All sprinkler systems should be able to with stand a 200 PSI hydro test at
any time the owner's or AHJ's might request it during the life span of that
sprinkler system. I don't think anyone would argue this point.

The point I was trying to make in my earlier response was that the
contractor performing this added work on the existing system (no matter how
old the sprinkler system is) better have details worked out with the owner,
owner's insurance company and his own insurance company as to who is going
to pay for possible damage incurred during this additional testing and if
his own (sprinkler contractor) insurance company will allow him to accept
this liability.

Paper work, Paper work, Paper work!!!

G. Tim Stone
 
G. Tim Stone Consulting, LLC 
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
 
216 Huntington Acres - Richmond, VT. 05477
TEL: (802) 434-2968          Fax: (802) 434-4343
                [EMAIL PROTECTED]
 
> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Greg McGahan
> Sent: Thursday, March 08, 2007 6:35 PM
> To: [email protected]
> Subject: RE: What I'm Hearing About Hydrostatic Testing
> 
> I agree with Garth with everything except we ALL have one huge
> unknown....who has worked on the system since it was new and the system
> was
> put in service? Has anyone changed a leaking head, relocated a head or etc
> and it was tested then? We have seen sprinklers in service that were slow
> dripping and literally had one thread inside the fitting with 125 psi
> static
> pressure on the system. Would it have held 200 psi? maybe maybe not.
> 
> So my angle is always that you are asking us to test not only the
> integrity
> of the existing system and our work, but the work of everyone in between.
> 
> Greg
> Living Water Fire Protection, LLC
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> Fax: 850-937-1852
> 
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
> Sent: Thursday, March 08, 2007 5:19 PM
> To: [email protected]
> Subject: RE: What I'm Hearing About Hydrostatic Testing
> 
> The Fitter makes good sense.
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
> Warren
> Sent: Thursday, March 08, 2007 5:39 PM
> To: [email protected]
> Subject: Re: What I'm Hearing About Hydrostatic Testing
> 
> The owner may not care but the firefighters that were expecting the water
> at
> the fire area would sure be disappointed.  If we are actually scared our
> systems are going to blow-up during pressurization, like will normally
> happen during firefighter response, then we are offering a false sense of
> security by installing our systems.  I am not saying the official's
> requirement is good or bad, but I think scare tactics are a bad idea.
> Repeatedly stating we believe our system piping and fittings will explode
> during simple pressurization of a system could really come back to bite us
> all in the butt.
> Say it was not part of the bid, say you want a disclaimer of liability as
> part of your proposal for this "extra" work, but making nuances that a 20
> year old system is somehow dangerous when pressurized should not be part
> of
> this process.
> 
> Garth
> a fitter
> ----- Original Message -----
> From: <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Thursday, March 08, 2007 2:22 PM
> Subject: RE: What I'm Hearing About Hydrostatic Testing
> 
> 
> That would depend on your point of view.  As an owner he may not care if
> the cap blows off while the FD is pumping it up during a fire as mush as
> he would if there was no emergency and someone just wanted a test
> because they wanted to see what happens to the system.
> 
> 
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [EMAIL PROTECTED]
> http://www.lg.com
> 
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Brooks,
> Bill
> Sent: Thursday, March 08, 2007 2:19 PM
> To: '[email protected]'
> Subject: What I'm Hearing About Hydrostatic Testing
> 
> I'm concerned about the undertone of the discussions.  That is,
> hydrostatic testing of existing systems will lead to unpredictable
> results (things leaking and coming apart).
> 
> If this is the case, then we may have many very fragile systems out
> there that shouldn't be in service in the first place.
> 
> Perhaps it's time to add a hydrostatic testing requirement to NFPA 25.
> Isn't it better to find out the 6" cap comes off during the hydrostatic
> test than to find out when the fire department pumps in during a fire?
> 
> Bill Brooks
> Pittsburgh, PA
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] Behalf Of mail
> Sent: Thursday, March 08, 2007 2:09 PM
> To: [email protected]
> Subject: RE: Hydrostatic testing recalled sprinkler heads
> 
> 
> Because this building is a US Air Force building, I don't think it will
> go to a code appeals process, but I can always ask.
> 
> We make a quote to change the heads and they issued a purchase order for
> the heads and labor.  There is no contract language that I can rely on
> in this case.  Their purchase order did not state a hydro test at 200
> psi was a requirement.
> 
> Martin Campbell
> List Member
> 
> 
> At 11:54 AM 3/8/2007, you wrote:
> >We call these folks "inventors" and they generally give us AHJ-types a
> >bad reputation. I struggle to get folks to comply with the minimum
> >standards, let alone invent new requirements!
> >
> >I think the technical code issues have been well addressed. My only
> >recommendation to add - avoid turning this into a people problem (or
> >one of those biological function contests). You have a code problem you
> 
> >need to resolve. You should have some recourse through a code appeals
> >process or, inevitably, a court appearance. Agree to disagree with the
> >AHJ and send it into the legal system.
> >
> >Jim Kettler
> >Fire Marshal
> >Buckingham, PA
> >
> >
> >
> >
> > > > They cannot ask for whatever they want.  We have to get the
> > > thought
> > > > they can
> > > > ask for whatever they want out of the industry.  They can only ask
> 
> > > > for what the law says they can ask for.
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to