...@firesprinkler.org] On Behalf Of Tom Duross
Sent: Tuesday, October 02, 2012 7:16 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Pump on vibration spring type isolators
It was the thirty minute run once a week from an engine that was the
concern.
-Original Message-
From
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Monday, October 01, 2012 7:01 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Pump on vibration spring type isolators
How'd that diesel work-out on sound reduction Tom? ...and painted it red
for fire protection
Of course, the one question that hasn't been asked is Why? Normally,
mechanical equipment is placed on isolators to reduce noise and vibration. Why?
Because the equipment runs periodically or often during the day and can be
disruptive to the building occupants if noise is not abated. How often
I'm grasping the idea of wanting to prevention the transmission of vibration
and such when the pump is mounted above an occupied floor, particularly in a
residential building, although I'm thinking there isn't a catcher's mitt big
enough for the pieces which will be bouncing off the IBC required
@firesprinkler.org
Subject: RE: Fire Pump on vibration spring type isolators
I'm grasping the idea of wanting to prevention the transmission of vibration
and such when the pump is mounted above an occupied floor, particularly in a
residential building, although I'm thinking there isn't a catcher's mitt big
This does not sound like a good idea to me. After a cursory glance at 20,
the Handbook, and a couple of others books I couldn't find anything to back
up my gut opinion. I'm curious as to what others think and know.
On Mon, Oct 1, 2012 at 11:18 AM, Gregg Key gr...@keyfps.com wrote:
Formites and
: Re: Fire Pump on vibration spring type isolators
This does not sound like a good idea to me. After a cursory glance at 20,
the Handbook, and a couple of others books I couldn't find anything to back
up my gut opinion. I'm curious as to what others think and know.
On Mon, Oct 1, 2012 at 11:18 AM
Of Bobby Gillett
Sent: Monday, October 01, 2012 2:39 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Pump on vibration spring type isolators
We do a good share of pumps, doesn't sound like a good idea to me either. I
would definitely run it by the pump representative and get their thoughts
: RE: Fire Pump on vibration spring type isolators
We do a good share of pumps, doesn't sound like a good idea to me either. I
would definitely run it by the pump representative and get their thoughts.
Curious to see who is requiring this and how it shakes out.
Bobby Gillett
Sr. Project Manager
Key
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Monday, October 01, 2012 2:39 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Pump on vibration spring type isolators
We do a good share of pumps, doesn't sound like a good idea to me either. I
...@firesprinkler.org] On Behalf Of Timothy W Goins
Sent: Monday, October 01, 2012 5:38 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Pump on vibration spring type isolators
They're called vibration arresters and I can see where there will be alignment
problems. Ask your pump supplier if he
...@firesprinkler.org] On Behalf Of Timothy W Goins
Sent: Monday, October 01, 2012 5:38 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Pump on vibration spring type isolators
They're called vibration arresters and I can see where there will be alignment
problems. Ask your pump supplier
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Timothy W Goins
Sent: Monday, October 01, 2012 5:38 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Pump on vibration spring type isolators
They're called vibration arresters and I can see where there will be alignment
problems
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, October 01, 2012 5:52 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Pump on vibration spring type isolators
Looks like someone did a cut and paste from a general mechanical spec and just
painted
...@firesprinkler.org [mailto:
sprinklerforum-boun...@firesprinkler.org] On Behalf Of Timothy W Goins
Sent: Monday, October 01, 2012 5:38 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Pump on vibration spring type isolators
They're called vibration arresters and I can see where