If providing 1½" reducers it is assumed that 1½" hoses be provided. Most FD do not use 1½" hoses to fight fires, they are for clean-up and untrained persons. If there aren't any hoses then why provide the 1½" reducers?
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Tuesday, January 30, 2007 2:02 PM To: [email protected] Subject: RE: NFPA #14 and pressures One thing that does not make sense....where are these untrained people going to get 1 1/2" hose? Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Timothy W Goins Sent: Tuesday, January 30, 2007 3:00 PM To: [email protected] Subject: RE: NFPA #14 and pressures Must meet both criteria. The 1½" hose station is available for untrained persons thus the pressure limit. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dave Thompson Sent: Tuesday, January 30, 2007 12:11 PM To: [email protected] Subject: NFPA #14 and pressures NFPA #14 states that when the static pressure at a hose connection exceeds 175 psi, a pressure regulating device shall be provided to limit the pressure to 100 psi for 1 ½" hose connections and to 175 psi for all other hose connections. What if the standpipe is a Class III utilizing the fully sprinklered building exception allowing 2 ½" hose valves with 1 ½" reducers, caps and chains? Does the pressure need to be limited to 100 psi or 175 psi? Dave David K. Thompson Vice President Allstate Fire Sprinkler, Inc. P.O. Box 2350 Hartford, CT 06146 Phone = 860-246-7711 Fax = 860-246-7707 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum **************************************************************************** ****************** IMPORTANT: The contents of this email and any attachments are confidential. They are intended for the named recipient(s) only. If you have received this email in error, please notify the system manager or the sender immediately and do not disclose the contents to anyone or make copies thereof. **************************************************************************** ****************** _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum