You can't calculate and ESFR for a density less than about 0.80 because they will not develop an effective distribution patern at those low pressures. That's why Tyco reacted to your suggestion the way they did.

Joe

Fletcher, Ron wrote:

We have run into the problem of ESFR's in production areas many times
but mostly due to the obstruction rules. I haven't had an AHJ try to
apply area/density criteria to ESFR's.
Offer to calc a full RA at "X" density to prove the system exceeds that
prescribed for the hazard. There is no precedence for treating ESFR's as
area/density but if the AHJ wants a full size remote "area" then they
should be willing to allow a "density" calc in lieu of the ESFR
discharge criteria. (In for a penny in for a pound.)

The Tyco guys once asked me if I had any ideas for new products. I
suggested they cross list ESFR's for area/density. They looked at me
like I had two heads so I wouldn't look for any changes from the OEM.

Ron Fletcher
Aero Automatic
Phoenix, AZ





-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Powell
Sent: Monday, December 18, 2006 3:25 PM
To: [email protected]
Subject: ESFR in production areas

We have an issue with ESFR in a rack storage area interspersed with
componant assembly.  The assembly process does not involve flamable
liquids or hydraulic equipment.  There are no shielded hazards and the
storage complies with the ESFR listing.  Our AHJ requires that the
limited assembly/process hazard be listed for QR sprinklers, which it
is, and the number of ESFR sprinklers calculated for the usual OH area
of operation discharging at the listed pressure for the storage and
building height involved.  Seems excessive to me.  Have the forum
members had any similar ruling?
John Powell - New Zealand
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to