Tom:

Our AHJ's allow us to ignore door shadow. If they didn't we'd have to start installing heads under the doors, like 13. I really like Rolland's, "A living room with a car in it" It immediately reminded me of all the Choppers I've seen stripped down in certain living rooms, awaiting parts or ambition.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Tom Duross" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, February 06, 2007 3:59 PM
Subject: Re: Residential 13D Garage


I got a comment back from a reviewer wondering why I did a 2 head calc in a garage with dry pendents. I pointed him to that section and he was satisfied. The garage had 6 heads btw, due to the door shadow.

Tom Duross


It's a living room with a car in it. The Annex saying use the same piping as the dwelling unit and allowing residential sprinklers with a two sprinkler discharge indicates that but does not state it. we do get additional guidance from 13R which allows garages serving a single dwelling unit states "shall be considered as part of that dwelling unit and uses residential sprinklers in accordance with 8.6.1 - Design Criteria Inside Dwelling Unit". SInce 13R is a higher level of protection, it would be hard to argue that 13D needs more.

Roland

On Feb 6, 2007, at 12:58 PM, Cliff Whitfield wrote:

I have a question for the 13D residential gurus out there. I am looking over a drawing that a colleague did for a 13D system. The garage area is
being sprinklered and 8.6.4 of the 2002 edition addresses this to some
degree.  My question is that in the appendix (excuse me, the annex) it
states that a 2 sprinkler design with piping the same sizes as the rest of
the dwelling may be used.



My question is what about the head spacing? It doesn't specifically address that and I am not sure if that means that I can space the heads out per 13D or if they would need to be limited to 130 sf per ordinary hazard. The AHJ in the area is not as educated as some in larger metropolitan areas and he is okay with the 13D spacing for the garage. I'm just trying to make sure
that it's per code.



Thanks,



Cliff Whitfield



Fire Design, Inc.

3784 Holly Ridge Trail

Marianna, FL 32448



Phone:  850-526-1886

Fax:    850-526-1884

Cell:    850-819-5861



www.fire-design.com





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to