Back in the 99 edition of 13, the description in section 7-9.5 on what ESFR could protect included Ordinary Hazard. Granted it was developed and tested for storage buut I always ASSUMED this allowance was to address those small areas of other than storage within a facility.

Now when we rewrote / restructured the standard in the 02 edition, this reference disappeared (at least I can't put my finger on it). I don't remember us discussing deleting the reference but it did not fit in the improved format/presentation on ESFR criteria so would have been removed from this section. Since there is no section on ESFR within the occupancy hazard approach, there wasn't anywhere to move it to. It cold have just fluttered away.

Note the prior description did NOT say extra hazard.

Roland

On Dec 18, 2006, at 2:24 PM, John Powell wrote:

We have an issue with ESFR in a rack storage area interspersed with componant assembly. The assembly process does not involve flamable liquids or hydraulic equipment. There are no shielded hazards and the storage complies with the ESFR listing. Our AHJ requires that the limited assembly/process hazard be listed for QR sprinklers, which it is, and the number of ESFR sprinklers calculated for the usual OH area of operation discharging at the listed pressure for the storage and building height involved. Seems excessive to me. Have the forum members had any similar ruling?
John Powell - New Zealand
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to