Greg 

There has been no full scale fire testing of the PODs storage configuration,
and until there has been testing the design of sprinkler protection for this
storage needs to be very conservative, addressing some of the unique
features and problems presented by this storage configuration.

Regarding PODs storage you need to address the PODS storage by looking at
the fuel load and fuel load configuration. Let us look first at the type of
commodity being stored in the PODS unit. We have opened and inspected a
large number of the PODS units throughout our clients facilities and have
classified the storage to be typical Class IV commodity.  NFPA 13 Paragraph
2-2.3.4 defines a Class IV commodity as a product, with or without pallets,
that meets one of the following criteria:
(1)     Constructed partially or totally of Group B plastics.
(2)     Consists of free-flowing Group A plastic materials.
(3)     Contains within itself or its packaging an appreciable amount (5
percent to 15 percent by weight or 5 percent to 25 percent by volume) of
Group A plastics. The remaining materials shall be permitted to be metal,
wood, paper, natural or synthetic fibers, or Group B or Group C plastics.

The NFPA definition of a Class IV commodity describes almost all house hold
products that could be stored in a PODS unit.

The PODS unit is enclosed on five sides with ¾ inch plywood panels supported
by 4" x 4" wood framing, approximately 8' wide x 8'-5" high x 16' long with
a flexible plastic roof or solid wood roof.  A fire in a PODS unit will grow
within the unit, when the roof of the unit is breached by the fire a large
amount of heat and unburned products of combustion will be released into the
building, which can result in a large column of superheated air racing to
the ceiling of the building. This large heat release from a shielded fire
will overwhelm an ESFR sprinkler system by operating an excessive number of
sprinkler heads. Each three high set of stored units with have a minimum 3
ft access aisle on all four sides of each stack of three high PODS units.

To over come the heat release from a shielded fire 286ºF temperature rated
standard type of sprinkler will need to be used in the sprinkler system.
Historically, this sprinkler head was used to address high heat release
rated fires.

A similar occupancy that has a shielded fire growth potential is the
manufacturer of mobile /modular homes which is classified as an Extra Hazard
Group II occupancy classification which is required to be protected by a
sprinkler system designed to provide a design density of 0.40 gpm per sq.
ft. over the hydraulically most remote 2,000 sq. ft. using 286ºF temperature
rated sprinklers at the ceiling.

Because of the storage of the PODS units three high, there is a real
possibility that a fire in a lower unit will cause the collapse of the pile
onto a second pile of storage units and at the same time shield the fire
from the water discharge from the overhead sprinkler system. In order to
address the shielded fire issue from a collapse of a pile of three storage
units a second sprinkler system density design criteria needs to be
provided. Usually when there is a concern about a shielded fire the area of
operation for the sprinkler system is increased to either 4,000 sq. ft. or
even as high as 5,000 sq. ft. with a minimum design density of 0.30 gpm over
the hydraulic most remote area. 

For the design of our clients PODS storage warehouse we recommended to the
client to have the sprinkler system designed to produce both of the
following sprinkler system discharge densities over the referenced areas of
operation: 

1.      A 0.60 gpm per sq. ft. over the hydraulically most remote 3,000 sq.
ft. 
2.      A 0.40 gpm per sq. ft. over the hydraulically most remote 5,000 sq.
ft

Yes the site has a good water supply.

Greg hope this helps 

Jim Davidson 
 
Davidson Associates 
302-378-7600
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Thursday, January 18, 2007 8:01 AM
To: [email protected]
Subject: RE: POD Storage

The formal restrictions are what you would expect:

No flammable liquids, hazardous materials, explosives and blah blah blah.

I know there is the possibility of dangerous stuff but I do believe the
majority of the stuff in the containers is going to be normal household
items that are either in transit or in temporary storage while a home is
being built, etc.

My primary concern is the plastic roofs and the foam inside (mattresses,
sofas, etc.) and the fact that if the fire starts on the bottom level that
the water will not be able to penetrate the upper PODs. Maybe if we provide
enough water we could at least shield the adjacent pods and contain the
fire? 

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew J.
Willis
Sent: Thursday, January 18, 2007 6:48 AM
To: [email protected]
Subject: RE: POD Storage

If I recall the last time we discussed this, it was the "other" stuff that
can be placed in the PODS that make a big IF appear on the horizon. I know
you can't design to "if" but... Has anyone set fire on these yet since our
last discussion?

Matt 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- work
Sent: Thursday, January 18, 2007 7:38 AM
To: [email protected]
Subject: RE: POD Storage

Greg, From what I can tell, this would essentially be container storage. It
could be worthwhile to find out who they are marketing to to figure out what
might show up. If they are marketing to primarily individuals, the chances
of their being a POD of rubber tires would be slim. Does the company have
any restrictions on contents? You also might want to pursue the 'container
storage' thread on a commercial level and see what is out there. There may
be some government info on that subject. This is something could be coming
to everyone's jurisdiction at some point. I'd be interested to know what you
find out.


At 07:21 AM 1/18/2007, you wrote:
>Is there no help from the forum on this one?!
>
>The guy has to protect the building and the one thing I am absolutely 
>sure about is that we will not be putting sprinklers inside the PODs
themselves.
>
>Other than that it is in the air - water - foam?
>
>Has there been any recorded fires in these facilities that someone has 
>knowledge or experience with?
>
>ANY input is appreciated.
>Greg
>Living Water Fire Protection, LLC
>1160 McKenzie Road
>Cantonment, FL 32533
>850-937-1850
>Fax: 850-937-1852
>
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Matthew J.
>Willis
>Sent: Wednesday, January 17, 2007 3:39 PM
>To: [email protected]
>Subject: RE: POD Storage
>
>Take a break from it, ,buy us all a beer, and we will see what we come 
>up with.
>
>Matt
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Greg 
>McGahan
>Sent: Wednesday, January 17, 2007 3:00 PM
>To: [email protected]
>Subject: POD Storage
>
>I know this has been addressed but I did not see any conclusions in 
>forum archives.
>
>PODs stored 3 high: approximately 27' with a 30' eave height in the 
>building. I truly do not know where to start with this one.
>
>Any help would be appreciated.
>
>Thanks,
>Greg
>
>Living Water Fire Protection, LLC
>1160 McKenzie Road
>Cantonment, FL 32533
>850-937-1850
>Fax: 850-937-1852
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to