Interesting that NFPA-20 includes provisions for the fire resistance rating of the fire pump room itself, something one would assume would be in the building code.
The NEC includes a myriad of requirements for worker safety, including but not limited to lighting, working space, clearances, means of egress and even panic hardware. Sounds like a proposal ! John Drucker Fire Protection Subcode Official -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Tuesday, January 30, 2007 11:28 AM To: [email protected] Subject: RE: FIRE PUMP ROOM ACCESSIBILITY And electrical clearances to the controller doors. Too bad #20 doesn't specify minimums but they are getting better every edition. (I did 5 pumps since Sunday and only 1 pump room had enough space to put down your tools.) Tom -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of John Drucker Sent: Tuesday, January 30, 2007 9:29 AM To: [email protected] Subject: RE: FIRE PUMP ROOM ACCESSIBILITY Every space or room is required to have a means of egress. Minimum egress widths are prescribed by the building code. For a single means of egress typically 36" exit access and 32" net clear doorway width. There is also a provision prohibiting projections greater then 4" into the required egress width. Reference: IBC/IFC, Chapter 10. John Drucker Fire Protection Subcode Official Firefighter Borough of Red Bank, NJ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Tuesday, January 30, 2007 9:14 AM To: [email protected] Subject: FIRE PUMP ROOM ACCESSIBILITY We have a small pump room that the owner REFUSED to enlarge during the design phase of this project. Due to the structural engineer we were forced to move our stub in 1' closer to the wall and now the pump and panel infringe on the doorway coming into the room. As it currently stands you have to turn sideways in order to enter the room. Once you are in the room there is room. NFPA 20 states the following in the appendix: A.5.12.1.1 Most fire departments have procedures requiring operation of a fire pump unit during an incident. Building designers should locate the fire pump room to be easily accessible during an incident. Firefighters please give me your opinions! Greg McGahan _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum