Re: Ventilation for diesel driven fire pump room

2012-08-24 Thread Sprinkler Forum
Aha perfect time to jump in... I have been going through these calcs on Clarke's website all yesterday. I have a situation where we are looking at 125 degree ambient temperature (outside) and about 120 degree water that will be used for the heat exchanger. Using a delta t of 10 degrees F for

RE: Ventilation for diesel driven fire pump room

2012-08-24 Thread George Church
] On Behalf Of Sprinkler Forum Sent: Friday, August 24, 2012 7:36 AM To: sprinklerforum@firesprinkler.org Subject: Re: Ventilation for diesel driven fire pump room Aha perfect time to jump in... I have been going through these calcs on Clarke's website all yesterday. I have a situation where we

Re: Ventilation for diesel driven fire pump room

2012-08-24 Thread Sprinkler Forum
Oh and as far as determining the size of the ventilation opening. After you have found your CFM you should be able to use the equation Q= 2610 x A x squareroot (delta P) Or I guess, rearranged for the area you are looking for is A= (Q/(2610 x squareroot(delta P))) The variables are: Q= to

RE: Ventilation for diesel driven fire pump room

2012-08-24 Thread Bill Brooks
I've consulted with Tigerflow in the past on projects requiring standalone fire pump enclosures. They ship worldwide and I'm sure they would accept a phone call to discuss this if you do not have access to a mechanical engineer (HVAC type) who does this routinely. As others have noted the engine

RE: Ventilation for diesel driven fire pump room

2012-08-24 Thread Bill Brooks
Google search result for combustion air requirements diesel engine http://www.cumminsfirepower.com/documents/ES027_ventilation.pdf Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146-1904 410-544-3620 410-544-3032 FAX 412-400-6528

Re: Ventilation for diesel driven fire pump room

2012-08-24 Thread Ron Greenman
What about a total loss cooling system rather than recirculating through a radiator. You may need a larger, or multiple heat exchangers since you have such high ambients but you need no ventilation air, only combustion air, so no fans. On Fri, Aug 24, 2012 at 5:07 AM, Bill Brooks

Re: Ventilation for diesel driven fire pump room

2012-08-24 Thread Justin Reid
No ventilation fans would be great! I need to get more information on this total loss cooling system. I am working with an engine manufacturer right now to reach a solution...they are supposed to be calling me back so I will mention this. The other thought was to maybe try and duct the

Re: Ventilation for diesel driven fire pump room

2012-08-23 Thread Justin Petcosky
If you look on certain manufactures websites they will have a link where you can put all your information in and will give you the proper sizing and number of louvers. I know Clarke has something to this effect on there site. Justin Petcosky Petcosky Fire Protection Sent from my iPhone On Aug