Yes -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman Sent: Tuesday, March 13, 2007 5:18 PM To: [email protected] Subject: Re: Small Room Rule
Seems like everyone is forgetting the square footage limitation. 225 sqft max = 9-0 off one wall, 6-0 off one wall and 7-6 off two walls or any configuration that does not exceed 9-0 off one wall, 7-6 off the other three walls AND 225 sqft. On 3/13/07, Brian Harris <[EMAIL PROTECTED]> wrote: > That's the way I was taught, but if you look at A.8.6.3.2.4 (b,c,d) it > looks like you can only be 6'-0" off the wall if your 9'-0" in the same direction. > > Regards, > Brian Harris > First Defense Fire Protection > Design Engineer > [EMAIL PROTECTED] > 704.948.3506 phone > 704.948.3507 fax > > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Bill > Minkel > Sent: Tuesday, March 13, 2007 4:53 PM > To: [email protected] > Subject: RE: Small Room Rule > > You can be 9' off any ONE wall and 7'-6 max. off any other 3 > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Brian > Harris > Sent: Tuesday, March 13, 2007 4:38 PM > To: [email protected] > Subject: RE: Small Room Rule > > Ed, > Thanks, obviously there can be any combination of sizes that equal up > to 800 sq.ft. so those dim's can vary accordingly. One other question, > why when there's only one head can you be up to 9' off one wall and > still be 7'6 off the other (16'6" direction) but when there's 2 or > more heads the max you can be is 9'-0" & 6'-0"? > > > Brian Harris > First Defense Fire Protection > Design Engineer > [EMAIL PROTECTED] > 704.948.3506 phone > 704.948.3507 fax > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of > Tambini, Ed > Sent: Tuesday, March 13, 2007 4:17 PM > To: [email protected] > Subject: RE: Small Room Rule > > 30' x 26'-8 = 800 sq ft max size for small room It's what's left over > from the 2 7'-6 dims > > Ed > Aero > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Brian > Harris > Sent: Tuesday, March 13, 2007 12:42 PM > To: [email protected] > Subject: Small Room Rule > > Figure A.8.6.3.2.4.(d) shows an example of the small room rule with > (4) heads, where exactly does the 11'-8" between rows come from? > > > > Regards, > > Brian Harris > First Defense Fire Protection > Design Engineer > > <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED] > 704.948.3506 phone > 704.948.3507 fax > > > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum