Remember your Boyscout/Girlscout days when you could boil water over an open
flame in a paper bag. Same idea. Plastic bottle will be cooled from the
liquid it contains.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Joe Hankins" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, March 06, 2007 1:57 PM
Subject: Re: Combustible Salsa
Todd,
Salsa would behave the same as water. The liquid acts as a heat sink, not
as an extinquishing agent. A lot of bottles would have to fail in a very
short time to have any impact.
Water in plastic bottle's can't escape until the container melts. It can't
melt untill the contents are well above the boiling point. That's why the
test of soda in plastic bottles was such a non-event.
There was also a commodity classification test involving applesauce in
plastic single-service containers the produced no fire other than the
cartons the containers were in.
The idea that liquids in containers will extinguish a fire is a popular
myth, perhaps encouraged by the fact that combustible liquids in
containers contribute significantly to a fire when the containers fail.
The difference is that one gallon of flammable liquids can contribute the
equivaalent of 20 pounts of wood or paper to a fire, and it burns on the
floor, where it has the largest impact on the fire. Non-combustible
liquids do no more to extingush a fire than water, and they go straight to
the floor when the containers fail, doing very little to reduce the fire.
Joe
Todd Williams - work wrote:
David,
Mild, Hot or Nuclear aside, it don't think that salsa would meet the same
standard as juice or soda. I believe (and I think Joe could help me out
here), part of that comes from the fact the when a bottle of soda (or
whatever liquid) breaks, you would get a flood of liquid that could
inhibit the spread of the fire. Most salsa worth anything would flow that
much, so you wouldn't get the same effect.
Todd
At 02:37 PM 3/6/2007, you wrote:
Dear Forum,
According to NFPA 1 (2003) 13.3.2.23.1 a sprinkler system is required
for
high-piled storage of combustibles over 2500 sq. ft., and A13.3.2.23
states
that for this purpose combustibles include non-combustibles packaged in
combustible materials.
According to NFPA 13 (2002) Table A.5.6.3 glass jars filled with
non-combustible liquids is a Class I commodity. 5.6.3.1, states that
Class I
shall be defined as non-combustible.
Question I have is: What would salsa in glass jars packaged in cardboard
boxes (cases) stored over 12 ft. in racks be classified as?
It appears to me that NFPA 1 says to sprinkle the building, and then
NFPA 13
says its noncombustible storage for the purpose of determining rack
storage
protection. Is this a fair statement?
David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum