Charles,
Inserted is a copy of the earlier/similar question and some of the
responses:
<paste:> "...Here in San Diego County, over the course of the past 15-20
years, I have personally been involved with, or heard of literally
dozens (can't even guess at the number, really) of UG failures from
C-900 and AC piping that were run under footings and which  failed (some
spectacularly) due to compression from settlement of the building.     

I think that the intent of 10.6 (NFPA 13, 2002 ed.) is that pipe and
fittings should be of a type and design and arrangement that mitigates
the potential damage from running under footings where it's absolutely.
Taken literally, one could say that a tunnel under the footing might be
required.    Now, I'm admittedly speaking from a warm-weather
perspective, where we run UG mains on a 4'-0" trench bed.      If you're
in a freeze zone and running an 8'-0" trench, a good soils engineer
would likely tell you that the pipe under the footing will never be
influenced by building settlement.    I would still require D.I. on the
spigot piece, in any case.

Steve Leyton
Protection Design & Consulting

 -----Original Message-----
From: Bob Knight [mailto:[EMAIL PROTECTED]
Sent: Friday, May 05, 2006 8:44 AM
To: [email protected]
Subject: RE: Underground stub-in requirements


Gregg,
We have had this happen several times over the last few years.  In every
case the C-900 has been removed and replaced with DI or In-Builds. One
of the reasons lies with NFPA 13-10.1.4 which states that the pipe needs
to be "fire resistive".  C-900 is not listed for exposed aboveground
applications.  This could cause a potential catastrophic failure at the
point of connection to the overhead piping in a fire situation.  Also,
look at the Annex on A.10.1.  It sates here that piping that is exposed
should be considered aboveground.

Bob Knight 

..." <end of paste>

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Haugen,
Charles
Sent: Wednesday, March 07, 2007 8:28 AM
To: [email protected];
[EMAIL PROTECTED]
Subject: Underground Material...

Sorry if this gets posted 2x...
 
CAN the underground stub-in (Vertical) be of PVC material?  (Blue Brute
eq'.)  If so, what precautions are necessary?  A MN job in question...
 
Chuck Haugen
Go Twins!!  Red Sox are overrated!  :)
 
Sincerely,
Charles L. Haugen, Jr.
Fire Sprinkler CAD Designer
SIMPLEXGRINNELL LP - FARGO #357
DIRECT:      701-639-1406
FAX:           701-280-2955
TELE:          800-342-4668
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to