On 11/27/2014 01:10 AM, Jim Lux wrote:

On 11/26/14, 2:54 PM, Hal Murray wrote:


albertson.ch...@gmail.com said:

The ground rod needs to be bonded to the rest of the building ground
system.


How do I do that effectively if the power goes in the front of the
building
and the antenna is on the back?



AWG 6 wire with no breaks or splices between the two.

The goal of bonding all the grounding systems together is not for
transient suppression.  It's to make sure that there's no DC or line
frequency potential difference between electrical safety ground at
various places in the building.

The background on the whole grounding/bonding requirement is more about
safety when a power carrying conductor, either inside equipment or
overhead, touches something that people might touch. And, to a lesser
extent to ensure that if there's an internal short, that the breaker or
fuse will trip.

NEC requirements for grounding and bonding aren't there for transient
suppression.

A copy of IEEE 1100 (the Emerald Book) is good reading for the whole
bonding and equipotential planes, etc.  (unfortunately not free from IEEE).

A good book on transient protection is Ronald Standler's book
protection of electronic circuits from overvoltages
Something like $20 from Dover...


Do use the ITU-T K-series as a reference, it's a great starting point 
and they are there for free download. The ITU-T K.27 explains grounding 
in a station, and that could be interesting food for though in many 
cases, where people try to motivate Isolated Bonding Network while Mesh 
Bonding Network might be better in the end. K.40 may be inspiring. K.97 
a special case which is partly relevant here.


Cheers,
Magnus
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-12-07 Thread Bob Camp
Hi

Ok, here’s the full and proper answer to the question. Anything less is simply 
not adequate:

1) Lay down some ground cables, say a few thousand of them. Run them out at 
least 1/4 mile in each direction from your structure. Make sure they are at 
least 00 gauge and buried 10 feet deep.

2) At the perimeter (20’ past the walls) of the structure put down an 
underground aluminum plate at least 1” thick. Extend it  at least 10 feet under 
the structure. Bond all the ground cables to the plate. 

3) Route all cables, wires, and pipes  into and out of the structure to a 
single point below ground level. 

4) Bond all cables, wires, and pipes  to the plate at that single point and 
protect them to the plate with at least six properly rated protection devices 
in series. 

5) Extend the plate up to enclose the structure. Make sure it does not touch 
the walls or roof at any point. Nothing from the structure should be outside 
the plate. There always should be a 10’ air gap. 

6) Make sure that all joints in the plate are properly bonded to each other. 
Holes and openings are to be avoided. 

7) If EMP from nuclear attack is a major concern, add about 3/8” of steel to 
the aluminum plate. Make sure all openings are fully covered in the event of 
nuclear attack. 

8) Put up the usual towers at each corner of the plate, and 20’ beyond the 
edges of the plate. Independently ground each tower. Run cables between the 
towers to screen the top and sides of the plate. Tie the tower bases together 
with multiple 00 cables, all isolated from the ground cables in step 1.  At all 
points above ground the cable / tower screen should have an air gap of 20’ to 
the plate. 

Congratulations .. you are now fully protected against lightning ….

You can be sure that your basement timing system will be protected against 
disruption from lightning to the  99.99% ( 1 ppt ) level. None of your 
$150 GPS based timing boxes will be damaged. Should you properly and fully 
implement this system and have a problem from a lightning hit, I’ll personally 
replace any $150 box that is proven to be damaged by lightning with a similar 
box from my collection. I also will re-set your local clock against my wrist 
watch at no extra charge. This is about timing after all :)  Yes, you can paint 
the structure any color the rest of the family finds pleasing. We would not 
want our *hobby* to impact them too much. 

Bob

 On Dec 7, 2014, at 7:39 AM, Magnus Danielson mag...@rubidium.dyndns.org 
 wrote:
 
 
 
 On 11/27/2014 01:10 AM, Jim Lux wrote:
 On 11/26/14, 2:54 PM, Hal Murray wrote:
 
 albertson.ch...@gmail.com said:
 The ground rod needs to be bonded to the rest of the building ground
 system.
 
 How do I do that effectively if the power goes in the front of the
 building
 and the antenna is on the back?
 
 
 AWG 6 wire with no breaks or splices between the two.
 
 The goal of bonding all the grounding systems together is not for
 transient suppression.  It's to make sure that there's no DC or line
 frequency potential difference between electrical safety ground at
 various places in the building.
 
 The background on the whole grounding/bonding requirement is more about
 safety when a power carrying conductor, either inside equipment or
 overhead, touches something that people might touch. And, to a lesser
 extent to ensure that if there's an internal short, that the breaker or
 fuse will trip.
 
 NEC requirements for grounding and bonding aren't there for transient
 suppression.
 
 A copy of IEEE 1100 (the Emerald Book) is good reading for the whole
 bonding and equipotential planes, etc.  (unfortunately not free from IEEE).
 
 A good book on transient protection is Ronald Standler's book
 protection of electronic circuits from overvoltages
 Something like $20 from Dover...
 
 Do use the ITU-T K-series as a reference, it's a great starting point and 
 they are there for free download. The ITU-T K.27 explains grounding in a 
 station, and that could be interesting food for though in many cases, where 
 people try to motivate Isolated Bonding Network while Mesh Bonding Network 
 might be better in the end. K.40 may be inspiring. K.97 a special case which 
 is partly relevant here.
 
 Cheers,
 Magnus
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-12-07 Thread Chris Albertson

 Bob,
 can you explain more about the effect of antenna performance on a GPSDO
 system?

 Now you have told me it is important,  I would like to know more! My lab
 has an East facing window.


Physically what is happening here is that the error bars on the fix your
GPS gets will cycle over a 12  hour period because of the sats all have 12
hour orbital periods.   If you can only see part of the sky the amplitude
of this is greater.

As an example thing of the worst possible case where you antenna can only
see a few degrees of the sky.  Every 12 hours one GPS satellite comes into
view and your GPS gets a decent fix but then for 8 hours the GPS sees
nothing and drifts off.  Now think about moving the antenna to a marginally
better place where it always sees at last ONE GPS stiletto but for 8 hours
there are two and for 2hours there are three satellites.   The quality if
the fix would still vary but would be better.   In the best case your 12
channel GPS receiver ALWAYS is able to select the 12 BEST places GPS
satellites that are in view.

This is not a great effect as long as there is enough sky that there are
always some in view.

Don
t worry about listening strike on your antenna.  If is FAR MORE likely that
lighting will strike some utility pole within 1/4 mile of your house and
the surge will come in through the AC mains power.  So if you want to fix a
problem fix that one first, then worry about less and less likely things.
This is not to say not to take normal precautions and ground the iron pipe
with a $7 aluminum ground wire just like you would do to an old fashioned
TV antenna.





-- 

Chris Albertson
Redondo Beach, California
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-12-07 Thread Bob Camp
Hi

The 12 hour periodicity of GPS is (in general) less obvious in an ADEV plot 
than 24 and 48 hour effects. Part of this is due to the lower “floor” at longer 
tau. Another part of it is due to things like the  ionosphere being at 
different places at the 12 hour points. 

Bob

 On Dec 7, 2014, at 2:27 PM, Chris Albertson albertson.ch...@gmail.com wrote:
 
 
 Bob,
 can you explain more about the effect of antenna performance on a GPSDO
 system?
 
 Now you have told me it is important,  I would like to know more! My lab
 has an East facing window.
 
 
 Physically what is happening here is that the error bars on the fix your
 GPS gets will cycle over a 12  hour period because of the sats all have 12
 hour orbital periods.   If you can only see part of the sky the amplitude
 of this is greater.
 
 As an example thing of the worst possible case where you antenna can only
 see a few degrees of the sky.  Every 12 hours one GPS satellite comes into
 view and your GPS gets a decent fix but then for 8 hours the GPS sees
 nothing and drifts off.  Now think about moving the antenna to a marginally
 better place where it always sees at last ONE GPS stiletto but for 8 hours
 there are two and for 2hours there are three satellites.   The quality if
 the fix would still vary but would be better.   In the best case your 12
 channel GPS receiver ALWAYS is able to select the 12 BEST places GPS
 satellites that are in view.
 
 This is not a great effect as long as there is enough sky that there are
 always some in view.
 
 Don
 t worry about listening strike on your antenna.  If is FAR MORE likely that
 lighting will strike some utility pole within 1/4 mile of your house and
 the surge will come in through the AC mains power.  So if you want to fix a
 problem fix that one first, then worry about less and less likely things.
 This is not to say not to take normal precautions and ground the iron pipe
 with a $7 aluminum ground wire just like you would do to an old fashioned
 TV antenna.
 
 
 
 
 
 -- 
 
 Chris Albertson
 Redondo Beach, California
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-12-07 Thread Jim Harman
The topic has shifted from lightning protection, but I thought I would
share my experiences on diurnal timing shifts.

On my home-built GPSDO, similar to the design posted by Lars Walenius some
time ago, I can see variations in the TIC output that correlate well to to
the variations 24 hours ago. The variations are about 100 ns p-p and are
noticeably larger when it is raining outside. I think the variations were
also greater over the summer, when the sky view was more obstructed by
leaves.

My system uses an Adafruit (Globaltop) GPS module, so not the greatest for
timing applications. I have an outdoor puck antenna located a few feet
above ground level and a few feet from a wooden house, with a mostly
unobstructed view to the west.

The time constant for steering the OCXO is set to 2048 sec. The timing
variations appear as noisy lumps that last about 90 minutes, so the
disciplining is reducing but not eliminating the variations.

On Sun, Dec 7, 2014 at 2:49 PM, Bob Camp kb...@n1k.org wrote:

 Hi

 The 12 hour periodicity of GPS is (in general) less obvious in an ADEV
 plot than 24 and 48 hour effects. Part of this is due to the lower “floor”
 at longer tau. Another part of it is due to things like the  ionosphere
 being at different places at the 12 hour points.

 Bob

  On Dec 7, 2014, at 2:27 PM, Chris Albertson albertson.ch...@gmail.com
 wrote:
 
 
  Bob,
  can you explain more about the effect of antenna performance on a GPSDO
  system?
 
  Now you have told me it is important,  I would like to know more! My lab
  has an East facing window.
 
 
  Physically what is happening here is that the error bars on the fix your
  GPS gets will cycle over a 12  hour period because of the sats all have
 12
  hour orbital periods.   If you can only see part of the sky the amplitude
  of this is greater.
 
  As an example thing of the worst possible case where you antenna can only
  see a few degrees of the sky.  Every 12 hours one GPS satellite comes
 into
  view and your GPS gets a decent fix but then for 8 hours the GPS sees
  nothing and drifts off.  Now think about moving the antenna to a
 marginally
  better place where it always sees at last ONE GPS stiletto but for 8
 hours
  there are two and for 2hours there are three satellites.   The quality if
  the fix would still vary but would be better.   In the best case your
 12
  channel GPS receiver ALWAYS is able to select the 12 BEST places GPS
  satellites that are in view.
 
  This is not a great effect as long as there is enough sky that there are
  always some in view.
 




-- 

--Jim Harman
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-27 Thread Bob Camp
Hi

If you are happy with 1x10^ -9 frequency accuracy, then there are a number of 
things you can ignore. If you are after  1x10^-11 frequency accuracy 99.9% of 
the time you have to do everything right. Different limits apply to different 
measures of stability. 

To reduce multi path you need a clear sky view. To keep the timing solution in 
the GPS happy you need to let it see 80 % of the sats it should see. In this 
case stuff below 20 degrees does not count towards the total.

In both cases the exact  numeric impact depends on a bunch of things. It would 
take a few hundred pages to go into all of it. You ultimately need a site 
survey to work out the multi path math. 

In the extreme case the antenna can not see any sats. The math is simple then. 
Your stability is just that of your oscillator. That gets us right back to Rb's 
are better than OCXO's. Both are better than a TCXO. 

Best advice is still the same. Get as good a GPSDO as you can afford. Put the 
antenna up on the roof. 

Bob

Sent from my iPhone

 On Nov 27, 2014, at 3:24 AM, Dr. David Kirkby (Kirkby Microwave Ltd) 
 drkir...@kirkbymicrowave.co.uk wrote:
 
 On 27 Nov 2014 03:06, Bob Camp kb...@n1k.org wrote:
 
 Hi
 
 You need a good antenna setup to get a good disciplined oscillator. The
 bigger question is if you *need* the sort of “better” it gives you. If you
 are running a simple TCXO based GPSDO, you will have a number of issues to
 deal with compared to an OCXO or Rb based system. If “better” is an
 objective, consider the entire system.
 
 Bob
 
 Bob,
 can you explain more about the effect of antenna performance on a GPSDO
 system?
 
 Now you have told me it is important,  I would like to know more! My lab
 has an East facing window.
 
 The only way I would use an external antenna is if I had optical isolation.
 
 I live in an area where the lightening risk is considered low,  but having
 lost equipment twice, I am probably more concerned than others might be.
 
 Dave.
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


[time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Dr. David Kirkby (Kirkby Microwave Ltd)
Said mentioned on an earlier thread that if a GPS antenna is used
outside, lightening protection should be used. This immediately
reminded me of something that happened about 10 years ago to me

1) Lightening damaged my ADSL modem. It because totally dead.
2) Every computer and a printer connected to that had the Ethernet
ports blown up.

After a hell of a fight with my insurance company, they paid up on my
household insurance. The total cost was about £10,000, as all were Sun
workstations, so a bit more expensive than a typical home computer.

A few years after that, a similar thing happened, but just the ADSL
modem got destroyed - no computers.

Clearly if an external antenna is put in a high enough E-field or
H-field, it can do damage to the antenna, and potentially anything
connected to it, which would be all your test equipment, in much the
same way all my computers got their Ethernet ports blown up.

I would be *very* reluctant to use an external antenna, which is in
some way connected to a distribution unit into the back of every bit
of test equipment I have. I can see a potential (excuse the pun), of
doing a serious amount of damage.

The only way I would consider doing it, is if there was some optical
isolation. In principle one could modulate a laser at 10 MHz, pass it
down an optical fibre, then have a photodiode to recover the
modulation. Can would obviously be needed not to compromise the
signal, and that might be impossible.

I realize the signal strength from an external antenna will be higher
than an internal antenna, but does that make much (any?) difference to
the operation of the GPSDO?


FUNNY, SAD but TRUE story.

After I got hit by lightening for the second time down my telephone
line, I decided I needed to do something about it. So I got onto my
service provider (BT) and asked them what could be done, as my
telephone is fed via an overhead line. After arguing with them for
months, they agree to fit some lightening protection to my telephone
line. The day they came to fit this was a lesson in how incompetent
some technicians, and their managers can be. Of course BT call them
engineers, but this guy is not an engineering in my mind.

BT TECHNICIAN: I need to run an earth wire
ME: That is ok, so I assume you are going to put an earth rod into the ground.
BT TECHNICIAN: No, I wont use an earth rod.
ME: So how are you going to earth it? What sort of wire is it?
BT TECHNICIAN: My manager said to move some earth away with my
fingers, poke the wire into the ground, then move the earth back with
my hand. The wire is 1 mm^2.
ME: That is no good. Let me speak to your manager.

The BT technician then rings his manager, and puts him on the phone. I
explain that is not acceptable.

MANAGER: So how do you suggest we earth it?
ME: I don't know how to do it. This is not my area of expertise, but I
know that what you are proposing, with 1 mm wire and poking the wire
into the ground with your fingers is not acceptable.




Dr. David Kirkby Ph.D CEng MIET
Kirkby Microwave Ltd
Registered office: Stokes Hall Lodge, Burnham Rd, Althorne, Essex, CM3 6DT, UK.
Registered in England and Wales, company number 08914892.
http://www.kirkbymicrowave.co.uk/
Tel: 07910 441670 / +44 7910 441670 (0900 to 2100 GMT only please)
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Martin A Flynn
The N2MO station has an external GPS antenna on the gable end of the 
building.  It's connected to the polyphaser arrestor with FSJ4-50 
superflex.


The antenna mounting pipe has a #2 ground wire  (33.6 mm/2)  the 
polyphaser has it's own #2 ground wire.  Both connect to an 8'  x 5/8 
(2.4m x 16mm) driven ground rod.  The jacket of the superflex is 
grounded with the factoryt Andrew kit as well


Even with the GPS antenna lower in elevation then the HF beam and other 
antenna (with similar protection)  I have concerns about leaving it 
connected all the time.


73 Martin Flynn
W2RWJ

On 11/26/2014 4:37 PM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote:

Said mentioned on an earlier thread that if a GPS antenna is used
outside, lightening protection should be used. This immediately
reminded me of something that happened about 10 years ago to me
(33.6
1) Lightening damaged my ADSL modem. It because totally dead.
2) Every computer and a printer connected to that had the Ethernet
ports blown up.

After a hell of a fight with my insurance company, they paid up on my
household insurance. The total cost was about £10,000, as all were Sun
workstations, so a bit more expensive than a typical home computer.

A few years after that, a similar thing happened, but just the ADSL
modem got destroyed - no computers.

Clearly if an external antenna is put in a high enough E-field or
H-field, it can do damage to the antenna, and potentially anything
connected to it, which would be all your test equipment, in much the
same way all my computers got their Ethernet ports blown up.

I would be *very* reluctant to use an external antenna, which is in
some way connected to a distribution unit into the back of every bit
of test equipment I have. I can see a potential (excuse the pun), of
doing a serious amount of damage.

The only way I would consider doing it, is if there was some optical
isolation. In principle one could modulate a laser at 10 MHz, pass it
down an optical fibre, then have a photodiode to recover the
modulation. Can would obviously be needed not to compromise the
signal, and that might be impossible.

I realize the signal strength from an external antenna will be higher
than an internal antenna, but does that make much (any?) difference to
the operation of the GPSDO?


FUNNY, SAD but TRUE story.

After I got hit by lightening for the second time down my telephone
line, I decided I needed to do something about it. So I got onto my
service provider (BT) and asked them what could be done, as my
telephone is fed via an overhead line. After arguing with them for
months, they agree to fit some lightening protection to my telephone
line. The day they came to fit this was a lesson in how incompetent
some technicians, and their managers can be. Of course BT call them
engineers, but this guy is not an engineering in my mind.

BT TECHNICIAN: I need to run an earth wire
ME: That is ok, so I assume you are going to put an earth rod into the ground.
BT TECHNICIAN: No, I wont use an earth rod.
ME: So how are you going to earth it? What sort of wire is it?
BT TECHNICIAN: My manager said to move some earth away with my
fingers, poke the wire into the ground, then move the earth back with
my hand. The wire is 1 mm^2.
ME: That is no good. Let me speak to your manager.

The BT technician then rings his manager, and puts him on the phone. I
explain that is not acceptable.

MANAGER: So how do you suggest we earth it?
ME: I don't know how to do it. This is not my area of expertise, but I
know that what you are proposing, with 1 mm wire and poking the wire
into the ground with your fingers is not acceptable.




Dr. David Kirkby Ph.D CEng MIET
Kirkby Microwave Ltd
Registered office: Stokes Hall Lodge, Burnham Rd, Althorne, Essex, CM3 6DT, UK.
Registered in England and Wales, company number 08914892.
http://www.kirkbymicrowave.co.uk/
Tel: 07910 441670 / +44 7910 441670 (0900 to 2100 GMT only please)
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.



-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4794 / Virus Database: 4189/8634 - Release Date: 11/26/14





--
V/Rbr
Martin A. Flynnbr
br
Chief Technology Officerbr
Information Age Learning Centerbr
2201 Marconi Roadbr
Wall Township, NJ 07719br
Cell: 732-585-9913br
Email: a href=mailto:mar...@infoage.org;mar...@infoage.org/abr
Visit us online at: a href=http://www.infoage.org;www.infoage.orgbr
Likes us on a 
href=https://www.facebook.com/infoagesciencemuseum;Facebook!/abr
br

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Jim Lux

On 11/26/14, 1:37 PM, Dr. David Kirkby (Kirkby Microwave Ltd) wrote:

Said mentioned on an earlier thread that if a GPS antenna is used
outside, lightening protection should be used. This immediately
reminded me of something that happened about 10 years ago to me

1) Lightening damaged my ADSL modem. It because totally dead.
2) Every computer and a printer connected to that had the Ethernet
ports blown up.




Here's what we do at JPL for spaceflight equipment: reradiators.

Antenna with preamp on the roof... long coax to wherever the signal is 
needed, amp(maybe), DC bias T (minicircuits has them, as do others, or 
build one), and a variable attenuator (in case the system has too much 
gain), feeding a passive antenna.  Another passive antenna (or your GPS 
receiver or your whatever) is a meter or so away.


The inside antennas can be pretty crude.  I suspect stripping back 1/4 
wavelength of coax shield would work.   We use ones that resemble a 
hockey puck and that have the required bandwidth (L1,L2, L5).


You could, if you like, build some sort of shielding box with absorber 
around the two antennas which would cut down on multipath reflections, 
etc.   But that box would require some design so that it doesn't become 
the path for the lightning to your gear.



The entire path from roof antenna to reradiator is sacrificial.



The only way I would consider doing it, is if there was some optical
isolation. In principle one could modulate a laser at 10 MHz, pass it
down an optical fibre, then have a photodiode to recover the
modulation. Can would obviously be needed not to compromise the
signal, and that might be impossible.


Sure, there's all sorts of RF over fiber stuff available. Some is even 
designed for GPS signals specifically.






___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Jim Lux

On 11/26/14, 2:00 PM, Martin A Flynn wrote:

The N2MO station has an external GPS antenna on the gable end of the
building.  It's connected to the polyphaser arrestor with FSJ4-50
superflex.

The antenna mounting pipe has a #2 ground wire  (33.6 mm/2)  the
polyphaser has it's own #2 ground wire.  Both connect to an 8'  x 5/8
(2.4m x 16mm) driven ground rod.  The jacket of the superflex is
grounded with the factoryt Andrew kit as well

Even with the GPS antenna lower in elevation then the HF beam and other
antenna (with similar protection)  I have concerns about leaving it
connected all the time.




AWG #2 seems a tad overkill, the current in a stroke can be carried by 
AWG #10 without melting, but maybe you had a lot of it around for other 
reasons.  I suspect the coax shield has smaller cross sectional area 
than AWG #2 and you'll protect your grounding wire by blowing up the 
coaxgrin. (in fact, looking at the data sheet for FSJ4-50, the DC 
resistance of the outer conductor is 1 ohm/1000 ft = AWG 10.. it's 
actually more resistance than the inner conductor (the inner conductor 
is 0.820ohms/kft, and 0.140 inch in diameter, compare to AWG 10 which is 
very close to 0.100 inch in diameter).


Hopefully your driven ground rod is bonded to the other system grounds?


I'd worry about multipath from the HF beam and tower (although maybe 
you're not using that GPS for time-nuts 1E-20 precision...grin)




___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Chris Albertson
You CAN (almost) lightening proof your system.  The trick is to give
lightening a low impedence path to grind at very opportunity.

Start with the antenna mast and call.  Use iron pipe for the mast and feed
the antenna cable down the center of the pipe.  Place two large ground
clamps on this pipe and connect a large diameter wire that takes a straight
path to a group rod.This will go a long way to diverting energy to
ground because high voltage likes to flow on the outside of a conductor
which would be the pipe and not so much the antenna cable.

The ground rod needs to be bonded to the rest of the building ground system.

Then the antenna cable passes through a metal bulkhead with a bulkhead
connector and all this is also grounded.  After this is might be a high
voltage e on the center conductor.  Use an lightening arrester that is
bolted to the bulkhead.

At this point you are reasonably safe.  Remember that Ethernet is always
gavalically isolated by transformers

On Wed, Nov 26, 2014 at 1:37 PM, Dr. David Kirkby (Kirkby Microwave Ltd) 
drkir...@kirkbymicrowave.co.uk wrote:

 Said mentioned on an earlier thread that if a GPS antenna is used
 outside, lightening protection should be used. This immediately
 reminded me of something that happened about 10 years ago to me

 1) Lightening damaged my ADSL modem. It because totally dead.
 2) Every computer and a printer connected to that had the Ethernet
 ports blown up.

 After a hell of a fight with my insurance company, they paid up on my
 household insurance. The total cost was about £10,000, as all were Sun
 workstations, so a bit more expensive than a typical home computer.

 A few years after that, a similar thing happened, but just the ADSL
 modem got destroyed - no computers.

 Clearly if an external antenna is put in a high enough E-field or
 H-field, it can do damage to the antenna, and potentially anything
 connected to it, which would be all your test equipment, in much the
 same way all my computers got their Ethernet ports blown up.

 I would be *very* reluctant to use an external antenna, which is in
 some way connected to a distribution unit into the back of every bit
 of test equipment I have. I can see a potential (excuse the pun), of
 doing a serious amount of damage.

 The only way I would consider doing it, is if there was some optical
 isolation. In principle one could modulate a laser at 10 MHz, pass it
 down an optical fibre, then have a photodiode to recover the
 modulation. Can would obviously be needed not to compromise the
 signal, and that might be impossible.

 I realize the signal strength from an external antenna will be higher
 than an internal antenna, but does that make much (any?) difference to
 the operation of the GPSDO?


 FUNNY, SAD but TRUE story.

 After I got hit by lightening for the second time down my telephone
 line, I decided I needed to do something about it. So I got onto my
 service provider (BT) and asked them what could be done, as my
 telephone is fed via an overhead line. After arguing with them for
 months, they agree to fit some lightening protection to my telephone
 line. The day they came to fit this was a lesson in how incompetent
 some technicians, and their managers can be. Of course BT call them
 engineers, but this guy is not an engineering in my mind.

 BT TECHNICIAN: I need to run an earth wire
 ME: That is ok, so I assume you are going to put an earth rod into the
 ground.
 BT TECHNICIAN: No, I wont use an earth rod.
 ME: So how are you going to earth it? What sort of wire is it?
 BT TECHNICIAN: My manager said to move some earth away with my
 fingers, poke the wire into the ground, then move the earth back with
 my hand. The wire is 1 mm^2.
 ME: That is no good. Let me speak to your manager.

 The BT technician then rings his manager, and puts him on the phone. I
 explain that is not acceptable.

 MANAGER: So how do you suggest we earth it?
 ME: I don't know how to do it. This is not my area of expertise, but I
 know that what you are proposing, with 1 mm wire and poking the wire
 into the ground with your fingers is not acceptable.




 Dr. David Kirkby Ph.D CEng MIET
 Kirkby Microwave Ltd
 Registered office: Stokes Hall Lodge, Burnham Rd, Althorne, Essex, CM3
 6DT, UK.
 Registered in England and Wales, company number 08914892.
 http://www.kirkbymicrowave.co.uk/
 Tel: 07910 441670 / +44 7910 441670 (0900 to 2100 GMT only please)
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.




-- 

Chris Albertson
Redondo Beach, California
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Hal Murray

albertson.ch...@gmail.com said:
 The ground rod needs to be bonded to the rest of the building ground system.

How do I do that effectively if the power goes in the front of the building 
and the antenna is on the back?



-- 
These are my opinions.  I hate spam.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Martin A Flynn

On 11/26/2014 5:14 PM, Jim Lux wrote:

On 11/26/14, 2:00 PM, Martin A Flynn wrote:

The N2MO station has an external GPS antenna on the gable end of the
building.  It's connected to the polyphaser arrestor with FSJ4-50
superflex.

The antenna mounting pipe has a #2 ground wire  (33.6 mm/2)  the
polyphaser has it's own #2 ground wire.  Both connect to an 8' x 5/8
(2.4m x 16mm) driven ground rod.  The jacket of the superflex is
grounded with the factoryt Andrew kit as well

Even with the GPS antenna lower in elevation then the HF beam and other
antenna (with similar protection)  I have concerns about leaving it
connected all the time.

AWG #2 seems a tad overkill, the current in a stroke can be carried by 
AWG #10 without melting, but maybe you had a lot of it around for 
other reasons.  I suspect the coax shield has smaller cross sectional 
area than AWG #2 and you'll protect your grounding wire by blowing up 
the coaxgrin. (in fact, looking at the data sheet for FSJ4-50, the 
DC resistance of the outer conductor is 1 ohm/1000 ft = AWG 10.. it's 
actually more resistance than the inner conductor (the inner conductor 
is 0.820ohms/kft, and 0.140 inch in diameter, compare to AWG 10 which 
is very close to 0.100 inch in diameter).


Hopefully your driven ground rod is bonded to the other system grounds?

I'd worry about multipath from the HF beam and tower (although maybe 
you're not using that GPS for time-nuts 1E-20 precision...grin)
The #2 copper was recycled.   The main RF grounding trapeze is tied to 
the grounding electrode system with 1/0, which was also recycled from 
another project.


Re the time-nuttery:  Only 1E-14.  Can't afford better (yet).





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Dr. David Kirkby (Kirkby Microwave Ltd)
On 26 November 2014 at 22:14, Chris Albertson albertson.ch...@gmail.com wrote:
 You CAN (almost) lightening proof your system.

BUT if the almost is not quite enough, one could damage a lot of
expensive test kit.

 Remember that Ethernet is always
 gavalically isolated by transformers

I lost Ethernet ports on

* Sun Blade 2000 workstation
* Sun Ultra 60 workstation
* Sun Netra T1 server
* HP Printer
* ADSL modem

All went at the same time. The next time just the modem went.

But I think I will be using an internal antenna.

Dave
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Martin A Flynn

On 11/26/2014 5:54 PM, Hal Murray wrote:

albertson.ch...@gmail.com said:

The ground rod needs to be bonded to the rest of the building ground system.

How do I do that effectively if the power goes in the front of the building
and the antenna is on the back?
If cost is no object, a ring ground circling the building. Otherwise a 
bonding jumper between the electrical system ground and the antenna 
grounding connection, preferably staying outside the building.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Bob Stewart
Surround your house with a complete loop of #6 wire with 8-10 ft long ground 
rods every 10-12 ft (but no less than 6ft), bonded (clamped) to the ground at 
the service entrance. That's the simple answer.  The somewhat longer answer is 
in a recent copy of the ARRL Handbook.  Some will argue for smaller wire, etc, 
but those are just details.  I am not an expert in this field.

Bob - AE6RV

  From: Hal Murray hmur...@megapathdsl.net
 To: Discussion of precise time and frequency measurement time-nuts@febo.com 
Cc: hmur...@megapathdsl.net 
 Sent: Wednesday, November 26, 2014 4:54 PM
 Subject: Re: [time-nuts] lightening protection of a GPSDO system / optical 
isolated distribution amp
   

albertson.ch...@gmail.com said:
 The ground rod needs to be bonded to the rest of the building ground system.

How do I do that effectively if the power goes in the front of the building 
and the antenna is on the back?



-- 
These are my opinions.  I hate spam.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


  
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Jim Lux

On 11/26/14, 2:14 PM, Chris Albertson wrote:

You CAN (almost) lightening proof your system.  The trick is to give
lightening a low impedence path to grind at very opportunity.

Start with the antenna mast and call.  Use iron pipe for the mast and feed
the antenna cable down the center of the pipe.  Place two large ground
clamps on this pipe and connect a large diameter wire that takes a straight
path to a group rod.This will go a long way to diverting energy to
ground because high voltage likes to flow on the outside of a conductor
which would be the pipe and not so much the antenna cable.


Not so much high voltage, as AC and skin effect.  However, bear in mind 
that lightning has a rise time of a microsecond or so: you can think of 
it having a fundamental of 300-500 kHz (e.g. the first quarter cycle of 
a sinewave), with most of the power below  1MHz.


Skin depth at 1 MHz in copper is 0.065mm.

In iron (using conductivty of 9.6 and relative mu of 1000) skin depth is 
0.005 mm


So, steel/iron pipe is a terrible conductor for a lightning impulse, 
compared to that nice copper coax next to it, or inside it.






The ground rod needs to be bonded to the rest of the building ground system.

Then the antenna cable passes through a metal bulkhead with a bulkhead
connector and all this is also grounded.  After this is might be a high
voltage e on the center conductor.  Use an lightening arrester that is
bolted to the bulkhead.


From a electrical code standpoint, a grounded bulkhead connector isn't 
compliant: you need one of those clamps that attaches to the shield in a 
quasi permanent way. I'm not sure of the entire rationale, but I think 
it's because connectors can become disconnected, but bolted connections 
less so.





At this point you are reasonably safe.  Remember that Ethernet is always
gavalically isolated by transformers


Which won't necessarily stand off a 10 kV lightning impulse. and, of 
course, a common mode impulse carried on both wires of a pair might 
couple via either capacitance, or more likely, through magnetic fields.


the ethernet galvanic isolation does a nice job dealing with the 10s or 
maybe 100V common mode issues, and protects the network if there is an 
internal short in a piece of equipment connected to the network.


Of course, with the increased prevalence of Power Over Ethernet, some 
implementations of which are, shall we say, sketchy, that PoE system 
might be a dandy conductor of transient energy.  For instance, a point 
to point microwave network terminal up on a mast running power for the 
circuit up the network cable.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Jim Lux

On 11/26/14, 2:54 PM, Hal Murray wrote:


albertson.ch...@gmail.com said:

The ground rod needs to be bonded to the rest of the building ground system.


How do I do that effectively if the power goes in the front of the building
and the antenna is on the back?



AWG 6 wire with no breaks or splices between the two.

The goal of bonding all the grounding systems together is not for 
transient suppression.  It's to make sure that there's no DC or line 
frequency potential difference between electrical safety ground at 
various places in the building.


The background on the whole grounding/bonding requirement is more about 
safety when a power carrying conductor, either inside equipment or 
overhead, touches something that people might touch. And, to a lesser 
extent to ensure that if there's an internal short, that the breaker or 
fuse will trip.


NEC requirements for grounding and bonding aren't there for transient 
suppression.


A copy of IEEE 1100 (the Emerald Book) is good reading for the whole 
bonding and equipotential planes, etc.  (unfortunately not free from IEEE).


A good book on transient protection is Ronald Standler's book 
protection of electronic circuits from overvoltages

Something like $20 from Dover...

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


[time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Arthur Dent
Here is a link to a good 12 page description of grounding
practices/requirements.

http://www.reeve.com/Documents/Articles%20Papers/AntennaSystemGroundingRequirements_Reeve.pdf
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Chris Albertson
You really do have to bond the two of them.  The VERY best way is to dig a
trench all the way around the building and install a loop of wire, #8 at
least (although I use much larger wire after the time and money to dug a
trench.)  This wire connects the rods and the water system.  While a full
loop is best yo can simply run a wire to the building's service entrance
but I think code requires these wires to be protected by any of several
methods.

You have to connect the grounds because otherwire you have a problem where
indoors there are two different ground potentials.  The Earth is just that
way, there is or may be a voltage potential between two spots.  There WILL
be a difference during a lightening strike.



On Wed, Nov 26, 2014 at 2:54 PM, Hal Murray hmur...@megapathdsl.net wrote:


 albertson.ch...@gmail.com said:
  The ground rod needs to be bonded to the rest of the building ground
 system.

 How do I do that effectively if the power goes in the front of the building
 and the antenna is on the back?



 --
 These are my opinions.  I hate spam.



 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.




-- 

Chris Albertson
Redondo Beach, California
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Dr. David Kirkby (Kirkby Microwave Ltd)
On 27 Nov 2014 01:14, Chris Albertson albertson.ch...@gmail.com wrote:

 After this minimum you have th think about the probability of a strike.
If
 you live in Orlando Florida then it might be 100% and nearly zero in other
 places and then you ask what the radio equipment cost.   I paid $18 for
my
 Motorola Encore GPS receiver.

Chris,
if a GPS receiver was the only item that would get damaged I would not care.

If it damaged 3 signal generators,  three VNAs, a frequency counter, and a
spectrum analyzer, I would care.

My experience with the lighting going down the telephone line and
destroying a few computers, printer and modem would make me unhappy about
an external antenna.

Nobody has answered my other question - whether one gets a better
disciplined oscillator with an external antenna.

Dave.
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Jim Lux

On 11/26/14, 5:23 PM, Chris Albertson wrote:

On Wed, Nov 26, 2014 at 4:03 PM, Jim Lux jim...@earthlink.net wrote:


On 11/26/14, 2:14 PM, Chris Albertson wrote:


You CAN (almost) lightening proof your system.  The trick is to give
lightening a low impedence path to grind at very opportunity.

Start with the antenna mast and call.  Use iron pipe for the mast and feed
the antenna cable down the center of the pipe.  Place two large ground
clamps on this pipe and connect a large diameter wire that takes a
straight
path to a group rod.This will go a long way to diverting energy to
ground because high voltage likes to flow on the outside of a conductor
which would be the pipe and not so much the antenna cable.



Not so much high voltage, as AC and skin effect.  However, bear in mind
that lightning has a rise time of a microsecond or so: you can think of it
having a fundamental of 300-500 kHz (e.g. the first quarter cycle of a
sinewave), with most of the power below  1MHz.

Skin depth at 1 MHz in copper is 0.065mm.

In iron (using conductivty of 9.6 and relative mu of 1000) skin depth is
0.005 mm

So, steel/iron pipe is a terrible conductor for a lightning impulse,
compared to that nice copper coax next to it, or inside it.



Really?  What you care about is the impedance, not the depth of the skin
effect.   Also not the the coax is NOT exposed to the environment.  Tacitly
the coax comes out from the user side of the antenna, so it never sees
daylight.  The current flows in that first .005mm of steel.   Running the
coax down the side of the pipe would be a really bad idea.



Skin effect greatly affects the resistive impedance.

Compare a copper pipe vs a steel pipe of the same diameter.

The copper is basically conductive ring 0.065 mm thick and resistivity 
of 1.67 and the steel is .005mm thick and resistivity 9.6


So the resistance ratio is 26:1920.. that is 2 orders of magnitude.

However.. the dominant impedance at lightning frequencies (at least for 
copper) is the inductance, which is very weakly dependent on the shape 
and cross-sectional size of the conductor: it's close to 1 uH/meter 
regardless..


A copper pipe that is 2 cm in diameter and 1 meter long has a resistance 
at 1 MHz of 0.004 Ohm


A steel/iron pipe that is 2 cm in diameter and 1 meter long has a 
resistance at 1 MHz of 1.43 Ohm


The inductive impedance is about 6.3 ohms.

So the steel has a somewhat higher impedance than the coax inside it. 
Yeah, there probably is some shielding effect, but I'm going to guess 
that there's some insulating gap between the bottom of antenna and 
top of pipe, although that gap may be bridged by the plasma from your 
lightning strike.


It's just that I'm not sure I'd trust the shielding effect of the 
pipe, nor any preferential current distribution from the magnetic 
fields.  For all one knows, that pipe might wind up filled with a plasma 
of vaporized coax.



I'd just consider the antenna and feedline sacrificial, and worry about 
dealing with the transient at the point of entry to the building, 
assuming that the coax is carrying all of it.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Mark Spencer
Sweet.   I settled on #3 copper for my antenna grounding system on economic 
grounds and had a debate with a residential electrical contractor about 
bonding the antenna ground to the electrical service ground.   The city 
inspector passed the system with the bond installed.

I haven't used poly phasers but do hope to at least stop the house from burning 
down in the event of a lightning strike on the roof mounted antennas.   

I also found that the metallic city water supply pipe is by far the best ground 
I have (at least for 60 cycle AC.) (Using a clamp on meter I can measure an 
appreciable current thru it, unlike the other two grounds.   I presume the 
current is being diverted from the utility neutral and is eventually making 
it's way back to the transformer that powers my house.) I'm glad the water pipe 
is also bonded to the electrical service ground.   I'm happy that I don't have 
any appreciable currents flowing thru my antenna ground.This might be 
something to carefully consider (or possibly have looked at by a pro) if you 
have a really low impedance ground.   I've heard anecdotal accounts of sparks 
occurring when low impedance antenna grounds are connected to an electrical 
service ground.

My usual disclaimer of I'm not an expert in this field, the preceding is only 
my opinion,  and don't rely on this applies.

Mark Spencer

On 2014-11-26, at 2:56 PM, Martin A Flynn mafl...@theflynn.org wrote:

 On 11/26/2014 5:14 PM, Jim Lux wrote:
 On 11/26/14, 2:00 PM, Martin A Flynn wrote:
 The N2MO station has an external GPS antenna on the gable end of the
 building.  It's connected to the polyphaser arrestor with FSJ4-50
 superflex.
 
 The antenna mounting pipe has a #2 ground wire  (33.6 mm/2)  the
 polyphaser has it's own #2 ground wire.  Both connect to an 8' x 5/8
 (2.4m x 16mm) driven ground rod.  The jacket of the superflex is
 grounded with the factoryt Andrew kit as well
 
 Even with the GPS antenna lower in elevation then the HF beam and other
 antenna (with similar protection)  I have concerns about leaving it
 connected all the time.
 AWG #2 seems a tad overkill, the current in a stroke can be carried by AWG 
 #10 without melting, but maybe you had a lot of it around for other reasons. 
  I suspect the coax shield has smaller cross sectional area than AWG #2 and 
 you'll protect your grounding wire by blowing up the coaxgrin. (in fact, 
 looking at the data sheet for FSJ4-50, the DC resistance of the outer 
 conductor is 1 ohm/1000 ft = AWG 10.. it's actually more resistance than the 
 inner conductor (the inner conductor is 0.820ohms/kft, and 0.140 inch in 
 diameter, compare to AWG 10 which is very close to 0.100 inch in diameter).
 
 Hopefully your driven ground rod is bonded to the other system grounds?
 
 I'd worry about multipath from the HF beam and tower (although maybe you're 
 not using that GPS for time-nuts 1E-20 precision...grin)
 The #2 copper was recycled.   The main RF grounding trapeze is tied to the 
 grounding electrode system with 1/0, which was also recycled from another 
 project.
 
 Re the time-nuttery:  Only 1E-14.  Can't afford better (yet).
 
 
 
 
 
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.
 
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Mark Spencer
In my opinion,

I'd be inclined to find a way to run a suitable wire around the building.I 
don't think you want your interior electrical wiring serving as the only bond 
between two different grounds if energy from a lightning strike flows thru your 
antenna feed line and then thru your time nuts gear that probably has a path to 
the other ground thru the wiring in the building.

Other fault conditions that cause significant currents to flow thru your ground 
system could also cause issues if the only bond between the two ground systems 
is thru your house wiring and time nuts gear.

Disclaimer I'm not an electrical engineer or lightning protection expert so 
please don't rely on this comment.



Mark Spencer

On 2014-11-26, at 2:54 PM, Hal Murray hmur...@megapathdsl.net wrote:

 
 albertson.ch...@gmail.com said:
 The ground rod needs to be bonded to the rest of the building ground system.
 
 How do I do that effectively if the power goes in the front of the building 
 and the antenna is on the back?
 
 
 
 -- 
 These are my opinions.  I hate spam.
 
 
 
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.
 
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp

2014-11-26 Thread Bob Camp
Hi

You need a good antenna setup to get a good disciplined oscillator. The bigger 
question is if you *need* the sort of “better” it gives you. If you are running 
a simple TCXO based GPSDO, you will have a number of issues to deal with 
compared to an OCXO or Rb based system. If “better” is an objective, consider 
the entire system. 

Bob

 On Nov 26, 2014, at 7:30 PM, Dr. David Kirkby (Kirkby Microwave Ltd) 
 drkir...@kirkbymicrowave.co.uk wrote:
 
 On 27 Nov 2014 01:14, Chris Albertson albertson.ch...@gmail.com wrote:
 
 After this minimum you have th think about the probability of a strike.
 If
 you live in Orlando Florida then it might be 100% and nearly zero in other
 places and then you ask what the radio equipment cost.   I paid $18 for
 my
 Motorola Encore GPS receiver.
 
 Chris,
 if a GPS receiver was the only item that would get damaged I would not care.
 
 If it damaged 3 signal generators,  three VNAs, a frequency counter, and a
 spectrum analyzer, I would care.
 
 My experience with the lighting going down the telephone line and
 destroying a few computers, printer and modem would make me unhappy about
 an external antenna.
 
 Nobody has answered my other question - whether one gets a better
 disciplined oscillator with an external antenna.
 
 Dave.
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.