I'm not Joe but I've seen entire lines rotate around grooved couplings.

On 3/9/07, Roland Huggins <[EMAIL PROTECTED]> wrote:
more worried about it NOT staying in its intended orientation.

Joe - Did you guys see any systems where sprigs and rotated?

Roland

On Mar 8, 2007, at 7:01 PM, Joe Hankins wrote:

> There was nothing to suggest water hammer. Water hammer resulting
> from a pump start is unlikely in sprinkler system piping. Even if
> there is a water hammer problem, it's something you want to know
> because it's easy to fiz.When you do see water hammer from a fire
> pump, it usually happens in underground.
>
> Also, starting fire pumps with the discharge valve open is by far
> the most common way weekly runs are made.  I've seen many sprinkler
> systems that have held up to weekly pump starts for more than 30
> years without incident.
>
> If you truly beleive that a sprinkler system can be blown apart by
> a fire pump, you have a very low opinion of  the quality of
> sprinkler installations!
>