Yea, 8.16.2.4.3 is what my brain said, but fingers weren't paying
attention.

Exactly how I'm reading it.  Any more opinions before I seek the informal
interpretation?

Ed Kramer
Littleton, CO


>You mean 8.16.2.4.3?
>
>That's for multiple system control valves on a common manifold that
>would share a common run-in.  It's just saying where the FD piping
>connection should attach to the risers between the supply (OS&Y) control
>valve and the System (Alarm Check) valves.
>
>If you're running new UG to this new addition, it's a totally separate
>system from the other part of the building and doesn't need to have
>anything to do with the existing. Let it stand on it's own.
>
>As far as 8.16.2.4.5, what they are alluding to there is if for example
>a system only serves from columns a-f on the south side of the bldg then
>there should be a sign stating such.  That way the FD knows which riser
>is serving what portion of the building.
>
>
>
>
>Craig L. Prahl, CET
>Fire Protection Group
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[EMAIL PROTECTED]
>http://www.lg.com
>
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
>Sent: Thursday, March 01, 2007 4:28 PM
>To: [email protected]
>Subject: FDC's on multiple systems
>
>Run into something new that I need opinions on.
>
>An addition is being added to an existing building.  Existing building
>is fully sprinklered.  The total area of the combined existing and new
>structure exceeds 52,000 sf and the existing system riser is in the far
>corner away from the addition.  So the decision was made to bring in a
>new underground supply to serve the new addition.  Thus the new addition
>will have its own independent system riser and fire department
>connection.
>
>Does 2002 NFPA 13 section 8.16.l2.4.3 (or any other section) require the
>two FDCs (one existing, one new) be tied together?
>
>The commentary hints at this, but I've never thought that was the
>intent.
>I thought the intent was that multiple systems SERVED BY THE SAME
>UNDERGROUND LEAD-IN be served by the same FDC.  Section 8.16.2.4.5 seams
>to
>support this.
>
>Opinions?
>
>Ed Kramer
>Littleton, CO
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to