I don't think what the value of the rule is, or how it's determined or any
other thing than what's required is germane to the discussion. If the AHJ
wants squealing raccoons glued to the ceiling and FM wants quiet ones you
have the problem of serving two masters. When they've both already decided
I thought about PEX as well Steve, its no four letter word for me. At
least with the CPVC we can comply with the pipe requirements from NFPA 13,
which would require less 'selling' than PEX use. Although as Mark points
out about thermal expansion, PEX does have a lower rate of I think about an
I think an investigation of the potential for thermal expansion would be
prudent. The applications I described topped with 3-8 feet of earth, so
temperatures were stable year-round. But PEX is designed to expand and
contract without loss of structural integrity, so it's well suited for
Excellent stuff here Pete.
I think you meant me, Brad, about the "it's a tie".
The distinguishing between concealer and non concealer has never occurred
to me. I input Temp Rating and RTI only (if it's just activation I'm
looking at).
You're right about the oven plunge tests to establish RTI not
I am starting a Freezer/Cooler installation and looking for a hole saw that
will cut a 2.25" diameter hole 6" deep. I need it that deep with a matching
pilot drill/mandrel. The cooler panels are 6" thick and I am dropping Dry
Pendants from above. I prefer to do this in one step and not drill
Thank you all for your responses! I enjoyed reading the conversation so much I
forgot I had asked the question.
Regards,
Scott H
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of rongreenman .
Sent: Friday, October 7, 2016 1:34 PM
To:
Isn't PEX used as the piping in heated floors where you would have a large
change in temperature from winter (using it to halt the floor cum building,
and summer where you wouldn't?
On Fri, Oct 7, 2016 at 6:31 AM, Steve Leyton
wrote:
> I think an investigation of
Interesting topic.
In my humble opinion, the UL 199 tests to qualify concealed sprinklers as quick
response is extremely questionable! On the other hand, what do you think you
are getting when you install a quick response sprinkler anyway? Effectively,
the UL 199 test requires the concealed
Hi Pete,
Just saying what the code stipulates and therein we follow, however if it’s
acceptable for AHJs to use interpretive approval discretion (i.e. I don’t agree
with that standard) regarding listings just say the word. Case in point UL
2196.
John Drucker
From: Sprinklerforum
From a code compliance standpoint Underwriters Laboratories is one of appx 22
Nationally Recognized Testing Laboratories (NRTL). Interestingly UL 199, 1626
etc. are the defacto standards for fire sprinklers which any of the other
NRTL’s would use to test and list a fire sprinkler (aside from
One thing no one has mentioned on this thread concerning the installation of
sprinkler pipe in cast in place concrete, is the differential rate of thermal
expansion. While concrete and steel have very similar rates of thermal
expansion, the rate of thermal expansion for pvc and cpvc is quite
I have drilled similar holes with a ship’s auger. If you cannot find one that
will drill to that depth, there is an extension available. The brand was
Milwaukee. I think the cost was about $100.00 10 years ago, from Home Depot
From: 321
Sent: Friday, October 07, 2016 2:16 PM
To: