IBC Section 3311 (Safeguards during Construction) provides the
requirement. 3311.3 directs us back to IBC Chapter 9.  IBC 905.3.2
provides the 200 ft "reach" requirement in buildings exceeding 10,000
s.f. in area per story.

John Drucker
Fire Protection Subcode Official
New Jersey



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Thursday, February 08, 2007 4:37 PM
To: [email protected]
Subject: Temporary Standpipe

Forum (Steve or Rich),
 
Must all portions of a floor be within 200 ft. reach of a temporary
standpipe valve?
 
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ
 
 