This is the water meter we use here a lot.
http://www.badgermeter.com/pdf/recdisk/tech/rd-t-34.pdf

http://www.vikinggroupinc.com/databook/sprinklers/residential/103105.pdf
is an example of a concealed head that could work with up to 16x16 spacing
(flat ceilings only though - if on sloped clgs, the press. requirement goes
way up) There are others that will work, but this is an example. Generally,
it is tough to go more than 16x16 spacing with a 3/4" meter, unless the run
of copper between the tap and meter is very short, the water pressure is
very high. (Don't forget the loss through the pipe between the tap and meter
must be included in the calcs)
Many have requested for only 1" meters to be installed now, which is a lot
more expensive.
Kathryn


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of PCE
Sent: Friday, March 09, 2007 8:48 AM
To: [email protected]
Subject: Re: Pandora's Box

Chris,

They would have the same effect that any valve or fitting would have on the
ability of a sprinkler system to function properly.  The loss in pressure
due to friction at various flows through the meters is required to be
accounted for in the hydraulic calculations.  Interestingly enough, NFPA-13D
tells us that the actual chart loss from the meter manufacturer should be
reviewed during the calculation process.  If the chart loss is lower than
those figures in the table in 13D it may be used, however the standard also
says that if the chart loss from the manufacturer is greater than those
shown in the table that the higher value MUST be used.

Out here we see hundreds of residential sprinklers systems every month, and
for the most part they utilize 1" meters.  With a 13 gpm demand per
sprinkler, and a 5 gpm allowance for domestic use, the system flow of 31 gpm
exceeds the values shown in 13D as acceptable for a 5/8", and is right on
the line at the maximum allowed for a 3/4". 

There has been much shouting regarding the issue of meter size out here, and
most of it accompanied by vague suggestions of dire consequences and
thousands of dollars needlessly wasted if one position or another isn't
followed.

What is your take on the issues involved?

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Chris Brown wrote:
> Question to the forum:
> What effect does a 5/8 inch or 3/4 inch water meter have on fire sprinkler
system installed in an NFPA 13D or NFPA 13R system. The issue is one of the
maximum continuous flow thru the meter and its effect on the ability of the
fire sprinkler system to operate as intended. I respectfully request, Please
research and answer after you have visited with the water meter
manufacturer's and or water departments as I have already done. Keep in mind
that a single residential sprinkler has a minimum of some where between 19
and 25 gpm requirements and that most dwellings have two sprinklers flowing
in the hydraulically remote area.
>  
> This will be fun for a Friday:)
>
> Thank you,
>
> Chris Brown
> Fire Protection Designer
> Please note our new company name, e-mail address and web site.
>
>  
>
> innovative leader    $B"%(J     trusted partner
>
> 19910 West 161st Street
> Olathe, KS  66062
> Office:  913.829.8650
>
> Direct:
> Cell: 
> Fax:
>
> 913.747.2056
> 913.208.3600
> 913.829.8690
>
> www.poolefire.com <http://www.poolefire.com/> Office Map 
> <http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&c
> ity=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb%3e19910%2
> 0W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,%20%20
> US&cid=lfmaplink2&name=>
>
> This e-mail, and any files transmitted with it, are confidential and
intended solely for the use of the individual or entity to which they are
addressed.  If you have received this e-mail in error, please notify
[EMAIL PROTECTED]
>
>  
>
>   
> ----------------------------------------------------------------------
> --
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>   
> ----------------------------------------------------------------------
> --
>
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 
> 3/8/2007 10:58 AM
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to