Todd,

Salsa would behave the same as water. The liquid acts as a heat sink, not as an extinquishing agent. A lot of bottles would have to fail in a very short time to have any impact.

Water in plastic bottle's can't escape until the container melts. It can't melt untill the contents are well above the boiling point. That's why the test of soda in plastic bottles was such a non-event.

There was also a commodity classification test involving applesauce in plastic single-service containers the produced no fire other than the cartons the containers were in.

The idea that liquids in containers will extinguish a fire is a popular myth, perhaps encouraged by the fact that combustible liquids in containers contribute significantly to a fire when the containers fail. The difference is that one gallon of flammable liquids can contribute the equivaalent of 20 pounts of wood or paper to a fire, and it burns on the floor, where it has the largest impact on the fire. Non-combustible liquids do no more to extingush a fire than water, and they go straight to the floor when the containers fail, doing very little to reduce the fire.

Joe


Todd Williams - work wrote:

David,

Mild, Hot or Nuclear aside, it don't think that salsa would meet the same standard as juice or soda. I believe (and I think Joe could help me out here), part of that comes from the fact the when a bottle of soda (or whatever liquid) breaks, you would get a flood of liquid that could inhibit the spread of the fire. Most salsa worth anything would flow that much, so you wouldn't get the same effect.

Todd


At 02:37 PM 3/6/2007, you wrote:

Dear Forum,

According to NFPA 1 (2003) 13.3.2.23.1 a sprinkler system is required for high-piled storage of combustibles over 2500 sq. ft., and A13.3.2.23 states
that for this purpose combustibles include non-combustibles packaged in
combustible materials.

According to NFPA 13 (2002) Table A.5.6.3 glass jars filled with
non-combustible liquids is a Class I commodity. 5.6.3.1, states that Class I
shall be defined as non-combustible.



Question I have is: What would salsa in glass jars packaged in cardboard
boxes (cases) stored over 12 ft. in racks be classified as?



It appears to me that NFPA 1 says to sprinkle the building, and then NFPA 13 says its noncombustible storage for the purpose of determining rack storage
protection. Is this a fair statement?





David Autry

Plans Examiner

Nebraska State Fire Marshal's Office

246 S. 14th Street

Lincoln, NE 68508

402-471-9659

402-471-3118 fax

www.sfm.ne.gov





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to