Our AHJ uses 200 LF 13/4" hose with 200 Gpm @ 85 up to 115 Psi with a 10 Lf 21/2' hose with a splitter and valves. ( Interesting Calc since only 250 Gpm demand is from a single outlet, and the other 250 from the one below.)
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Chris Cahill" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, December 06, 2006 9:43 AM
Subject: RE: pump capacity/standpipe


If you review what the FD actually uses you will probably find it's much
higher than 100psi.  A popular set up is 100 psi nozzles with 1-3/4" hose
200' which is 132 psi at the outlet at 100 gpm.  Then there is no guessing
what they will be using 5 years from now.  Through the 80's and 90's
required average pressures went up as a general trend.  They seem to be
going down IMHO in the '00's. Trends are irrelevant though when speaking of
a particular job in a particular city.

NFPA 14 requirements for gpm and pressure are broke beyond repair and FD's
haven't a clue what they want or need, thus why NFPA 14 is broke. If I knew
how to fix it I would send in a proposal, but I don't.

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.

763-658-4483
763-658-4921 fax

Email: [EMAIL PROTECTED]

Mail: P.O. Box 69
       Waverly, MN 55390

Location: 4439 Hwy 12 SW
             Waverly, MN 55390

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Wednesday, December 06, 2006 10:14 AM
To: [email protected]
Subject: Re: pump capacity/standpipe

I don't want to beat this horse to death like a "Big Ass Fan", but it would
be prudent if you reviewed the changes to 14 for 2007, and reviewed the
equipment used by the AHJ, to meet the hose and Nozzle friction loss calc's.

(They may actually be lower than the 100 Psi at the outlet depending on the
nozzle.)

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Joe Hankins" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, December 06, 2006 8:49 AM
Subject: Re: pump capacity



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to