Hello Bernd,

On Tue, 2007-10-23 at 12:22 +0200, Bernd Walter wrote:
> On Mon, Oct 22, 2007 at 11:27:15PM +0200, Bill Maas wrote:
[...]
> > I can't see what a Soekris box has to do with the DCD line, however.
> 
> If you configured your terminal/serial correctly for 3-wire then it
> shouldn't care about DCD at all.

Here's the serial port setup:

[EMAIL PROTECTED]:~# stty -F /dev/ttyS0 -a
speed 9600 baud; rows 0; columns 0; line = 0;
intr = ^C; quit = ^\; erase = ^?; kill = ^U; eof = ^D; eol = <undef>;
eol2 = <undef>; swtch = <undef>; start = ^Q; stop = ^S;
susp = ^Z; rprnt = ^R; werase = ^W; lnext = ^V; flush = ^O; min = 1;
time = 0;
-parenb -parodd cs8 hupcl -cstopb cread clocal -crtscts
-ignbrk -brkint -ignpar -parmrk -inpck -istrip -inlcr -igncr icrnl ixon
-ixoff -iuclc -ixany -imaxbel -iutf8
opost -olcuc -ocrnl onlcr -onocr -onlret -ofill -ofdel nl0 cr0 tab0 bs0
vt0 ff0
isig icanon iexten echo echoe echok -echonl -noflsh -xcase -tostop
-echoprt echoctl echoke


As the stty ouput shows, RTS/CTS flow control is turned off - but that's
on this side of the connection. Man page cu(1) hardly mentions
handshake, only for debugging. DCD isn't mentioned at all (but see
below..). Running 'cu' in debug mode hardly increases it's output:

------------------------------------------------------------------------
[EMAIL PROTECTED]:~# cu -d -l /dev/ttyS0 -s 19200
cu: fconn_open: Opening port /dev/ttyS0 (speed 19200)
cu: fconn_set: Changing setting to 0, 0, 2
Connected.
cu: Got hangup signal
cu: Exit status 0
cu: fconn_close: Closing connection

Disconnected.
[EMAIL PROTECTED]:~# cu -x handshake -l /dev/ttyS0 -s 19200
Connected.
cu: Got hangup signal

Disconnected.
------------------------------------------------------------------------

The soekris docs don't mention handshaking modes either.


> The other point is that you likely don't have the correct 0-modem
> cable to supply a DCD signal into your computer.
> It might be that DCD input is open and floating.
> 

Cable is wired as follows:

RxD 2 ------------------- 3 TxD
TxD 3 ------------------- 2 RxD

DTR 4 ------------------- 6 DSR
DSR 6 ------------------- 4 DTR

RTS 7 / 8 CTS ----------- 1 DCD
1 DCD ----------- 7 RTS / 8 CTS

Apparently the Soekris comBIOS drops the voltage on its RTS/CTS pair
once a character arrives, which 'cu' sees as a hangup signal.


I wouldn't know where to go from here, but here's something very
interesting I found about IBM's cu (command options):

-m   Instructs the cu command to ignore modem control signal data
carrier detect (DCD).

(http://publib.boulder.ibm.com/infocenter/pseries/v5r3/index.jsp?topic=/com.ibm.aix.cmds/doc/aixcmds1/cu.htm
 )

Seems to be exactly what I am looking for. Unfortunately this option is
missing in the Linux version. And I'm still not convinced that the
Soekris comBIOS should be touching those RTS/CTS lines..

Thanks for the reply anyway, at least it gave me something to look for.

Meanwhile, every piece of soft- or hardware I touch today seems to
immediately disintegrate:-(


Bill


-- 
"Ask not what it's for, ask what you can do with it."

_______________________________________________