This is one is a little more defined than some others:

It is NOT a tenant space; it is a stand alone building being built by a
reputable company that has been in business for many years.

The building has a separate 20,000 sqft storage warehouse in the same
building but is in a completely separate area from the showroom which will
be addressed accordingly.

This will strictly be an entry area of the business with a SHOWROOM meaning
the office products will be placed in situations like a real operating
office minus all of the computers and people.

The products in this room will be no higher than normal bookshelves in your
own office.

The following description is why I question it Occupancy type. If this were
the office portion of the building then it would clearly be Light Hazard.
Since the furniture is on DISPLAY and not being USED as an office then this
should be Ordinary Hazard? This I do not understand.

BTW, I had already laid it out and bid it for Ord Hazard Group II but wanted
more input.
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Thursday, January 11, 2007 5:36 PM
To: [email protected]
Subject: RE: Office furniture showroom

Mercantile tends to start at OH2 and then go UP in classification, rarely
down. Maybe if they were selling angle iron out of a 10' high building,
you'd have a chance for OH1. Bigbox retail, hey-class 4 25' high racks. 
But furniture and plastic- only in my area could you get an AHJ to sign off
on LH.

George Church
Rowe Sprinkler

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- work
Sent: Thursday, January 11, 2007 6:03 PM
To: [email protected]
Subject: Re: Office furniture showroom

My guess would be retail, due mostly to the concentration. Watch out 
for rack storage. I asked a similar regarding a jewelry store a few 
months back and got my you-know-what nailed to a tree.

At 05:59 PM 1/11/2007, you wrote:

>Is an Office Furniture Showroom "mercantile" or would it be considered more
>of an Office Space and be Light Hazard?
>
>Thanks,
>Greg McGahan
>
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to