Honestly, my first inclination would be to just walk away.  The
aggravation that will follow will not make the project worth fooling
with.  If the owner is bent on deception, I wouldn't have enough
confidence and trust that he'd even pay me without a hassle.

But if you do decide to do the job, I would have the basis for the
design plastered in multiple places on my drawings.  I would clearly
spell it out that this design is based on racked storage not to exceed
X'-X" and is based on ABC commodity stored in cartons, boxes on pallets,
etc......  That way if in the future he decides to do something
different it is clearly stated on the sprinkler shop drawings what the
sprinkler system was intended to protect.  I'd also fill out the riser
plaque the same way.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Tuesday, March 20, 2007 12:03 PM
To: [email protected]
Subject: owners information certificate

Part A:

 

What do we (as an industry) do when an owner completes the Owner's
Information Certificate incorrectly to deliberately mislead an AHJ? 

 

Part B:

 

What do we do when they technically tell the truth as in building a
warehouse that has no storage above 12' initially but they have every
intention (because they tell you so) to store PODS 24' high after they
get a CO?

 

BTW, the reason I have been unsuccessful in convincing the owner of the
proper level of protection is because there have 2 of these buildings
built within 200 miles in the last few months and both of them had
minimal systems. The installing contractor on one of the jobs told me
that they were told the building was a spec warehouse and to protect it
as an empty building and after they were done the owner would lease it
to the PODS franchisee. His comment was "I don't know if that protects
me or not"

 

Legally?

 

Morally I feel bound to walk away from this project but that just means
that they will find someone else to do the job incorrectly and although
there is no liability involved, there is still the knowledge that the
building (Ord.
Group II) will be grossly under protected.

 

I know the argument that we are not police of the industry nor can we
2nd guess what the potential future occupancy of a building is or may be
one day, but this is different and one of the 2 scenarios listed above
is going to happen on this project.

 

Thanks for your input,

Greg

 

Living Water Fire Protection, LLC

1160 McKenzie Road

Cantonment, FL 32533

850-937-1850

Fax: 850-937-1852

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to