Re: [WISPA] Low cost generator

2007-07-09 Thread Mark Nash
Just got off a vacation and picked up this thread.

I have the same off  on problem when I put my UPS inline on generator
power.  The batteries do not charge, instead they drain, even when adjusting
the sensitivity.

So I guess I have a 2-part question...

1. What portable gasoline generators have people been successful with using
the APC Smart-UPS 700VA or higher?  Successful meaning the generator
provides power and the UPS charges its batteries.

2. It's still not clear whether or not these larger generators with
automatic transfer switches can run clean enough power to do the same?

JohnnyO I'd like to hear about what you've got along these lines that's
affordable.

Thanks.

Mark Nash
UnwiredOnline.Net
350 Holly Street
Junction City, OR 97448
http://www.uwol.net
541-998-
541-998-5599 fax

- Original Message - 
From: Mac Dearman [EMAIL PROTECTED]
To: 'WISPA General List' wireless@wispa.org
Sent: Monday, July 02, 2007 6:22 PM
Subject: RE: [WISPA] Low cost generator


 We have the exact same generator as well - - only a 16KW  - - we too
ordered
 it from Lowes and it was $2900.00 with a $200.00 rebate. It was drop
shipped
 to the NOC - - -and no - - - - we haven't had a single power outage either
 since we bought and installed it 8 months ago :-)

  I hear it fire up and run on occasions, but I am still waiting to see it
 fire up when it really counts.

 Mac




 *-Original Message-
 *From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
 *Behalf Of [EMAIL PROTECTED]
 *Sent: Sunday, July 01, 2007 10:56 PM
 *To: WISPA General List
 *Subject: Re: [WISPA] Low cost generator
 *
 * I'm in the market for a generator and came across this one.
 *
 *[ snipped link ]
 *
 *That's either the very same generator I have, or very close to it.
 *
 *(Actually, it's just very close. Ours can run on either propane or
 *natural gas, and it's presently wired up for the latter.)
 *
 *Sadly, in the five months since we moved to our new office, with that
 *fancy new generator, we haven't had a single power outage. Not so much
 *as
 *a flicker. It pops on once a week for its exercise cycle, and I've done
 *the flip the big switch and make sure the generator fires up test a
 *couple times, so I assume it works.)
 *
 *As with any big purchase, shop around. Ours was $500 cheaper than the
 *price on that Web site; we just had Lowe's special-order it for us.
 *
 *David Smith
 *MVN.net
 *
 *--
 *WISPA Wireless List: wireless@wispa.org
 *
 *Subscribe/Unsubscribe:
 *http://lists.wispa.org/mailman/listinfo/wireless
 *
 *Archives: http://lists.wispa.org/pipermail/wireless/

 -- 
 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/




Would you like to see your advertisement here?  Let the WISPA Board know your 
feelings about allowing advertisements on the free WISPA lists.  The current 
Board is taking this under consideration at this time.  We want to know your 
thoughts.

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-09 Thread Jason




Are the generators you guys have trouble with the inverter type? These
are basically an alternator and an inverter tied together. I know
Honda makes a number of them. The inverter type generates a square
wave to simulate a sine wave, which may cause your trouble. 

Jason

Mark Nash wrote:

  Just got off a vacation and picked up this thread.

I have the same "off  on" problem when I put my UPS inline on generator
power.  The batteries do not charge, instead they drain, even when adjusting
the sensitivity.

So I guess I have a 2-part question...

1. What portable gasoline generators have people been successful with using
the APC Smart-UPS 700VA or higher?  Successful meaning the generator
provides power and the UPS charges its batteries.

2. It's still not clear whether or not these larger generators with
automatic transfer switches can run clean enough power to do the same?

JohnnyO I'd like to hear about what you've got along these lines that's
affordable.

Thanks.

Mark Nash
UnwiredOnline.Net
350 Holly Street
Junction City, OR 97448
http://www.uwol.net
541-998-
541-998-5599 fax

- Original Message - 
From: "Mac Dearman" [EMAIL PROTECTED]
To: "'WISPA General List'" wireless@wispa.org
Sent: Monday, July 02, 2007 6:22 PM
Subject: RE: [WISPA] Low cost generator


  
  
We have the exact same generator as well - - only a 16KW  - - we too

  
  ordered
  
  
it from Lowes and it was $2900.00 with a $200.00 rebate. It was drop

  
  shipped
  
  
to the NOC - - -and no - - - - we haven't had a single power outage either
since we bought and installed it 8 months ago :-)

 I hear it fire up and run on occasions, but I am still waiting to see it
fire up when it really counts.

Mac




*-Original Message-
*From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED]] On
*Behalf Of [EMAIL PROTECTED]
*Sent: Sunday, July 01, 2007 10:56 PM
*To: WISPA General List
*Subject: Re: [WISPA] Low cost generator
*
* I'm in the market for a generator and came across this one.
*
*[ snipped link ]
*
*That's either the very same generator I have, or very close to it.
*
*(Actually, it's just "very close." Ours can run on either propane or
*natural gas, and it's presently wired up for the latter.)
*
*Sadly, in the five months since we moved to our new office, with that
*fancy new generator, we haven't had a single power outage. Not so much
*as
*a flicker. It pops on once a week for its exercise cycle, and I've done
*the "flip the big switch and make sure the generator fires up" test a
*couple times, so I assume it works.)
*
*As with any big purchase, shop around. Ours was $500 cheaper than the
*price on that Web site; we just had Lowe's special-order it for us.
*
*David Smith
*MVN.net
*
*--
*WISPA Wireless List: wireless@wispa.org
*
*Subscribe/Unsubscribe:
*http://lists.wispa.org/mailman/listinfo/wireless
*
*Archives: http://lists.wispa.org/pipermail/wireless/

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


  
  


Would you like to see your advertisement here?  Let the WISPA Board know your feelings about allowing advertisements on the free WISPA lists.  The current Board is taking this under consideration at this time.  We want to know your thoughts.

  




Would you like to see your advertisement here?  Let the WISPA Board know your 
feelings about allowing advertisements on the free WISPA lists.  The current 
Board is taking this under consideration at this time.  We want to know your 
thoughts.

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

Re: [WISPA] Low cost generator

2007-07-09 Thread Scott Lambert
On Mon, Jul 09, 2007 at 10:19:19AM -0700, Mark Nash wrote:
 Just got off a vacation and picked up this thread.
 
 I have the same off  on problem when I put my UPS inline on generator
 power.  The batteries do not charge, instead they drain, even when adjusting
 the sensitivity.

Have you measured the voltage coming out of the generator?

-- 
Scott LambertKC5MLE   Unix SysAdmin
[EMAIL PROTECTED]


Would you like to see your advertisement here?  Let the WISPA Board know your 
feelings about allowing advertisements on the free WISPA lists.  The current 
Board is taking this under consideration at this time.  We want to know your 
thoughts.

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-09 Thread Tom DeReggi

Also...

What generator models/brands have you used with the APC700 UPSs, and had 
troubles?


Maybe we can compare similarities to the various Generators that gave 
problems.
To identify what we are dealing with. It has not been conclusively defined 
for sure whether this is a UPS or Generator problem.


I recognize that the original post had to do with finding a generator that 
worked with existing deployed APC UPSs.
But I have not seen these results with the generators that I have used and 
our Triplite Smart UPSs.  Doesn;t mean there couldn;t be a problem, nor am I 
contesting that the APC700 has a problem with some generators.


This is just a scary topic for me, as I was about to go buy a bunch of APC 
smart 700 UPSs, and thinking maybe I should reconsider staying with 
Tripplite.


Tom DeReggi
RapidDSL  Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: Scott Lambert [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Monday, July 09, 2007 5:30 PM
Subject: Re: [WISPA] Low cost generator



On Mon, Jul 09, 2007 at 10:19:19AM -0700, Mark Nash wrote:

Just got off a vacation and picked up this thread.

I have the same off  on problem when I put my UPS inline on generator
power.  The batteries do not charge, instead they drain, even when 
adjusting

the sensitivity.


Have you measured the voltage coming out of the generator?

--
Scott LambertKC5MLE   Unix 
SysAdmin

[EMAIL PROTECTED]


Would you like to see your advertisement here?  Let the WISPA Board know 
your feelings about allowing advertisements on the free WISPA lists.  The 
current Board is taking this under consideration at this time.  We want to 
know your thoughts.


--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


--
Internal Virus Database is out-of-date.
Checked by AVG Free Edition.
Version: 7.5.472 / Virus Database: 269.9.6/865 - Release Date: 6/24/2007 
8:33 AM






Would you like to see your advertisement here?  Let the WISPA Board know your 
feelings about allowing advertisements on the free WISPA lists.  The current 
Board is taking this under consideration at this time.  We want to know your 
thoughts.

--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-02 Thread David E. Smith
Brad Belton wrote:
 So, you bought this LP  Natural Gas generator for $1460 delivered,
 including tax and transfer switch?

Not quite. I was going on the price posted with the OP's link, which had
a displayed price of about $3800 (at the time I looked at it, at least).
That unit can run on either propane or natural gas, out of the box (as
it were).

We paid about $3000 plus sales tax and delivery, which made it around
$3200, including the transfer switch and sundry bits.

I was surprised to find a good price on a generator at Lowe's, but then
I always thought of Lowe's as more of a home improvement store, and
didn't expect them to carry things this big. (Maybe I'm just naive or
something, dunno.)

David Smith
MVN.net
-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


RE: [WISPA] Low cost generator

2007-07-02 Thread Ralph
We've used the Guardians (Generac) from Home Depot.  Work fine.
Every one I have ever seen came with the transfer switch.
Best deal was a 12Kw I got that was brand new, but the transfer switch and
the top of the generator were slightly dented. Seems like I gave $1500.00
for it. HD said it was 400.00 below cost.

I have been told by the HD folks that unless you have it installed by their
folks, the warranty is void, though. I am not sure how true that is.  I
don't think they (HD) sell them without installation.

Ralph



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of David E. Smith
Sent: Monday, July 02, 2007 9:26 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

Brad Belton wrote:
 So, you bought this LP  Natural Gas generator for $1460 delivered,
 including tax and transfer switch?

Not quite. I was going on the price posted with the OP's link, which had
a displayed price of about $3800 (at the time I looked at it, at least).
That unit can run on either propane or natural gas, out of the box (as
it were).

We paid about $3000 plus sales tax and delivery, which made it around
$3200, including the transfer switch and sundry bits.

I was surprised to find a good price on a generator at Lowe's, but then
I always thought of Lowe's as more of a home improvement store, and
didn't expect them to carry things this big. (Maybe I'm just naive or
something, dunno.)

David Smith
MVN.net

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


RE: [WISPA] Low cost generator

2007-07-02 Thread Brad Belton
David,

Oh, ok...I missed the original post link to the 3800.00 generator.  After
poking around on the www.electricgeneratorsdirect.com site I came across the
$1959.00 7kW LP  Natural gas genset delivered, tax included, with transfer
switch and $40 check discount.

I'm inclined to bite off on that deal if I knew for certain all my APC's
(500VA and greater) would be happy with it.  grin


Ralph,

Kudos on a great score at Home Depot!  Gotta love a motivated big box
manager when in their eyes they have an albatross SKU.


Best,


Brad



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Ralph
Sent: Monday, July 02, 2007 9:33 AM
To: 'WISPA General List'
Subject: RE: [WISPA] Low cost generator

We've used the Guardians (Generac) from Home Depot.  Work fine.
Every one I have ever seen came with the transfer switch.
Best deal was a 12Kw I got that was brand new, but the transfer switch and
the top of the generator were slightly dented. Seems like I gave $1500.00
for it. HD said it was 400.00 below cost.

I have been told by the HD folks that unless you have it installed by their
folks, the warranty is void, though. I am not sure how true that is.  I
don't think they (HD) sell them without installation.

Ralph



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of David E. Smith
Sent: Monday, July 02, 2007 9:26 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

Brad Belton wrote:
 So, you bought this LP  Natural Gas generator for $1460 delivered,
 including tax and transfer switch?

Not quite. I was going on the price posted with the OP's link, which had
a displayed price of about $3800 (at the time I looked at it, at least).
That unit can run on either propane or natural gas, out of the box (as
it were).

We paid about $3000 plus sales tax and delivery, which made it around
$3200, including the transfer switch and sundry bits.

I was surprised to find a good price on a generator at Lowe's, but then
I always thought of Lowe's as more of a home improvement store, and
didn't expect them to carry things this big. (Maybe I'm just naive or
something, dunno.)

David Smith
MVN.net

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


RE: [WISPA] Low cost generator

2007-07-02 Thread Justin S. Wilson
Talk with JohnnyO. He has some industrial grade generators with ultra low
hours, low rpm running, etc. They put the Home Depot ones to shame and
probably not that much more.

Justin

---
Justin S. Wilson [EMAIL PROTECTED]
Technology Services - WISP Consulting - Tower Services
WEB: http://www.mtin.net
WEB: http://www.metrospan.net
WEB: http://www.findfastinternet.com


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Brad Belton
Sent: Monday, July 02, 2007 11:37 AM
To: 'WISPA General List'
Subject: RE: [WISPA] Low cost generator

David,

Oh, ok...I missed the original post link to the 3800.00 generator.  After
poking around on the www.electricgeneratorsdirect.com site I came across the
$1959.00 7kW LP  Natural gas genset delivered, tax included, with transfer
switch and $40 check discount.

I'm inclined to bite off on that deal if I knew for certain all my APC's
(500VA and greater) would be happy with it.  grin


Ralph,

Kudos on a great score at Home Depot!  Gotta love a motivated big box
manager when in their eyes they have an albatross SKU.


Best,


Brad



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Ralph
Sent: Monday, July 02, 2007 9:33 AM
To: 'WISPA General List'
Subject: RE: [WISPA] Low cost generator

We've used the Guardians (Generac) from Home Depot.  Work fine.
Every one I have ever seen came with the transfer switch.
Best deal was a 12Kw I got that was brand new, but the transfer switch and
the top of the generator were slightly dented. Seems like I gave $1500.00
for it. HD said it was 400.00 below cost.

I have been told by the HD folks that unless you have it installed by their
folks, the warranty is void, though. I am not sure how true that is.  I
don't think they (HD) sell them without installation.

Ralph



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of David E. Smith
Sent: Monday, July 02, 2007 9:26 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

Brad Belton wrote:
 So, you bought this LP  Natural Gas generator for $1460 delivered,
 including tax and transfer switch?

Not quite. I was going on the price posted with the OP's link, which had
a displayed price of about $3800 (at the time I looked at it, at least).
That unit can run on either propane or natural gas, out of the box (as
it were).

We paid about $3000 plus sales tax and delivery, which made it around
$3200, including the transfer switch and sundry bits.

I was surprised to find a good price on a generator at Lowe's, but then
I always thought of Lowe's as more of a home improvement store, and
didn't expect them to carry things this big. (Maybe I'm just naive or
something, dunno.)

David Smith
MVN.net

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-02 Thread JohnnyO

Hey Brad - Being George don't wanna call me You call me LOL

JohnnyO
337-764-5953

ps. call me after 5pm today .. I may have something you may 
want...maybe :)



- Original Message - 
From: Brad Belton [EMAIL PROTECTED]

To: 'WISPA General List' wireless@wispa.org
Sent: Monday, July 02, 2007 10:37 AM
Subject: RE: [WISPA] Low cost generator


David,

Oh, ok...I missed the original post link to the 3800.00 generator.  After
poking around on the www.electricgeneratorsdirect.com site I came across the
$1959.00 7kW LP  Natural gas genset delivered, tax included, with transfer
switch and $40 check discount.

I'm inclined to bite off on that deal if I knew for certain all my APC's
(500VA and greater) would be happy with it.  grin


Ralph,

Kudos on a great score at Home Depot!  Gotta love a motivated big box
manager when in their eyes they have an albatross SKU.


Best,


Brad



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Ralph
Sent: Monday, July 02, 2007 9:33 AM
To: 'WISPA General List'
Subject: RE: [WISPA] Low cost generator

We've used the Guardians (Generac) from Home Depot.  Work fine.
Every one I have ever seen came with the transfer switch.
Best deal was a 12Kw I got that was brand new, but the transfer switch and
the top of the generator were slightly dented. Seems like I gave $1500.00
for it. HD said it was 400.00 below cost.

I have been told by the HD folks that unless you have it installed by their
folks, the warranty is void, though. I am not sure how true that is.  I
don't think they (HD) sell them without installation.

Ralph



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of David E. Smith
Sent: Monday, July 02, 2007 9:26 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

Brad Belton wrote:

So, you bought this LP  Natural Gas generator for $1460 delivered,
including tax and transfer switch?


Not quite. I was going on the price posted with the OP's link, which had
a displayed price of about $3800 (at the time I looked at it, at least).
That unit can run on either propane or natural gas, out of the box (as
it were).

We paid about $3000 plus sales tax and delivery, which made it around
$3200, including the transfer switch and sundry bits.

I was surprised to find a good price on a generator at Lowe's, but then
I always thought of Lowe's as more of a home improvement store, and
didn't expect them to carry things this big. (Maybe I'm just naive or
something, dunno.)

David Smith
MVN.net

--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


RE: [WISPA] Low cost generator

2007-07-02 Thread Justin S. Wilson
You could always buy a Toyota Prius and use it as a generator:

http://www.wikihow.com/Use-a-Toyota-Prius-As-a-Backup-Generator



---
Justin S. Wilson [EMAIL PROTECTED]
Technology Services - WISP Consulting - Tower Services
WEB: http://www.mtin.net
WEB: http://www.metrospan.net
WEB: http://www.findfastinternet.com



-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-02 Thread George Rogato

I called and got voice mail for someone named Mike?


JohnnyO wrote:

Hey Brad - Being George don't wanna call me You call me LOL

JohnnyO
337-764-5953

ps. call me after 5pm today .. I may have something you may 
want...maybe :)



- Original Message - From: Brad Belton [EMAIL PROTECTED]
To: 'WISPA General List' wireless@wispa.org
Sent: Monday, July 02, 2007 10:37 AM
Subject: RE: [WISPA] Low cost generator


David,

Oh, ok...I missed the original post link to the 3800.00 generator.  After
poking around on the www.electricgeneratorsdirect.com site I came across 
the

$1959.00 7kW LP  Natural gas genset delivered, tax included, with transfer
switch and $40 check discount.

I'm inclined to bite off on that deal if I knew for certain all my APC's
(500VA and greater) would be happy with it.  grin


Ralph,

Kudos on a great score at Home Depot!  Gotta love a motivated big box
manager when in their eyes they have an albatross SKU.


Best,


Brad



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Ralph
Sent: Monday, July 02, 2007 9:33 AM
To: 'WISPA General List'
Subject: RE: [WISPA] Low cost generator

We've used the Guardians (Generac) from Home Depot.  Work fine.
Every one I have ever seen came with the transfer switch.
Best deal was a 12Kw I got that was brand new, but the transfer switch and
the top of the generator were slightly dented. Seems like I gave $1500.00
for it. HD said it was 400.00 below cost.

I have been told by the HD folks that unless you have it installed by their
folks, the warranty is void, though. I am not sure how true that is.  I
don't think they (HD) sell them without installation.

Ralph



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of David E. Smith
Sent: Monday, July 02, 2007 9:26 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

Brad Belton wrote:

So, you bought this LP  Natural Gas generator for $1460 delivered,
including tax and transfer switch?


Not quite. I was going on the price posted with the OP's link, which had
a displayed price of about $3800 (at the time I looked at it, at least).
That unit can run on either propane or natural gas, out of the box (as
it were).

We paid about $3000 plus sales tax and delivery, which made it around
$3200, including the transfer switch and sundry bits.

I was surprised to find a good price on a generator at Lowe's, but then
I always thought of Lowe's as more of a home improvement store, and
didn't expect them to carry things this big. (Maybe I'm just naive or
something, dunno.)

David Smith
MVN.net



--
George Rogato

Welcome to WISPA

www.wispa.org

http://signup.wispa.org/
--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


RE: [WISPA] Low cost generator

2007-07-02 Thread Mac Dearman
We have the exact same generator as well - - only a 16KW  - - we too ordered
it from Lowes and it was $2900.00 with a $200.00 rebate. It was drop shipped
to the NOC - - -and no - - - - we haven't had a single power outage either
since we bought and installed it 8 months ago :-)

 I hear it fire up and run on occasions, but I am still waiting to see it
fire up when it really counts.

Mac 




*-Original Message-
*From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
*Behalf Of [EMAIL PROTECTED]
*Sent: Sunday, July 01, 2007 10:56 PM
*To: WISPA General List
*Subject: Re: [WISPA] Low cost generator
*
* I'm in the market for a generator and came across this one.
*
*[ snipped link ]
*
*That's either the very same generator I have, or very close to it.
*
*(Actually, it's just very close. Ours can run on either propane or
*natural gas, and it's presently wired up for the latter.)
*
*Sadly, in the five months since we moved to our new office, with that
*fancy new generator, we haven't had a single power outage. Not so much
*as
*a flicker. It pops on once a week for its exercise cycle, and I've done
*the flip the big switch and make sure the generator fires up test a
*couple times, so I assume it works.)
*
*As with any big purchase, shop around. Ours was $500 cheaper than the
*price on that Web site; we just had Lowe's special-order it for us.
*
*David Smith
*MVN.net
*
*--
*WISPA Wireless List: wireless@wispa.org
*
*Subscribe/Unsubscribe:
*http://lists.wispa.org/mailman/listinfo/wireless
*
*Archives: http://lists.wispa.org/pipermail/wireless/

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-02 Thread John Thomas
If you are serious about backup power, here is some equipment you might 
consider;


http://www.xantrex.com/web/id/42/p/1/pt/10/product.asp

or

http://www.xantrex.com/web/id/44/p/1/pt/8/product.asp

or

http://www.outbackpower.com/Backup.htm

John


George Rogato wrote:
If it was just for radios, I'd be just using ups with extra batteries, 
but it's actually for a small data room with a half a dozen or more 
servers and some pc routers etc as well as couple of radios.


Right now we are just using ups for each server, but they don't last 
long, they just help if the power blinks or is out for a short time.


But if the power is out for a few hours, I'd like to keep operating.


Tom DeReggi wrote:

George,

We investigated these units about 4 years ago, and they were our 
first pick for converting to Propaine backup.
However, at the time we decided against it for cost reasons. We did 
not need 16Kwatt and we were not aware of a 7Kwatt model at that time.
The $3500 for the 16K base unit is not the only cost. The autotranser 
switch added about $500, and then the Propain Tank is also an 
additional cost, but more importantly, the second we used Propaine in 
a cmmercial building, we needed a licensed Propain installer to do 
the work, to meet landlords requirements, which added another grand 
or two.


We instead installed Triplite 3500 watt power inverters $500 + 8 high 
end batteries (CD150AH batteries @ $350 each, but have a 10year + 
lifespan).


The arguement was that generators can be finicky, sometimes not 
starting on demand, if not routinely tested and started, and with the 
battery inverter solution we also were bypassing a high UPS cost, 
which is high for 3500watt rated units. So we solved our problem for 
3 grand, instead of 6 grand after all considered, said, and done.


Now with that said. Seeing a 7Kwatt unit for only $2000, that 
changes everything! It would definately be more cost effective doing 
the generator instead of batteries.


Tom DeReggi
RapidDSL  Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - From: George Rogato 
[EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Saturday, June 30, 2007 12:27 PM
Subject: [WISPA] Low cost generator


http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id=538 



I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd 
share it with the list.


--
George Rogato

Welcome to WISPA

www.wispa.org

http://signup.wispa.org/
--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


--
No virus found in this incoming message.
Checked by AVG Free Edition. Version: 7.5.472 / Virus Database: 
269.9.6/865 - Release Date: 6/24/2007 8:33 AM









--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-01 Thread Peter R.

You could just add a line conditioner.


Brad Belton wrote:


We have found many (most all?) 10kW job site type generators do not work
well if at all with APC UPS.  In the event of a power failure we simply rent
a 25kW towable diesel generator.  Granted 25kW is way overkill for most any
HUB site, but apparently the larger generators provide cleaner power that
the APC UPS's are happy with.

Does anyone have one of these 7kW Guardian standby generators in use with
APC UPS's?  $1999.00 delivered with transfer switch is a pretty strong deal!

Best,


Brad
 


--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


RE: [WISPA] Low cost generator

2007-07-01 Thread Brad Belton
Do you mean something like this:

http://cgi.ebay.com/ws/eBayISAPI.dll?ViewItemitem=150135562844

This idea actually came up as a possible idea between another ISP and me not
long ago.  I can get the 5605 joule rated version (looks identical to the
one listed above) for about $100.00.  

Brad


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Peter R.
Sent: Sunday, July 01, 2007 10:55 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

You could just add a line conditioner.


Brad Belton wrote:

We have found many (most all?) 10kW job site type generators do not work
well if at all with APC UPS.  In the event of a power failure we simply
rent
a 25kW towable diesel generator.  Granted 25kW is way overkill for most any
HUB site, but apparently the larger generators provide cleaner power that
the APC UPS's are happy with.

Does anyone have one of these 7kW Guardian standby generators in use with
APC UPS's?  $1999.00 delivered with transfer switch is a pretty strong
deal!

Best,


Brad
  

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


RE: [WISPA] Low cost generator

2007-07-01 Thread Brad Belton
This is true on the larger more expensive APC UPSs, but the smaller 500 -
750VA models don't have this feature, do they?

 

Brad

 

 

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Travis Johnson
Sent: Saturday, June 30, 2007 11:57 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

 

Brad,

You can adjust the sensitivity of the APC UPS's to handle just about any
type of incoming power. We have run a tower off a cheap Home Depot 2000watt
by adjusting the APC so it would not keep switching off an on.

Travis
Microserv

Brad Belton wrote: 

We have found many (most all?) 10kW job site type generators do not work
well if at all with APC UPS.  In the event of a power failure we simply rent
a 25kW towable diesel generator.  Granted 25kW is way overkill for most any
HUB site, but apparently the larger generators provide cleaner power that
the APC UPS's are happy with.
 
Does anyone have one of these 7kW Guardian standby generators in use with
APC UPS's?  $1999.00 delivered with transfer switch is a pretty strong deal!
 
Best,
 
 
Brad
 
 
 
 
 
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Scott Reed
Sent: Saturday, June 30, 2007 11:30 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator
 
The Guardian comes as small as 7KW for about $2100 and goes up a long 
way from there.
I have seen Guardians at cell sites and waste water lift stations around 
here.
 
George Rogato wrote:
  
http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id
=538 
  

 
I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd 
share it with the list.
 


 
  
--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-01 Thread Travis Johnson
Any of the Smart-UPS units have this option. There is a little 
push-button on the back that you can change the sensitivity without 
having to use the software.


Travis
Microserv

Brad Belton wrote:

This is true on the larger more expensive APC UPSs, but the smaller 500 -
750VA models don't have this feature, do they?

 


Brad

 

 


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Travis Johnson
Sent: Saturday, June 30, 2007 11:57 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

 


Brad,

You can adjust the sensitivity of the APC UPS's to handle just about any
type of incoming power. We have run a tower off a cheap Home Depot 2000watt
by adjusting the APC so it would not keep switching off an on.

Travis
Microserv

Brad Belton wrote: 


We have found many (most all?) 10kW job site type generators do not work
well if at all with APC UPS.  In the event of a power failure we simply rent
a 25kW towable diesel generator.  Granted 25kW is way overkill for most any
HUB site, but apparently the larger generators provide cleaner power that
the APC UPS's are happy with.
 
Does anyone have one of these 7kW Guardian standby generators in use with

APC UPS's?  $1999.00 delivered with transfer switch is a pretty strong deal!
 
Best,
 
 
Brad
 
 
 
 
 
-Original Message-

From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Scott Reed
Sent: Saturday, June 30, 2007 11:30 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator
 
The Guardian comes as small as 7KW for about $2100 and goes up a long 
way from there.
I have seen Guardians at cell sites and waste water lift stations around 
here.
 
George Rogato wrote:
  
http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id
=538 
  

 
I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd 
share it with the list.
 


 
  
  

--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-01 Thread Mike Hammett

Which ones?  I'd only use Smart-UPS and AFAIK, they all have that feature.


-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com


- Original Message - 
From: Brad Belton [EMAIL PROTECTED]

To: 'WISPA General List' wireless@wispa.org
Sent: Sunday, July 01, 2007 11:25 AM
Subject: RE: [WISPA] Low cost generator


This is true on the larger more expensive APC UPSs, but the smaller 500 -
750VA models don't have this feature, do they?



Brad





-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Travis Johnson
Sent: Saturday, June 30, 2007 11:57 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator



Brad,

You can adjust the sensitivity of the APC UPS's to handle just about any
type of incoming power. We have run a tower off a cheap Home Depot 2000watt
by adjusting the APC so it would not keep switching off an on.

Travis
Microserv

Brad Belton wrote:

We have found many (most all?) 10kW job site type generators do not work
well if at all with APC UPS.  In the event of a power failure we simply rent
a 25kW towable diesel generator.  Granted 25kW is way overkill for most any
HUB site, but apparently the larger generators provide cleaner power that
the APC UPS's are happy with.

Does anyone have one of these 7kW Guardian standby generators in use with
APC UPS's?  $1999.00 delivered with transfer switch is a pretty strong deal!

Best,


Brad





-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Scott Reed
Sent: Saturday, June 30, 2007 11:30 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

The Guardian comes as small as 7KW for about $2100 and goes up a long
way from there.
I have seen Guardians at cell sites and waste water lift stations around
here.

George Rogato wrote:

http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id
=538



I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd
share it with the list.





--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-01 Thread Tom DeReggi

automatic transfer does not take place at
one quarter of a cycle in a 60 cycle per second AC
power supply, then the sensitive logic controllers of
any network equipment, PLCs, etc will detect the
automatic transfer as a possible zero voltage
condition.


So What? Does that matter, as it is a one time event when the initial 
transfer occurs?
So the 750VA UPS, temporarilly switches to the UPS battery standby power, 
keeping Radios up, until the Generator power stablizes as on, then UPS 
switches back to line power from the generator.  IF the generator delivers 
unclean unstable power so what, that is the purpose of the small APC UPS to 
keep clean power going to the radio devices. So what if the UPS regularly 
switches back and forth from battery to Line voltage, as long as the switch 
is quick within required tolerances, and that it is not to frequent to drain 
the UPS battery.


From my experience, when the UPS did not do its job, it was because the UPS 
had a bad battery that could not handle the load, or a low grade UPS that 
did not have a fast enough transfer time itself, not a flaw in the 
generator's or its autoswitch.


What I had understood that George had said was not the the UPS switched back 
and forth between line and battery, but he said the UPS itself kept 
switching OFF and ON, as if the UPS was then malfunctioning.


What I was wondering was what type of power output was the problematic 
generator putting out? Pure Sinewave or  Pulse Modulated.  Many low cost 
devices put out PulseModulated, which is easier to regulate, to put out 
regulated power.  However, the Squared edge nature of the wave can be 
interpreted by a UPS further downstream as Bad Power, and possibly even 
damage the downstream UPS.  Which is a reason one is never supposed to 
install a ppure sinewave UPS downstream of a Pulsemodulated UPS.


We had designed some battery backup systems usign Tripplite's Power 
Inverters (pulse modulated output), which worked great, but we could not use 
APC Online UPS (puresinewave) UPSes in the racks.  To add better surve 
protection we put the protection directly in the Panel box with AC surge 
protection.  To check status of power outage, we install a cheap Linksys 
router, plugged directly into the AC outlet prior to the backup power 
systems, and then when this device stops responding, we know that there is 
not power beign sent to it. (yes there is an issue where the Linksys could 
lock up, and then us not know if it is the Linksys locked up or no power). 
One thing we were considering was to plug it inline with the Generators AC 
output feed, so teh Linksys bydefault is always off, and then when generator 
power kicks in the Linksys powers up, and if we can get to it, we know we 
are runnign on backup power.


So the point I'm making is, many generators, just put out raw voltage 
without regulation, purposely, so a UPS can be used after it to protect 
against drops and surges, and so Rack based UPSes do not need to be removed. 
The acception to this is if it has high end voltage regulation that puts out 
Pure Sinewave power.


Its actually relevent that we are specifically talkign about the APC 750VA 
rackmount UPS. I'm assuming you are talking about the Pure sine wave Online 
version.
That model is a sweat spot model because it is inexpensive, has SNMP model 
support, and it allows external batteries, and uses the slighly larger 
battery type, which enables longer run-time. Its worth finding a generator 
compatible with it. I was surprised to hear you were having the problem you 
represent.


Thats my take on it.  But will be interesting what you guys find out on what 
ends up working best.


Tom DeReggi
RapidDSL  Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: Felix A. Lopez [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Saturday, June 30, 2007 3:33 PM
Subject: Re: [WISPA] Low cost generator



George/Mike:  I worked for 6 years in deep UPS and
power quality at PGE in Silicon Valley including
IEEE1159 and CBEMA curve.  Our field work demonstrated
that if an automatic transfer does not take place at
one quarter of a cycle in a 60 cycle per second AC
power supply, then the sensitive logic controllers of
any network equipment, PLCs, etc will detect the
automatic transfer as a possible zero voltage
condition.  The weblink provided below did not specify
the automatic transfer switch cycle time (see pages 18
to pages 23).  A true UPS with continuous power will
actually provide your utility power source through a
battery system  including power conditioning along
with generator backup.  I had the opportunity to work
with the FAA in Fremont, California which has true
UPS it was quite a setup.

So you may want to ask at what level you of continuity
you need for your wireless network.

I know of a few subject matter experts in the industry
should you need a consultant.

Felix
Energy and Wireless practioneer
Silicon Valley Area

Re: [WISPA] Low cost generator

2007-07-01 Thread Mike Hammett
Unclean power will cause it to switch back and forth to\from the battery. 
As said, this is an adjustable setting on the UPS.


What Felix is talking about is the switch from line to battery is detected 
as zero voltage by the powered equipment.  There is no doubt that this 
exists and is an issue that more sensitive electronics have problems with. 
With constant switching, the powered equipment may fail.  If your supply is 
not clean, the UPS will not fix it.  I am unsure if clean power is produced 
when on battery.  A line conditioner's job is to clean up the power.



-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com


- Original Message - 
From: Tom DeReggi [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Sunday, July 01, 2007 12:39 PM
Subject: Re: [WISPA] Low cost generator



automatic transfer does not take place at
one quarter of a cycle in a 60 cycle per second AC
power supply, then the sensitive logic controllers of
any network equipment, PLCs, etc will detect the
automatic transfer as a possible zero voltage
condition.


So What? Does that matter, as it is a one time event when the initial 
transfer occurs?
So the 750VA UPS, temporarilly switches to the UPS battery standby power, 
keeping Radios up, until the Generator power stablizes as on, then UPS 
switches back to line power from the generator.  IF the generator delivers 
unclean unstable power so what, that is the purpose of the small APC UPS 
to keep clean power going to the radio devices. So what if the UPS 
regularly switches back and forth from battery to Line voltage, as long as 
the switch is quick within required tolerances, and that it is not to 
frequent to drain the UPS battery.


From my experience, when the UPS did not do its job, it was because the 
UPS
had a bad battery that could not handle the load, or a low grade UPS that 
did not have a fast enough transfer time itself, not a flaw in the 
generator's or its autoswitch.


What I had understood that George had said was not the the UPS switched 
back and forth between line and battery, but he said the UPS itself kept 
switching OFF and ON, as if the UPS was then malfunctioning.


What I was wondering was what type of power output was the problematic 
generator putting out? Pure Sinewave or  Pulse Modulated.  Many low cost 
devices put out PulseModulated, which is easier to regulate, to put out 
regulated power.  However, the Squared edge nature of the wave can be 
interpreted by a UPS further downstream as Bad Power, and possibly even 
damage the downstream UPS.  Which is a reason one is never supposed to 
install a ppure sinewave UPS downstream of a Pulsemodulated UPS.


We had designed some battery backup systems usign Tripplite's Power 
Inverters (pulse modulated output), which worked great, but we could not 
use APC Online UPS (puresinewave) UPSes in the racks.  To add better surve 
protection we put the protection directly in the Panel box with AC surge 
protection.  To check status of power outage, we install a cheap Linksys 
router, plugged directly into the AC outlet prior to the backup power 
systems, and then when this device stops responding, we know that there is 
not power beign sent to it. (yes there is an issue where the Linksys could 
lock up, and then us not know if it is the Linksys locked up or no power). 
One thing we were considering was to plug it inline with the Generators AC 
output feed, so teh Linksys bydefault is always off, and then when 
generator power kicks in the Linksys powers up, and if we can get to it, 
we know we are runnign on backup power.


So the point I'm making is, many generators, just put out raw voltage 
without regulation, purposely, so a UPS can be used after it to protect 
against drops and surges, and so Rack based UPSes do not need to be 
removed. The acception to this is if it has high end voltage regulation 
that puts out Pure Sinewave power.


Its actually relevent that we are specifically talkign about the APC 750VA 
rackmount UPS. I'm assuming you are talking about the Pure sine wave 
Online version.
That model is a sweat spot model because it is inexpensive, has SNMP model 
support, and it allows external batteries, and uses the slighly larger 
battery type, which enables longer run-time. Its worth finding a generator 
compatible with it. I was surprised to hear you were having the problem 
you represent.


Thats my take on it.  But will be interesting what you guys find out on 
what ends up working best.


Tom DeReggi
RapidDSL  Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: Felix A. Lopez [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Saturday, June 30, 2007 3:33 PM
Subject: Re: [WISPA] Low cost generator



George/Mike:  I worked for 6 years in deep UPS and
power quality at PGE in Silicon Valley including
IEEE1159 and CBEMA curve.  Our field work demonstrated
that if an automatic transfer does not take place

Re: [WISPA] Low cost generator

2007-07-01 Thread Tom DeReggi

Mike,

Thanks for the clarification...And the information provided is All good and 
helpful.  But this is where I'm confused



With constant switching


What makes characteristics of Constent switching.
It should only switch ONCE or TWICE unnecessarilly (which is not 
Constent), when the backup generator first kicks in.

Not sure why thats considered a big problem.
Unless one is thinking ahead, that the UPS Batteries may not be good enough, 
at the time a Power failure occurs and Generator activity is required.


Unless suggesting that running on the generator, will cause constant voltage 
drops, causing repeat UPS false detects.



If your supply is not clean, the UPS will not fix it.


Most UPSs made by APC above 500VA, both low cost Pulse Modulation models and 
Smart Online (pure Sinewave) models have Voltage Regulation built-in, and 
minor surge protection (350 joules or so) for the purpose to clean up the 
power.  With the exception of the really cheapo Desktop models shaped like 
thick surge protector trips.


I recognize that the switch setting on the APC UPS, is what allows one to 
set the Voltage Variation Range to be less sensitive to the Voltage drops 
and such, possibly solving the problem using them with generators.


Tom DeReggi
RapidDSL  Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: Mike Hammett [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Sunday, July 01, 2007 2:14 PM
Subject: Re: [WISPA] Low cost generator


Unclean power will cause it to switch back and forth to\from the battery. 
As said, this is an adjustable setting on the UPS.


What Felix is talking about is the switch from line to battery is detected 
as zero voltage by the powered equipment.  There is no doubt that this 
exists and is an issue that more sensitive electronics have problems with. 
With constant switching, the powered equipment may fail.  If your supply 
is not clean, the UPS will not fix it.  I am unsure if clean power is 
produced when on battery.  A line conditioner's job is to clean up the 
power.



-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com


- Original Message - 
From: Tom DeReggi [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Sunday, July 01, 2007 12:39 PM
Subject: Re: [WISPA] Low cost generator



automatic transfer does not take place at
one quarter of a cycle in a 60 cycle per second AC
power supply, then the sensitive logic controllers of
any network equipment, PLCs, etc will detect the
automatic transfer as a possible zero voltage
condition.


So What? Does that matter, as it is a one time event when the initial 
transfer occurs?
So the 750VA UPS, temporarilly switches to the UPS battery standby power, 
keeping Radios up, until the Generator power stablizes as on, then UPS 
switches back to line power from the generator.  IF the generator 
delivers unclean unstable power so what, that is the purpose of the small 
APC UPS to keep clean power going to the radio devices. So what if the 
UPS regularly switches back and forth from battery to Line voltage, as 
long as the switch is quick within required tolerances, and that it is 
not to frequent to drain the UPS battery.


From my experience, when the UPS did not do its job, it was because the 
UPS
had a bad battery that could not handle the load, or a low grade UPS that 
did not have a fast enough transfer time itself, not a flaw in the 
generator's or its autoswitch.


What I had understood that George had said was not the the UPS switched 
back and forth between line and battery, but he said the UPS itself kept 
switching OFF and ON, as if the UPS was then malfunctioning.


What I was wondering was what type of power output was the problematic 
generator putting out? Pure Sinewave or  Pulse Modulated.  Many low cost 
devices put out PulseModulated, which is easier to regulate, to put out 
regulated power.  However, the Squared edge nature of the wave can be 
interpreted by a UPS further downstream as Bad Power, and possibly even 
damage the downstream UPS.  Which is a reason one is never supposed to 
install a ppure sinewave UPS downstream of a Pulsemodulated UPS.


We had designed some battery backup systems usign Tripplite's Power 
Inverters (pulse modulated output), which worked great, but we could not 
use APC Online UPS (puresinewave) UPSes in the racks.  To add better 
surve protection we put the protection directly in the Panel box with AC 
surge protection.  To check status of power outage, we install a cheap 
Linksys router, plugged directly into the AC outlet prior to the backup 
power systems, and then when this device stops responding, we know that 
there is not power beign sent to it. (yes there is an issue where the 
Linksys could lock up, and then us not know if it is the Linksys locked 
up or no power). One thing we were considering was to plug it inline with 
the Generators AC output feed, so teh Linksys bydefault

Re: [WISPA] Low cost generator

2007-07-01 Thread Tom DeReggi

George,

We investigated these units about 4 years ago, and they were our first pick 
for converting to Propaine backup.
However, at the time we decided against it for cost reasons. We did not need 
16Kwatt and we were not aware of a 7Kwatt model at that time.
The $3500 for the 16K base unit is not the only cost. The autotranser switch 
added about $500, and then the Propain Tank is also an additional cost, but 
more importantly, the second we used Propaine in a cmmercial building, we 
needed a licensed Propain installer to do the work, to meet landlords 
requirements, which added another grand or two.


We instead installed Triplite 3500 watt power inverters $500 + 8 high end 
batteries (CD150AH batteries @ $350 each, but have a 10year + lifespan).


The arguement was that generators can be finicky, sometimes not starting on 
demand, if not routinely tested and started, and with the battery inverter 
solution we also were bypassing a high UPS cost, which is high for 3500watt 
rated units. So we solved our problem for 3 grand, instead of 6 grand after 
all considered, said, and done.


Now with that said. Seeing a 7Kwatt unit for only $2000, that changes 
everything! It would definately be more cost effective doing the generator 
instead of batteries.


Tom DeReggi
RapidDSL  Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: George Rogato [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Saturday, June 30, 2007 12:27 PM
Subject: [WISPA] Low cost generator



http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id=538

I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd share 
it with the list.


--
George Rogato

Welcome to WISPA

www.wispa.org

http://signup.wispa.org/
--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


--
No virus found in this incoming message.
Checked by AVG Free Edition. Version: 7.5.472 / Virus Database: 
269.9.6/865 - Release Date: 6/24/2007 8:33 AM





--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-01 Thread JohnnyO

Ok George - don't call me :)

JohnnyO
337-764-5953


- Original Message - 
From: George Rogato [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Sunday, July 01, 2007 8:50 PM
Subject: Re: [WISPA] Low cost generator


If it was just for radios, I'd be just using ups with extra batteries, but 
it's actually for a small data room with a half a dozen or more servers 
and some pc routers etc as well as couple of radios.


Right now we are just using ups for each server, but they don't last long, 
they just help if the power blinks or is out for a short time.


But if the power is out for a few hours, I'd like to keep operating.


Tom DeReggi wrote:

George,

We investigated these units about 4 years ago, and they were our first 
pick for converting to Propaine backup.
However, at the time we decided against it for cost reasons. We did not 
need 16Kwatt and we were not aware of a 7Kwatt model at that time.
The $3500 for the 16K base unit is not the only cost. The autotranser 
switch added about $500, and then the Propain Tank is also an additional 
cost, but more importantly, the second we used Propaine in a cmmercial 
building, we needed a licensed Propain installer to do the work, to meet 
landlords requirements, which added another grand or two.


We instead installed Triplite 3500 watt power inverters $500 + 8 high end 
batteries (CD150AH batteries @ $350 each, but have a 10year + lifespan).


The arguement was that generators can be finicky, sometimes not starting 
on demand, if not routinely tested and started, and with the battery 
inverter solution we also were bypassing a high UPS cost, which is high 
for 3500watt rated units. So we solved our problem for 3 grand, instead 
of 6 grand after all considered, said, and done.


Now with that said. Seeing a 7Kwatt unit for only $2000, that changes 
everything! It would definately be more cost effective doing the 
generator instead of batteries.


Tom DeReggi
RapidDSL  Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - From: George Rogato [EMAIL PROTECTED]
To: WISPA General List wireless@wispa.org
Sent: Saturday, June 30, 2007 12:27 PM
Subject: [WISPA] Low cost generator



http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id=538

I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd 
share it with the list.


--
George Rogato

Welcome to WISPA

www.wispa.org

http://signup.wispa.org/
--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


--
No virus found in this incoming message.
Checked by AVG Free Edition. Version: 7.5.472 / Virus Database: 
269.9.6/865 - Release Date: 6/24/2007 8:33 AM







--
George Rogato

Welcome to WISPA

www.wispa.org

http://signup.wispa.org/
--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/




--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-01 Thread dave
 I'm in the market for a generator and came across this one.

[ snipped link ]

That's either the very same generator I have, or very close to it.

(Actually, it's just very close. Ours can run on either propane or
natural gas, and it's presently wired up for the latter.)

Sadly, in the five months since we moved to our new office, with that
fancy new generator, we haven't had a single power outage. Not so much as
a flicker. It pops on once a week for its exercise cycle, and I've done
the flip the big switch and make sure the generator fires up test a
couple times, so I assume it works.)

As with any big purchase, shop around. Ours was $500 cheaper than the
price on that Web site; we just had Lowe's special-order it for us.

David Smith
MVN.net

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


RE: [WISPA] Low cost generator

2007-07-01 Thread Brad Belton
So, you bought this LP  Natural Gas generator for $1460 delivered,
including tax and transfer switch?

http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id
=370

That is an amazing deal!  Maybe Lowe's made a mistake on the price?


Brad



-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of [EMAIL PROTECTED]
Sent: Sunday, July 01, 2007 10:56 PM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

 I'm in the market for a generator and came across this one.

[ snipped link ]

That's either the very same generator I have, or very close to it.

(Actually, it's just very close. Ours can run on either propane or
natural gas, and it's presently wired up for the latter.)

Sadly, in the five months since we moved to our new office, with that
fancy new generator, we haven't had a single power outage. Not so much as
a flicker. It pops on once a week for its exercise cycle, and I've done
the flip the big switch and make sure the generator fires up test a
couple times, so I assume it works.)

As with any big purchase, shop around. Ours was $500 cheaper than the
price on that Web site; we just had Lowe's special-order it for us.

David Smith
MVN.net

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-07-01 Thread Blake Bowers

Shame, you have some nice gensets


- Original Message - 
From: JohnnyO [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Sunday, July 01, 2007 9:39 PM
Subject: Re: [WISPA] Low cost generator



Ok George - don't call me :)

JohnnyO
337-764-5953


- Original Message - 
From: George Rogato [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Sunday, July 01, 2007 8:50 PM
Subject: Re: [WISPA] Low cost generator


If it was just for radios, I'd be just using ups with extra batteries, 
but it's actually for a small data room with a half a dozen or more 
servers and some pc routers etc as well as couple of radios.


Right now we are just using ups for each server, but they don't last 
long, they just help if the power blinks or is out for a short time.


But if the power is out for a few hours, I'd like to keep operating.


Tom DeReggi wrote:

George,

We investigated these units about 4 years ago, and they were our first 
pick for converting to Propaine backup.
However, at the time we decided against it for cost reasons. We did not 
need 16Kwatt and we were not aware of a 7Kwatt model at that time.
The $3500 for the 16K base unit is not the only cost. The autotranser 
switch added about $500, and then the Propain Tank is also an additional 
cost, but more importantly, the second we used Propaine in a cmmercial 
building, we needed a licensed Propain installer to do the work, to meet 
landlords requirements, which added another grand or two.


We instead installed Triplite 3500 watt power inverters $500 + 8 high 
end batteries (CD150AH batteries @ $350 each, but have a 10year + 
lifespan).


The arguement was that generators can be finicky, sometimes not starting 
on demand, if not routinely tested and started, and with the battery 
inverter solution we also were bypassing a high UPS cost, which is high 
for 3500watt rated units. So we solved our problem for 3 grand, instead 
of 6 grand after all considered, said, and done.


Now with that said. Seeing a 7Kwatt unit for only $2000, that 
changes everything! It would definately be more cost effective doing the 
generator instead of batteries.


Tom DeReggi
RapidDSL  Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - From: George Rogato 
[EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Saturday, June 30, 2007 12:27 PM
Subject: [WISPA] Low cost generator



http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id=538

I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd 
share it with the list.


--
George Rogato

Welcome to WISPA

www.wispa.org

http://signup.wispa.org/
--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


--
No virus found in this incoming message.
Checked by AVG Free Edition. Version: 7.5.472 / Virus Database: 
269.9.6/865 - Release Date: 6/24/2007 8:33 AM







--
George Rogato

Welcome to WISPA

www.wispa.org

http://signup.wispa.org/
--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/




--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/ 


--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-06-30 Thread Scott Reed
The Guardian comes as small as 7KW for about $2100 and goes up a long 
way from there.
I have seen Guardians at cell sites and waste water lift stations around 
here.


George Rogato wrote:
http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id=538 



I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd 
share it with the list.




--
Scott Reed
Owner
NewWays
Wireless Networking
Network Design, Installation and Administration
www.nwwnet.net

--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-06-30 Thread JohnnyO

George - Call me - Soon Sir !

337-764-5953

JohnnyO
- Original Message - 
From: George Rogato [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Saturday, June 30, 2007 11:27 AM
Subject: [WISPA] Low cost generator



http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id=538

I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd share 
it with the list.


--
George Rogato

Welcome to WISPA

www.wispa.org

http://signup.wispa.org/
--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/




--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


RE: [WISPA] Low cost generator

2007-06-30 Thread Joe
I have one at my house and have two at one of the data centers. Works great.
Im close to putting a couple more on rooftops. 



-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-06-30 Thread Travis Johnson




Brad,

You can adjust the sensitivity of the APC UPS's to handle just about
any type of incoming power. We have run a tower off a cheap Home Depot
2000watt by adjusting the APC so it would not keep switching off an on.

Travis
Microserv

Brad Belton wrote:

  We have found many (most all?) 10kW "job site" type generators do not work
well if at all with APC UPS.  In the event of a power failure we simply rent
a 25kW towable diesel generator.  Granted 25kW is way overkill for most any
HUB site, but apparently the larger generators provide "cleaner" power that
the APC UPS's are happy with.

Does anyone have one of these 7kW Guardian standby generators in use with
APC UPS's?  $1999.00 delivered with transfer switch is a pretty strong deal!

Best,


Brad





-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED]] On
Behalf Of Scott Reed
Sent: Saturday, June 30, 2007 11:30 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

The Guardian comes as small as 7KW for about $2100 and goes up a long 
way from there.
I have seen Guardians at cell sites and waste water lift stations around 
here.

George Rogato wrote:
  
  http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id
=538 
  
  

I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd 
share it with the list.


  
  
  



-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

Re: [WISPA] Low cost generator

2007-06-30 Thread Mike Hammett

You can change this all via the APC management software.


-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com


- Original Message - 
From: Eric Muehleisen [EMAIL PROTECTED]

To: WISPA General List wireless@wispa.org
Sent: Saturday, June 30, 2007 12:23 PM
Subject: Re: [WISPA] Low cost generator



Travis,
How do you go about tweaking a UPS? We use APC 750's at most small tower 
sites. During the event of a power outage we use 1000watt generators but 
as you said...the UPS just shuts off and on, repeatedly.


-Eric

Travis Johnson wrote:

Brad,

You can adjust the sensitivity of the APC UPS's to handle just about any 
type of incoming power. We have run a tower off a cheap Home Depot 
2000watt by adjusting the APC so it would not keep switching off an on.


Travis
Microserv

Brad Belton wrote:
We have found many (most all?) 10kW job site type generators do not 
work
well if at all with APC UPS.  In the event of a power failure we simply 
rent
a 25kW towable diesel generator.  Granted 25kW is way overkill for most 
any
HUB site, but apparently the larger generators provide cleaner power 
that

the APC UPS's are happy with.

Does anyone have one of these 7kW Guardian standby generators in use 
with
APC UPS's?  $1999.00 delivered with transfer switch is a pretty strong 
deal!


Best,


Brad





-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Scott Reed
Sent: Saturday, June 30, 2007 11:30 AM
To: WISPA General List
Subject: Re: [WISPA] Low cost generator

The Guardian comes as small as 7KW for about $2100 and goes up a long 
way from there.
I have seen Guardians at cell sites and waste water lift stations around 
here.


George Rogato wrote:

http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id
=538

I'm in the market for a generator and came across this one.
The auto transfer switch and propane caught my eye and I figured I'd 
share it with the list.








--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/



--
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Low cost generator

2007-06-30 Thread Felix A. Lopez
It should work, But In our particular case the
question was what is the automatic transfer time
between the UPS inline with the backup generator?
what is the switch over time??? And at what voltage
threshold does it switch.  IEEE 1159 and the CBEMA
curve typically recommend to start looking at 65% to
60% of nominal voltage when switching to backup.  The
weblink your provided on page 18-23 discusses this
point (see the operators manual)   But they don't
specify the automatic transfers cycle time.  We
typically called APS, or Exide and also generator
manufacturer to ask for what is called relay
coordinaton settings. 

Felix

--- George Rogato [EMAIL PROTECTED] wrote:

 I was hoping to use my apc ups's inline with the
 back up generator.
 
 Any reason why this won't work?
 
 
 Felix A. Lopez wrote:
  George/Mike:  I worked for 6 years in deep UPS and
  power quality at PGE in Silicon Valley including
  IEEE1159 and CBEMA curve.  Our field work
 demonstrated
  that if an automatic transfer does not take place
 at
  one quarter of a cycle in a 60 cycle per second AC
  power supply, then the sensitive logic controllers
 of
  any network equipment, PLCs, etc will detect the
  automatic transfer as a possible zero voltage
  condition.  The weblink provided below did not
 specify
  the automatic transfer switch cycle time (see
 pages 18
  to pages 23).  A true UPS with continuous power
 will
  actually provide your utility power source through
 a
  battery system  including power conditioning along
  with generator backup.  I had the opportunity to
 work
  with the FAA in Fremont, California which has true
  UPS it was quite a setup.  
  
  So you may want to ask at what level you of
 continuity
  you need for your wireless network.  
  
  I know of a few subject matter experts in the
 industry
  should you need a consultant.
  
  Felix
  Energy and Wireless practioneer 
  Silicon Valley Area
  
  
  --- Mike Hammett [EMAIL PROTECTED] wrote:
  
  You can change this all via the APC management
  software.
 
 
  -
  Mike Hammett
  Intelligent Computing Solutions
  http://www.ics-il.com
 
 
  - Original Message - 
  From: Eric Muehleisen [EMAIL PROTECTED]
  To: WISPA General List wireless@wispa.org
  Sent: Saturday, June 30, 2007 12:23 PM
  Subject: Re: [WISPA] Low cost generator
 
 
  Travis,
  How do you go about tweaking a UPS? We use APC
  750's at most small tower 
  sites. During the event of a power outage we use
  1000watt generators but 
  as you said...the UPS just shuts off and on,
  repeatedly.
  -Eric
 
  Travis Johnson wrote:
  Brad,
 
  You can adjust the sensitivity of the APC UPS's
  to handle just about any 
  type of incoming power. We have run a tower off
 a
  cheap Home Depot 
  2000watt by adjusting the APC so it would not
  keep switching off an on.
  Travis
  Microserv
 
  Brad Belton wrote:
  We have found many (most all?) 10kW job
 site
  type generators do not 
  work
  well if at all with APC UPS.  In the event of
 a
  power failure we simply 
  rent
  a 25kW towable diesel generator.  Granted 25kW
  is way overkill for most 
  any
  HUB site, but apparently the larger generators
  provide cleaner power 
  that
  the APC UPS's are happy with.
 
  Does anyone have one of these 7kW Guardian
  standby generators in use 
  with
  APC UPS's?  $1999.00 delivered with transfer
  switch is a pretty strong 
  deal!
 
  Best,
 
 
  Brad
 
 
 
 
 
  -Original Message-
  From: [EMAIL PROTECTED]
  [mailto:[EMAIL PROTECTED] On
  Behalf Of Scott Reed
  Sent: Saturday, June 30, 2007 11:30 AM
  To: WISPA General List
  Subject: Re: [WISPA] Low cost generator
 
  The Guardian comes as small as 7KW for about
  $2100 and goes up a long 
  way from there.
  I have seen Guardians at cell sites and waste
  water lift stations around 
  here.
 
  George Rogato wrote:
 
 
 

http://www.electricgeneratorsdirect.com/catalog/product_info.php?products_id
  =538
  I'm in the market for a generator and came
  across this one.
  The auto transfer switch and propane caught
 my
  eye and I figured I'd 
  share it with the list.
 
 
 
  -- 
  WISPA Wireless List: wireless@wispa.org
 
  Subscribe/Unsubscribe:
  http://lists.wispa.org/mailman/listinfo/wireless
 
  Archives:
  http://lists.wispa.org/pipermail/wireless/
  -- 
  WISPA Wireless List: wireless@wispa.org
 
  Subscribe/Unsubscribe:
  http://lists.wispa.org/mailman/listinfo/wireless
 
  Archives:
 http://lists.wispa.org/pipermail/wireless/
 
  
  
  
 
 


  Take the Internet to Go: Yahoo!Go puts the
 Internet in your pocket: mail, news, photos  more. 
  http://mobile.yahoo.com/go?refer=1GNXIC
 
 -- 
 George Rogato
 
 Welcome to WISPA
 
 www.wispa.org
 
 http://signup.wispa.org/
 -- 
 WISPA Wireless List: wireless@wispa.org
 
 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless
 
 Archives: http://lists.wispa.org/pipermail/wireless