Thanks for the responses.  I went out today and measured the building
height....   25' 10" to the walking surface of the top floor. The AHJ
and code call out 30' so it became a moot point.  Now to write a NICE
response to the AHJ.



Wednesday, December 27, 2006, 12:31:54 PM, you wrote:

> Good point Ro - I was thinking about the definition and speaking to
> Charles' question.   If you're going to retrofit the building with
> sprinklers the standard allows you to substitute a 2.5" x 1.5" reducer
> at each Class I connection for the Class II hose stations.  The 130'
> coverage requirement is specifically excepted as well.

> Steve Leyton
> Protection Design & Consulting



> -----Original Message-----
> From: Roland Huggins [mailto:[EMAIL PROTECTED] 
> Sent: Wednesday, December 27, 2006 9:17 AM
> To: [email protected]
> Subject: Re: Class III Standpipe

> SInce sprinklers are being added, what's the schedule for completion?
> If it's all part of the same job, why not talk to the AHJ and owner
> about just going with a Class I standpipe and do a manual-dry one?

> Roland

> On Dec 26, 2006, at 5:16 PM, Coastal wrote:

>> Hello sprinklerforum,
>>
>>   I need to install a Class III standpipe in a location where it is 
>> subject to freezing. I see a reference in NFPA 14 2003 section
>> 5.4.3 to a "Semiautomatic-Wet" but no definition for one. I am open to

>> suggestions. Looks like this little 4 story 32 room hotel is going to 
>> be spending a bundle on the remodel work.
>>
>>       I am unable to reuse the existing standpipe as it could require 
>> passing a burning room the get to the existing location. The building 
>> is not sprinklered now but they are being added throughout.
>>
>> --
>> Best regards,
>> Charles Thurston
>> Coastal Fire Protection                           
>> mailto:[EMAIL PROTECTED]
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



-- 
Best regards,
 Charles                            mailto:[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to