Hopefully there won't be a burning room after the sprinkler retro ...
Seriously, what exactly is a burning room and why can't you take piping
through it?   

Actually, the definition of a semi-automatic standpipe system can be
found in both the 2003 (3.3.21) and 2007 (3.3.12.5) editions of NFPA 14:
"A standpipe system that is attached to a water supply capable of
supplying the system demand at all times and that requires activation of
a control device to provide water at hose connections."

Essentially, it's a preaction standpipe system and the actuation of the
valve is manual in lieu of automatic detection as is used in sprinkler
systems.   The remote actuator can be a pull station or even a hose
valve (non-interlock design) or an electronic device such as a pull
station (single and double interlock designs).  To clarify the
definition and intent, the 2007 standard has been greatly enhanced by
excerpting some of the preaction prescriptives from NFPA 13 - if you
have the 2007, see section 5.2.3.

Steve Leyton
Protection Design & Consulting



-----Original Message-----
From: Coastal [mailto:[EMAIL PROTECTED] 
Sent: Tuesday, December 26, 2006 5:17 PM
To: [email protected]
Subject: Class III Standpipe

Hello sprinklerforum,

  I need to install a Class III standpipe in a location where it is
subject to freezing. I see a reference in NFPA 14 2003 section 5.4.3 to
a "Semiautomatic-Wet" but no definition for one. I am open to
suggestions. Looks like this little 4 story 32 room hotel is going to be
spending a bundle on the remodel work.

        I am unable to reuse the existing standpipe as it could require
passing a burning room the get to the existing location. The building is
not sprinklered now but they are being added throughout.

--
Best regards,
Charles Thurston 
Coastal Fire Protection
mailto:[EMAIL PROTECTED]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to