Re: [WISPA] Fiber/Copper Combo Wire

2009-05-09 Thread Blair Davis




There is no reason one couldn't do a custom POE that was AC.

A couple thoughts...

To maintain a max input of 48VDC, (to be under the low voltage codes),
and to deliver 50W topside, is going to require a 14-16AWG wire pair
and a 48V 60W supply at the bottom.

I suspect that you will need to get some DC-DC converters in various
sizes to run the equipment up there...


os10ru...@gmail.com wrote:

  Isn't POE DC?

On May 9, 2009, at 5:37 PM, George Rogato wrote:

  
  
Or a person could buy a set of up down transformers to increase the
voltage going up the tower to avoid voltage drop.

Of course, running 110 up to the top is probably easier.

Jack Unger wrote:


  You have the best solution - regulating at the top. Otherwise, as you
state, the voltage at the top will go up when the current load goes
down. The voltage at the top will go down when the current load  
goes up.
MUCH better to regulate at the top...

os10ru...@gmail.com wrote:
  
  
I'd worry about what would happen as the load varies, specifically  
if
the load gets substantially less which could lead to the device
getting overloaded. I'd rather sent up something unregulated and
regulate it at the top.

Greg

On May 8, 2009, at 5:58 PM, Kevin Neal wrote:




  So..what about this...get an adjustable voltage power supply.
Install the
RG6 or whatever coax/wire would handle the load/distance.  Adjust  
the
voltage with a meter up top so that you have ~24-28v at your
equipment?

-Kevin



  

  
  < all previous content "peached" 'cuz we were out of prunes>

  



WISPA Wants You! Join today!
http://signup.wispa.org/


WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

  
  



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/
  







WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

Re: [WISPA] Fiber/Copper Combo Wire

2009-05-09 Thread os10rules
Isn't POE DC?

On May 9, 2009, at 5:37 PM, George Rogato wrote:

> Or a person could buy a set of up down transformers to increase the
> voltage going up the tower to avoid voltage drop.
>
> Of course, running 110 up to the top is probably easier.
>
> Jack Unger wrote:
>> You have the best solution - regulating at the top. Otherwise, as you
>> state, the voltage at the top will go up when the current load goes
>> down. The voltage at the top will go down when the current load  
>> goes up.
>> MUCH better to regulate at the top...
>>
>> os10ru...@gmail.com wrote:
>>> I'd worry about what would happen as the load varies, specifically  
>>> if
>>> the load gets substantially less which could lead to the device
>>> getting overloaded. I'd rather sent up something unregulated and
>>> regulate it at the top.
>>>
>>> Greg
>>>
>>> On May 8, 2009, at 5:58 PM, Kevin Neal wrote:
>>>
>>>
 So..what about this...get an adjustable voltage power supply.
 Install the
 RG6 or whatever coax/wire would handle the load/distance.  Adjust  
 the
 voltage with a meter up top so that you have ~24-28v at your
 equipment?

 -Kevin



>> < all previous content "peached" 'cuz we were out of prunes>
>>
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Fiber/Copper Combo Wire

2009-05-09 Thread George Rogato
Or a person could buy a set of up down transformers to increase the 
voltage going up the tower to avoid voltage drop.

Of course, running 110 up to the top is probably easier.

Jack Unger wrote:
> You have the best solution - regulating at the top. Otherwise, as you 
> state, the voltage at the top will go up when the current load goes 
> down. The voltage at the top will go down when the current load goes up. 
> MUCH better to regulate at the top...
> 
> os10ru...@gmail.com wrote:
>> I'd worry about what would happen as the load varies, specifically if  
>> the load gets substantially less which could lead to the device  
>> getting overloaded. I'd rather sent up something unregulated and  
>> regulate it at the top.
>>
>> Greg
>>
>> On May 8, 2009, at 5:58 PM, Kevin Neal wrote:
>>
>>   
>>> So..what about this...get an adjustable voltage power supply.   
>>> Install the
>>> RG6 or whatever coax/wire would handle the load/distance.  Adjust the
>>> voltage with a meter up top so that you have ~24-28v at your  
>>> equipment?
>>>
>>> -Kevin
>>>
>>>
>>> 
> < all previous content "peached" 'cuz we were out of prunes>
> 



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Fiber/Copper Combo Wire

2009-05-08 Thread Jack Unger
You have the best solution - regulating at the top. Otherwise, as you 
state, the voltage at the top will go up when the current load goes 
down. The voltage at the top will go down when the current load goes up. 
MUCH better to regulate at the top...

os10ru...@gmail.com wrote:
> I'd worry about what would happen as the load varies, specifically if  
> the load gets substantially less which could lead to the device  
> getting overloaded. I'd rather sent up something unregulated and  
> regulate it at the top.
>
> Greg
>
> On May 8, 2009, at 5:58 PM, Kevin Neal wrote:
>
>   
>> So..what about this...get an adjustable voltage power supply.   
>> Install the
>> RG6 or whatever coax/wire would handle the load/distance.  Adjust the
>> voltage with a meter up top so that you have ~24-28v at your  
>> equipment?
>>
>> -Kevin
>>
>>
>> 
< all previous content "peached" 'cuz we were out of prunes>

-- 
Jack Unger - President, Ask-Wi.Com, Inc.
Author - "Deploying License-Free Wireless WANs"
Serving the Broadband Wireless Industry Since 1993
www.ask-wi.com  818-227-4220  jun...@ask-wi.com

"Email spam is just the latest way of asking
for "Forgiveness" instead of asking for "Permission". 







WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Fiber/Copper Combo Wire

2009-05-08 Thread Scott Reed
Yep, unless it isn't 24V equipment.  :)

Kevin Neal wrote:
> So..what about this...get an adjustable voltage power supply.  Install the
> RG6 or whatever coax/wire would handle the load/distance.  Adjust the
> voltage with a meter up top so that you have ~24-28v at your equipment?
>
> -Kevin
>  
>
> -Original Message-
> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
> Behalf Of David Hulsebus
> Sent: Friday, May 08, 2009 2:59 PM
> To: WISPA General List
> Subject: Re: [WISPA] Fiber/Copper Combo Wire
>
> Ive used RG8 coax in the past to deliver 24V DC to about 600ft, but not at
> 1500ft. RG6 has significantly less loss over distance than 24AWG wire.
>
> Dave Hulsebus
>
> Scott Reed wrote:
>   
>> Belden makes this, but I don't have a number for it.
>>
>> I would be really cautious if they are running 1500' single run for 
>> POE.  Need to do the voltage loss calculation to be sure to use the 
>> correct power supply.
>>
>> Jeff Broadwick wrote:
>>   
>> 
>>>  
>>> Hi All,
>>>
>>> One of my customers is looking for these critters for a 1500 foot tower.
>>> Gig fiber for the data, copper for POE.
>>>
>>> Any ideas?
>>>
>>> Regards,
>>>
>>> Jeff
>>> ImageStream
>>>
>>>
>>>
>>> -
>>> ---
>>> WISPA Wants You! Join today!
>>> http://signup.wispa.org/
>>> -
>>> ---
>>>  
>>> WISPA Wireless List: wireless@wispa.org
>>>
>>> Subscribe/Unsubscribe:
>>> http://lists.wispa.org/mailman/listinfo/wireless
>>>
>>> Archives: http://lists.wispa.org/pipermail/wireless/
>>>   
>>> -
>>> ---
>>>
>>>
>>> No virus found in this incoming message.
>>> Checked by AVG - www.avg.com
>>> Version: 8.5.325 / Virus Database: 270.12.21/2104 - Release Date: 
>>> 05/08/09 06:34:00
>>>
>>>   
>>> 
>>>   
>>   
>> 
>
>
> 
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
> 
>  
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/
>
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>  
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/
>   
> 
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com 
> Version: 8.5.325 / Virus Database: 270.12.21/2104 - Release Date: 05/08/09 
> 06:34:00
>
>   

-- 
Scott Reed
Sr. Systems Engineer
GAB Midwest
1-800-363-1544 x4000
Cell: 260-273-7239




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Fiber/Copper Combo Wire

2009-05-08 Thread os10rules
I'd worry about what would happen as the load varies, specifically if  
the load gets substantially less which could lead to the device  
getting overloaded. I'd rather sent up something unregulated and  
regulate it at the top.

Greg

On May 8, 2009, at 5:58 PM, Kevin Neal wrote:

> So..what about this...get an adjustable voltage power supply.   
> Install the
> RG6 or whatever coax/wire would handle the load/distance.  Adjust the
> voltage with a meter up top so that you have ~24-28v at your  
> equipment?
>
> -Kevin
>
>
> -Original Message-
> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]  
> On
> Behalf Of David Hulsebus
> Sent: Friday, May 08, 2009 2:59 PM
> To: WISPA General List
> Subject: Re: [WISPA] Fiber/Copper Combo Wire
>
> Ive used RG8 coax in the past to deliver 24V DC to about 600ft, but  
> not at
> 1500ft. RG6 has significantly less loss over distance than 24AWG wire.
>
> Dave Hulsebus
>
> Scott Reed wrote:
>> Belden makes this, but I don't have a number for it.
>>
>> I would be really cautious if they are running 1500' single run for
>> POE.  Need to do the voltage loss calculation to be sure to use the
>> correct power supply.
>>
>> Jeff Broadwick wrote:
>>
>>>
>>> Hi All,
>>>
>>> One of my customers is looking for these critters for a 1500 foot  
>>> tower.
>>> Gig fiber for the data, copper for POE.
>>>
>>> Any ideas?
>>>
>>> Regards,
>>>
>>> Jeff
>>> ImageStream
>>>
>>>
>>>
>>> -
>>> ---
>>> WISPA Wants You! Join today!
>>> http://signup.wispa.org/
>>> -
>>> ---
>>>
>>> WISPA Wireless List: wireless@wispa.org
>>>
>>> Subscribe/Unsubscribe:
>>> http://lists.wispa.org/mailman/listinfo/wireless
>>>
>>> Archives: http://lists.wispa.org/pipermail/wireless/
>>>
>>> -
>>> ---
>>>
>>>
>>> No virus found in this incoming message.
>>> Checked by AVG - www.avg.com
>>> Version: 8.5.325 / Virus Database: 270.12.21/2104 - Release Date:
>>> 05/08/09 06:34:00
>>>
>>>
>>>
>>
>>
>
>
> 
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/
>
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Fiber/Copper Combo Wire

2009-05-08 Thread Kevin Neal
So..what about this...get an adjustable voltage power supply.  Install the
RG6 or whatever coax/wire would handle the load/distance.  Adjust the
voltage with a meter up top so that you have ~24-28v at your equipment?

-Kevin
 

-Original Message-
From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of David Hulsebus
Sent: Friday, May 08, 2009 2:59 PM
To: WISPA General List
Subject: Re: [WISPA] Fiber/Copper Combo Wire

Ive used RG8 coax in the past to deliver 24V DC to about 600ft, but not at
1500ft. RG6 has significantly less loss over distance than 24AWG wire.

Dave Hulsebus

Scott Reed wrote:
> Belden makes this, but I don't have a number for it.
>
> I would be really cautious if they are running 1500' single run for 
> POE.  Need to do the voltage loss calculation to be sure to use the 
> correct power supply.
>
> Jeff Broadwick wrote:
>   
>>  
>> Hi All,
>>
>> One of my customers is looking for these critters for a 1500 foot tower.
>> Gig fiber for the data, copper for POE.
>>
>> Any ideas?
>>
>> Regards,
>>
>> Jeff
>> ImageStream
>>
>>
>>
>> -
>> ---
>> WISPA Wants You! Join today!
>> http://signup.wispa.org/
>> -
>> ---
>>  
>> WISPA Wireless List: wireless@wispa.org
>>
>> Subscribe/Unsubscribe:
>> http://lists.wispa.org/mailman/listinfo/wireless
>>
>> Archives: http://lists.wispa.org/pipermail/wireless/
>>   
>> -
>> ---
>>
>>
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com
>> Version: 8.5.325 / Virus Database: 270.12.21/2104 - Release Date: 
>> 05/08/09 06:34:00
>>
>>   
>> 
>
>   




WISPA Wants You! Join today!
http://signup.wispa.org/


 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Fiber/Copper Combo Wire

2009-05-08 Thread David Hulsebus
Ive used RG8 coax in the past to deliver 24V DC to about 600ft, but not 
at 1500ft. RG6 has significantly less loss over distance than 24AWG wire.

Dave Hulsebus

Scott Reed wrote:
> Belden makes this, but I don't have a number for it.
>
> I would be really cautious if they are running 1500' single run for 
> POE.  Need to do the voltage loss calculation to be sure to use the 
> correct power supply.
>
> Jeff Broadwick wrote:
>   
>>  
>> Hi All,
>>
>> One of my customers is looking for these critters for a 1500 foot tower.
>> Gig fiber for the data, copper for POE.
>>
>> Any ideas?
>>
>> Regards,
>>
>> Jeff
>> ImageStream
>>
>>
>>
>> 
>> WISPA Wants You! Join today!
>> http://signup.wispa.org/
>> 
>>  
>> WISPA Wireless List: wireless@wispa.org
>>
>> Subscribe/Unsubscribe:
>> http://lists.wispa.org/mailman/listinfo/wireless
>>
>> Archives: http://lists.wispa.org/pipermail/wireless/
>>   
>> 
>>
>>
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com 
>> Version: 8.5.325 / Virus Database: 270.12.21/2104 - Release Date: 05/08/09 
>> 06:34:00
>>
>>   
>> 
>
>   



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Fiber/Copper Combo Wire

2009-05-08 Thread Scott Reed
Belden makes this, but I don't have a number for it.

I would be really cautious if they are running 1500' single run for 
POE.  Need to do the voltage loss calculation to be sure to use the 
correct power supply.

Jeff Broadwick wrote:
>  
> Hi All,
>
> One of my customers is looking for these critters for a 1500 foot tower.
> Gig fiber for the data, copper for POE.
>
> Any ideas?
>
> Regards,
>
> Jeff
> ImageStream
>
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>  
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/
>   
> 
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com 
> Version: 8.5.325 / Virus Database: 270.12.21/2104 - Release Date: 05/08/09 
> 06:34:00
>
>   

-- 
Scott Reed
Sr. Systems Engineer
GAB Midwest
1-800-363-1544 x4000
Cell: 260-273-7239




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


[WISPA] Fiber/Copper Combo Wire

2009-05-08 Thread Jeff Broadwick
 
Hi All,

One of my customers is looking for these critters for a 1500 foot tower.
Gig fiber for the data, copper for POE.

Any ideas?

Regards,

Jeff
ImageStream




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/