
accepted idea in the housing industry.
On Fri, Sep 21, 2012 at 5:46 AM, å...
@firesprinkler.org
Subject: RE: Excellent comments from a smart guy
Not to prolong this discussion, but...
Basement Storage in Multi-Residential: According to the Building ode
the common storage area located in the basement of a Group R-2
multi-residential building such as apartments or condos would
...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Friday, September 21, 2012 5:01 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Excellent comments from a smart guy
Not to prolong the prolongation but ...
Galen's comments were based in part on CA
WHATEVER!
SML
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Friday, September 21, 2012 2:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Excellent comments from a smart guy
But what about treating it as a mixed use, NONSEPARATED ocupancies.
As such, no separation and since 903.2.9 does not require the S-1 to
be sprinklered (unless larger than 12,000 sf) NFPA 13 is not required
but with 903.2.8 requiring the residential portion to be sprinklered
(and 508.3.1
thanks
-Original Message-
From: Steve Leyton st...@protectiondesign.com
To: sprinklerforum sprinklerforum@firesprinkler.org
Sent: Wed, Sep 19, 2012 2:18 pm
Subject: Excellent comments from a smart guy
Forumites:
A fire official here in SoCal asked me to forward his comments on