Cutsheets on all listed devices should be submitted BUT the wording in 13 is a tad obscure - Specially Listed Equipment must be submitted. Now that's clear as mud.

Back in my days reviewing items, EVERYTHING was submitted. What is the norm today?

I beat this would be a good item to be included in some type of seminar on common mistakes in submittals.

Roland

On Mar 9, 2007, at 11:01 AM, PCE wrote:

Chris,

Badger makes a meter, model M40, which is 3/4 x 3/4, and their chart shows that it can accept flows of up to 35 gpm. And, at that flow, it has a pressure loss of around 6.5 to 7.0 psi. I would think that would certainly be sufficient to not impact the design of a residential system at the same level as the chart losses shown in NFPA-13D. Out here, the AHJ's are starting to require the designers [sue me if you don't like that word] to submit the data on the meter along with the calculations and plans.

Just one more item to check prior to submittal.

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Chris Brown wrote:
Thank you for the information and now we have another manufacturer a
meter of with the same results as described in my last email, a 5/8 inch or 3/4 inch will not meet the flow requirements of a lot of the NFPA 13D
and NFPA 13R systems. IF as the AHJ, designer or installer of such
systems you should be thinking pretty hard right now.

Thank you,

Chris Brown
Fire Protection Designer, Poole Fire Protection
Office: 913.829.8650 Direct: 913.747.2056 Cell: 913.208.3600 Fax:
913.829.8690


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kathryn
Tyler
Sent: Friday, March 09, 2007 11:40 AM
To: [email protected]
Subject: RE: Pandora's Box

This is the water meter we use here a lot.
http://www.badgermeter.com/pdf/recdisk/tech/rd-t-34.pdf

http://www.vikinggroupinc.com/databook/sprinklers/residential/ 103105.pdf
is an example of a concealed head that could work with up to 16x16
spacing (flat ceilings only though - if on sloped clgs, the press.
requirement goes way up) There are others that will work, but this is an
example. Generally, it is tough to go more than 16x16 spacing with a
3/4" meter, unless the run of copper between the tap and meter is very short, the water pressure is very high. (Don't forget the loss through the pipe between the tap and meter must be included in the calcs) Many
have requested for only 1" meters to be installed now, which is a lot
more expensive.
Kathryn


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of PCE
Sent: Friday, March 09, 2007 8:48 AM
To: [email protected]
Subject: Re: Pandora's Box

Chris,

They would have the same effect that any valve or fitting would have on
the ability of a sprinkler system to function properly.  The loss in
pressure due to friction at various flows through the meters is required
to be accounted for in the hydraulic calculations.  Interestingly
enough, NFPA-13D tells us that the actual chart loss from the meter
manufacturer should be reviewed during the calculation process. If the
chart loss is lower than those figures in the table in 13D it may be
used, however the standard also says that if the chart loss from the
manufacturer is greater than those shown in the table that the higher
value MUST be used.

Out here we see hundreds of residential sprinklers systems every month, and for the most part they utilize 1" meters. With a 13 gpm demand per sprinkler, and a 5 gpm allowance for domestic use, the system flow of 31
gpm exceeds the values shown in 13D as acceptable for a 5/8", and is
right on the line at the maximum allowed for a 3/4".
There has been much shouting regarding the issue of meter size out here, and most of it accompanied by vague suggestions of dire consequences and thousands of dollars needlessly wasted if one position or another isn't
followed.

What is your take on the issues involved?

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Chris Brown wrote:

Question to the forum:
What effect does a 5/8 inch or 3/4 inch water meter have on fire sprinkler

system installed in an NFPA 13D or NFPA 13R system. The issue is one of the maximum continuous flow thru the meter and its effect on the ability
of the fire sprinkler system to operate as intended. I respectfully
request, Please research and answer after you have visited with the
water meter manufacturer's and or water departments as I have already
done. Keep in mind that a single residential sprinkler has a minimum of
some where between 19 and 25 gpm requirements and that most dwellings
have two sprinklers flowing in the hydraulically remote area.

 This will be fun for a Friday:)

Thank you,

Chris Brown
Fire Protection Designer
Please note our new company name, e-mail address and web site.


innovative leader    $B"%(J     trusted partner

19910 West 161st Street
Olathe, KS  66062
Office:  913.829.8650

Direct:
Cell: Fax:

913.747.2056
913.208.3600
913.829.8690

www.poolefire.com <http://www.poolefire.com/> Office Map <http:// www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&c ity=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb% 3e19910%2 0W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,% 20%20
US&cid=lfmaplink2&name=>

This e-mail, and any files transmitted with it, are confidential and

intended solely for the use of the individual or entity to which they
are addressed. If you have received this e-mail in error, please notify
[EMAIL PROTECTED]


-------------------------------------------------------------------- --
--

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------------------------------------------------------------- --
--

No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007 10:58 AM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________