RE: Excessive air leak rate

2016-12-05 Thread Nicky Marshall
We have some items in our specification that may help:

· The compressor shall be fitted with an hour meter and number of 
starts counter.

· The air leak rate from the isolated compressor shall not require the 
compressor to run more than once every 4 hours.
The system shall be designed and installed in such a way that the running hours 
for the compressor do not exceed 2 hours / day and the duty cycle (starts/hour) 
does not exceed the manufacturer’s recommendations.

These were developed by a leading industry engineer here.

Nicky Marshall
Southern Regional Manager
PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Phone: +64 (0)3 579 5577 extn 2  Mobile: +64 (0)21 433 488  Email: 
ni...@protechdesign.co.nz<mailto:ni...@protechdesign.co.nz>  Skype: 
nicky-marshall Web :www.protechdesign.co.nz
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Postal: PO Box 4022, 
Redwood Village, Blenheim 7242, NZ

From: AKS-Gmail-IMAP [mailto:aksei...@gmail.com]
Sent: Saturday, 3 December 2016 3:56 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Excessive air leak rate

There you go Mike, your next product, an IOT supervisory air monitor/recorder 
device. It could be Arduinoed up with a pressure transducer, real time clock, 
vibration sensor (sense compressor running and track increasing vibration), 
thumb drive for data storage and wi-fi. There would really be no need for much 
of any display on the device. Someone’s phone or pad would be where the user 
would see the data and where the analysis intelligence takes place. What is of 
interest is trend. In other words change in rate of all things recorded.

Allan Seidel
St. Louis, MO


On Dec 2, 2016, at 4:02 PM, Larry Keeping 
mailto:lkeep...@plcfire.com>> wrote:

Hi Mike:

I didn’t give a reply before, because I thought it best that the “hands on” 
guys give you their input rather than my more theoretical ideas.

Anyway, since you came up dry with your first query, my answer to the options 
that you presented is that all of them would be examples of excessive air 
leakage.

Of course it depends on the start / stop pressures, but to my mind if the 
compressor comes on more than once a day, there is too much leakage. It depends 
on the type of system too. A low pressure system can’t afford as much leakage 
as one with a 40 psi pressure and a 5 or 6 to 1 water/air ratio.

The reason the requirement changed from the NFPA 25 - 2002 edition text of 10 
psi per week to what is in the standard today is because that leak rate (less 
than 1.5 psi per day) is hard to detect during an inspection.

I don’t think the idea is to be totally satisfied with a pressure loss as large 
as 36 psi per day, but the test is just for something detectable during an 
annual ITM site visit – 3 psi in 2 hours, which the inspector can measure 
fairly easily during his time on site, in conjunction with the annual trip 
test, etc. Anything less would prove difficult to determine.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Henke
Sent: December-02-16 3:41 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Excessive air leak rate

Since I only received one response, I’ll try this one last time.

What do you consider to be an excessive air leak for dry or preaction systems 
or at what point do you go searching for the cause of the leak?

How do you know that you have an excessive air leak?
When someone complains about the compressor running all the time?
When the compressor burns out?
When/if you conduct a 3 year leak rate test?
When you go to investigate low air supervisory signals?
Something else?

Would it help if you were notified that the air leak rate is increasing or 
approaching the maximum allowable rate?

Feel free to email me off line.


Kind Regards,

mike

Mike Henke CET
Sprinkler Product Manager
___



Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936   |   direct: 314-595-6740

mi...@pottersignal.com<mailto:mi...@pottersignal.com>   |   
www.pottersignal.com<http://www.pottersignal.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Henke
Sent: Thursday, December 01, 2016 1:22 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Excessive air leak rate

What would you consider to be an excessive air leak rate for dry or preaction 
systems?
How many psi per day?

An acceptance test for a new system requires less than 1.5 psi in 24 hours. 
That’s pretty tight.

NFPA 25 allows 36 psi in 24 hours for the 3 year test. That seems pretty loose.

It looks like NFPA 25 changed it in 2008 from 10 psi per week, which is 1.5 psi 
per day, to 36 psi per day. That’s a pretty drastic change.

Would it help if

Re: Excessive air leak rate

2016-12-02 Thread AKS-Gmail-IMAP
There you go Mike, your next product, an IOT supervisory air monitor/recorder 
device. It could be Arduinoed up with a pressure transducer, real time clock, 
vibration sensor (sense compressor running and track increasing vibration), 
thumb drive for data storage and wi-fi. There would really be no need for much 
of any display on the device. Someone’s phone or pad would be where the user 
would see the data and where the analysis intelligence takes place. What is of 
interest is trend. In other words change in rate of all things recorded.

Allan Seidel
St. Louis, MO


> On Dec 2, 2016, at 4:02 PM, Larry Keeping  wrote:
> 
> Hi Mike:
>  
> I didn’t give a reply before, because I thought it best that the “hands on” 
> guys give you their input rather than my more theoretical ideas.
>  
> Anyway, since you came up dry with your first query, my answer to the options 
> that you presented is that all of them would be examples of excessive air 
> leakage.
>  
> Of course it depends on the start / stop pressures, but to my mind if the 
> compressor comes on more than once a day, there is too much leakage. It 
> depends on the type of system too. A low pressure system can’t afford as much 
> leakage as one with a 40 psi pressure and a 5 or 6 to 1 water/air ratio.
>  
> The reason the requirement changed from the NFPA 25 - 2002 edition text of 10 
> psi per week to what is in the standard today is because that leak rate (less 
> than 1.5 psi per day) is hard to detect during an inspection.
>  
> I don’t think the idea is to be totally satisfied with a pressure loss as 
> large as 36 psi per day, but the test is just for something detectable during 
> an annual ITM site visit – 3 psi in 2 hours, which the inspector can measure 
> fairly easily during his time on site, in conjunction with the annual trip 
> test, etc. Anything less would prove difficult to determine.
>  
> Larry Keeping
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Mike Henke
> Sent: December-02-16 3:41 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Excessive air leak rate
>  
> Since I only received one response, I’ll try this one last time.
>  
> What do you consider to be an excessive air leak for dry or preaction systems 
> or at what point do you go searching for the cause of the leak?
>  
> How do you know that you have an excessive air leak?
> When someone complains about the compressor running all the time?
> When the compressor burns out?
> When/if you conduct a 3 year leak rate test?
> When you go to investigate low air supervisory signals?
> Something else?
>  
> Would it help if you were notified that the air leak rate is increasing or 
> approaching the maximum allowable rate?
>  
> Feel free to email me off line.
>  
>  
> Kind Regards,
>  
> mike
>  
> Mike Henke CET
> Sprinkler Product Manager
> ___
>  
> 
>  
> Potter Electric Signal Company, LLC
> 1609 Park 370 Place, St. Louis, MO 63042
> phone: 800-325-3936   |   direct: 314-595-6740
>  
> mi...@pottersignal.com <mailto:mi...@pottersignal.com>   |   
> www.pottersignal.com <http://www.pottersignal.com/>
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
> <mailto:sprinklerforum-boun...@lists.firesprinkler.org>] On Behalf Of Mike 
> Henke
> Sent: Thursday, December 01, 2016 1:22 PM
> To: sprinklerforum@lists.firesprinkler.org 
> <mailto:sprinklerforum@lists.firesprinkler.org>
> Subject: Excessive air leak rate
>  
> What would you consider to be an excessive air leak rate for dry or preaction 
> systems?
> How many psi per day?
>  
> An acceptance test for a new system requires less than 1.5 psi in 24 hours. 
> That’s pretty tight.
>  
> NFPA 25 allows 36 psi in 24 hours for the 3 year test. That seems pretty 
> loose.
>  
> It looks like NFPA 25 changed it in 2008 from 10 psi per week, which is 1.5 
> psi per day, to 36 psi per day. That’s a pretty drastic change.
>  
> Would it help if you were notified that the air leak rate is increasing or 
> approaching the maximum allowable rate?
>  
> How do you know that you have an excessive air leak?
> When someone complains about the compressor running all the time?
> When the compressor burns out?
> When/if you conduct a 3 year leak rate test?
> When you go to investigate low air supervisory signals?
>  
> Kind Regards,
>  
> mike
>  
> Mike Henke CET
> Sprinkler Product Manager
> ___
>  
> 
>  
> Potter Electric Signal Company, LLC
> 1609 Park 370 Place, St. Louis, MO 63042

RE: Excessive air leak rate

2016-12-02 Thread Larry Keeping
Hi Mike:

I didn't give a reply before, because I thought it best that the "hands on" 
guys give you their input rather than my more theoretical ideas.

Anyway, since you came up dry with your first query, my answer to the options 
that you presented is that all of them would be examples of excessive air 
leakage.

Of course it depends on the start / stop pressures, but to my mind if the 
compressor comes on more than once a day, there is too much leakage. It depends 
on the type of system too. A low pressure system can't afford as much leakage 
as one with a 40 psi pressure and a 5 or 6 to 1 water/air ratio.

The reason the requirement changed from the NFPA 25 - 2002 edition text of 10 
psi per week to what is in the standard today is because that leak rate (less 
than 1.5 psi per day) is hard to detect during an inspection.

I don't think the idea is to be totally satisfied with a pressure loss as large 
as 36 psi per day, but the test is just for something detectable during an 
annual ITM site visit - 3 psi in 2 hours, which the inspector can measure 
fairly easily during his time on site, in conjunction with the annual trip 
test, etc. Anything less would prove difficult to determine.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Henke
Sent: December-02-16 3:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Excessive air leak rate

Since I only received one response, I'll try this one last time.

What do you consider to be an excessive air leak for dry or preaction systems 
or at what point do you go searching for the cause of the leak?

How do you know that you have an excessive air leak?
When someone complains about the compressor running all the time?
When the compressor burns out?
When/if you conduct a 3 year leak rate test?
When you go to investigate low air supervisory signals?
Something else?

Would it help if you were notified that the air leak rate is increasing or 
approaching the maximum allowable rate?

Feel free to email me off line.


Kind Regards,

mike

Mike Henke CET
Sprinkler Product Manager
___

[http://www.pottersignal.com/signatures/graphics/logo.jpg]

Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936   |   direct: 314-595-6740

mi...@pottersignal.com<mailto:mi...@pottersignal.com>   |   
www.pottersignal.com<http://www.pottersignal.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Henke
Sent: Thursday, December 01, 2016 1:22 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Excessive air leak rate

What would you consider to be an excessive air leak rate for dry or preaction 
systems?
How many psi per day?

An acceptance test for a new system requires less than 1.5 psi in 24 hours. 
That's pretty tight.

NFPA 25 allows 36 psi in 24 hours for the 3 year test. That seems pretty loose.

It looks like NFPA 25 changed it in 2008 from 10 psi per week, which is 1.5 psi 
per day, to 36 psi per day. That's a pretty drastic change.

Would it help if you were notified that the air leak rate is increasing or 
approaching the maximum allowable rate?

How do you know that you have an excessive air leak?
When someone complains about the compressor running all the time?
When the compressor burns out?
When/if you conduct a 3 year leak rate test?
When you go to investigate low air supervisory signals?

Kind Regards,

mike

Mike Henke CET
Sprinkler Product Manager
___

[http://www.pottersignal.com/signatures/graphics/logo.jpg]

Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936   |   direct: 314-595-6740

mi...@pottersignal.com<mailto:mi...@pottersignal.com>   |   
www.pottersignal.com<http://www.pottersignal.com/>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Excessive air leak rate

2016-12-02 Thread Douglas Hicks
I must be the only person working today.  Did I miss a holiday?  

25-2014 13.4.4.2.9 . Page 436 of NFPA 25-2014 Handbook
(1) Air at 40 PSI for 2 hours, 3 PSI loss or less is OK
(2) Normal air pressure, with air source off for 4 hours.  If low pressure 
alarm goes off within the 4 hours period, the leaks shall be fixed. 
   

From: Mike Henke 
Sent: Friday, December 02, 2016 12:40 PM
To: sprinklerforum@lists.firesprinkler.org 
Subject: RE: Excessive air leak rate

Since I only received one response, I’ll try this one last time.

 

What do you consider to be an excessive air leak for dry or preaction systems 
or at what point do you go searching for the cause of the leak?

 

How do you know that you have an excessive air leak?

When someone complains about the compressor running all the time?

When the compressor burns out?

When/if you conduct a 3 year leak rate test?

When you go to investigate low air supervisory signals?

Something else?

 

Would it help if you were notified that the air leak rate is increasing or 
approaching the maximum allowable rate?

 

Feel free to email me off line.

 

 

Kind Regards,

 

mike

 

Mike Henke CET

Sprinkler Product Manager

___

  



  

Potter Electric Signal Company, LLC

1609 Park 370 Place, St. Louis, MO 63042

phone: 800-325-3936   |   direct: 314-595-6740

  

mi...@pottersignal.com   |   www.pottersignal.com

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Henke
Sent: Thursday, December 01, 2016 1:22 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Excessive air leak rate

 

What would you consider to be an excessive air leak rate for dry or preaction 
systems?

How many psi per day?

 

An acceptance test for a new system requires less than 1.5 psi in 24 hours. 
That’s pretty tight.

 

NFPA 25 allows 36 psi in 24 hours for the 3 year test. That seems pretty loose.

 

It looks like NFPA 25 changed it in 2008 from 10 psi per week, which is 1.5 psi 
per day, to 36 psi per day. That’s a pretty drastic change.

 

Would it help if you were notified that the air leak rate is increasing or 
approaching the maximum allowable rate?

 

How do you know that you have an excessive air leak?

When someone complains about the compressor running all the time?

When the compressor burns out?

When/if you conduct a 3 year leak rate test?

When you go to investigate low air supervisory signals?

 

Kind Regards,

 

mike

 

Mike Henke CET

Sprinkler Product Manager

___

  



  

Potter Electric Signal Company, LLC

1609 Park 370 Place, St. Louis, MO 63042

phone: 800-325-3936   |   direct: 314-595-6740

  

mi...@pottersignal.com   |   www.pottersignal.com

 




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Excessive air leak rate

2016-12-02 Thread Greg McGahan
What do you consider to be an excessive air leak for dry or preaction
systems or at what point do you go searching for the cause of the leak? in
my experience a compressor should not even run every day...once every few
days to a week on a typical system. More than that is not acceptable.



How do you know that you have an excessive air leak? All of the items below
sometimes..

When someone complains about the compressor running all the time?

When the compressor burns out?

When/if you conduct a 3 year leak rate test?

When you go to investigate low air supervisory signals?

Something else? false trips



Would it help if you were notified that the air leak rate is increasing or
approaching the maximum allowable rate? if it were in combination with the
low air alarm yesif it requires more hardware, trim etc, only in some
instances.




Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852

On Fri, Dec 2, 2016 at 2:40 PM, Mike Henke  wrote:

> Since I only received one response, I’ll try this one last time.
>
>
>
> What do you consider to be an excessive air leak for dry or preaction
> systems or at what point do you go searching for the cause of the leak?
>
>
>
> How do you know that you have an excessive air leak?
>
> When someone complains about the compressor running all the time?
>
> When the compressor burns out?
>
> When/if you conduct a 3 year leak rate test?
>
> When you go to investigate low air supervisory signals?
>
> Something else?
>
>
>
> Would it help if you were notified that the air leak rate is increasing or
> approaching the maximum allowable rate?
>
>
>
> Feel free to email me off line.
>
>
>
>
>
> Kind Regards,
>
>
>
> mike
>
>
>
> *Mike Henke CET*
>
> Sprinkler Product Manager
>
> ___
>
>
>
> [image: http://www.pottersignal.com/signatures/graphics/logo.jpg]
>
>
>
> Potter Electric Signal Company, LLC
>
> 1609 Park 370 Place, St. Louis, MO 63042
>
> phone: 800-325-3936 <(800)%20325-3936>   |   direct: 314-595-6740
> <(314)%20595-6740>
>
>
>
> mi...@pottersignal.com   |   www.pottersignal.com
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] *On Behalf Of *Mike Henke
> *Sent:* Thursday, December 01, 2016 1:22 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Excessive air leak rate
>
>
>
> What would you consider to be an excessive air leak rate for dry or
> preaction systems?
>
> How many psi per day?
>
>
>
> An acceptance test for a new system requires less than 1.5 psi in 24
> hours. That’s pretty tight.
>
>
>
> NFPA 25 allows 36 psi in 24 hours for the 3 year test. That seems pretty
> loose.
>
>
>
> It looks like NFPA 25 changed it in 2008 from 10 psi per week, which is
> 1.5 psi per day, to 36 psi per day. That’s a pretty drastic change.
>
>
>
> Would it help if you were notified that the air leak rate is increasing or
> approaching the maximum allowable rate?
>
>
>
> How do you know that you have an excessive air leak?
>
> When someone complains about the compressor running all the time?
>
> When the compressor burns out?
>
> When/if you conduct a 3 year leak rate test?
>
> When you go to investigate low air supervisory signals?
>
>
>
> Kind Regards,
>
>
>
> mike
>
>
>
> *Mike Henke CET*
>
> Sprinkler Product Manager
>
> ___
>
>
>
> [image: http://www.pottersignal.com/signatures/graphics/logo.jpg]
>
>
>
> Potter Electric Signal Company, LLC
>
> 1609 Park 370 Place, St. Louis, MO 63042
>
> phone: 800-325-3936 <(800)%20325-3936>   |   direct: 314-595-6740
> <(314)%20595-6740>
>
>
>
> mi...@pottersignal.com   |   www.pottersignal.com
>
>
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Excessive air leak rate

2016-12-02 Thread Mike Henke
Since I only received one response, I'll try this one last time.

What do you consider to be an excessive air leak for dry or preaction systems 
or at what point do you go searching for the cause of the leak?

How do you know that you have an excessive air leak?
When someone complains about the compressor running all the time?
When the compressor burns out?
When/if you conduct a 3 year leak rate test?
When you go to investigate low air supervisory signals?
Something else?

Would it help if you were notified that the air leak rate is increasing or 
approaching the maximum allowable rate?

Feel free to email me off line.


Kind Regards,

mike

Mike Henke CET
Sprinkler Product Manager
___

[http://www.pottersignal.com/signatures/graphics/logo.jpg]

Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936   |   direct: 314-595-6740

mi...@pottersignal.com<mailto:mi...@pottersignal.com>   |   
www.pottersignal.com<http://www.pottersignal.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Henke
Sent: Thursday, December 01, 2016 1:22 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Excessive air leak rate

What would you consider to be an excessive air leak rate for dry or preaction 
systems?
How many psi per day?

An acceptance test for a new system requires less than 1.5 psi in 24 hours. 
That's pretty tight.

NFPA 25 allows 36 psi in 24 hours for the 3 year test. That seems pretty loose.

It looks like NFPA 25 changed it in 2008 from 10 psi per week, which is 1.5 psi 
per day, to 36 psi per day. That's a pretty drastic change.

Would it help if you were notified that the air leak rate is increasing or 
approaching the maximum allowable rate?

How do you know that you have an excessive air leak?
When someone complains about the compressor running all the time?
When the compressor burns out?
When/if you conduct a 3 year leak rate test?
When you go to investigate low air supervisory signals?

Kind Regards,

mike

Mike Henke CET
Sprinkler Product Manager
___

[http://www.pottersignal.com/signatures/graphics/logo.jpg]

Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936   |   direct: 314-595-6740

mi...@pottersignal.com<mailto:mi...@pottersignal.com>   |   
www.pottersignal.com<http://www.pottersignal.com/>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Excessive air leak rate

2016-12-01 Thread Mike Henke
What would you consider to be an excessive air leak rate for dry or preaction 
systems?
How many psi per day?

An acceptance test for a new system requires less than 1.5 psi in 24 hours. 
That's pretty tight.

NFPA 25 allows 36 psi in 24 hours for the 3 year test. That seems pretty loose.

It looks like NFPA 25 changed it in 2008 from 10 psi per week, which is 1.5 psi 
per day, to 36 psi per day. That's a pretty drastic change.

Would it help if you were notified that the air leak rate is increasing or 
approaching the maximum allowable rate?

How do you know that you have an excessive air leak?
When someone complains about the compressor running all the time?
When the compressor burns out?
When/if you conduct a 3 year leak rate test?
When you go to investigate low air supervisory signals?

Kind Regards,

mike

Mike Henke CET
Sprinkler Product Manager
___

[http://www.pottersignal.com/signatures/graphics/logo.jpg]

Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936   |   direct: 314-595-6740

mi...@pottersignal.com<mailto:mi...@pottersignal.com>   |   
www.pottersignal.com<http://www.pottersignal.com/>