I was deep into this a while back and and Bill Brooks gave a great response that has held true in all of our dealings. Here was the main points of Bills post: The basic simple way to determine neccesity is as follows:
1. Step 1- Architect identifies building classification. 2. Step 2- Structural engineer identifies seismic design category 3. Step 3- If both parties above do their jobs correctly, bracing is not necessary for Seismic design categories A or B The sprinker designer should never attempt to perform Steps 1 or 2. You might also note the reference to storage racks. You don't want to get into a situation where you are bracing your rack sprinkler system using non- braced racks as your support points. Now the longer explanation: The difficulty with determining when bracing is required is compoiunded by the fact that the information comes from two documents. (IBC 03 and ASCE 7-02) and that there are multiple factors, use groups, etc, that must be defined. The need for bracing cannot be determined solely by the sprinkler designer. The project architect and structural engineer MUST play a role. In some cases you could have a MEP engineering firm create a spec that is in conflict with the architect's and structural engineer's determinations. These are the steps required to determine if seismic bracing is neccesary for a sprinkler system: 1. Determine building classification (I, II, III, or IV) to identify its seismic Importance factor. To do this refer to IBC 2003, Table 1604.5 The values are between 1.00 and 1.50 The sprinkler designer can guess at this one , but the project architect would be the responsible individual to make the building classification determination. 2. Look at Table 1604.5 footnote a to determine the seismic use group. Once the building classification is identified, the project arch. Would pass this information on to the structural engineer. The structural eng. uses the seismic use group in conjunction with step 3 below. 3. Determine seisic design category based on ground motion using tables 1616.3(1) and 1616.3(2). Note ground motion factors on left and seismic use group on top. The structural engineer must evaluate the ground motion values and determine the seismic design category. 4. Determine need for seismic bracing using ASCE 7-02, 9.6.1.5 Quoting: "Component Importance factor. The component importance factor shall be slected as follows: Ip = 1.5 life safety component required to function after an earthquake (e.g. fire sprinker system) Ip = 1.5 component that contains hazardous component Ip = 1.5 storage racks in structures open to the public ( e.g. warehouse, retail stores) Ip = 1.0 all other components In addition, for structures in Seismic Use Group III: Ip = 1.5 all components needed for continued operation of the facility or whose failure could impair the continued operation of the facility" Once the component importance factor is identified, the 6 exceptions to 9.6.1 can be reviewed to determine the need for seismic bracing. Only exceptions 1, 2 and 4 are applicable to fire sprinkler systems. "Exception: The following componenets are exempt from the requirements of this section:" 1. All components in seismic design category A 3. Mechanical and electrical components in seismic design category B 4. Mechanical and electrical components in structures assigned to seismic design category c provided the (component)importance factor is equal to 1.0. Here is where the answer comes in. During the design process the architect determines the building classification and passes this informatin on to the structural engineer. The structrural engineer determines ground motion factors and identifies the seismic design category. Then, the sprinkler contractor uses ASCE 7-02, 9.6.1 to determine the need for bracing. As you can see, the answer is going to be yes for design categories C, D, E and F because the sprinkler system component importance factor is 1.5. The answer will be no for design categories A and B. We have found this EXTREMELY usefull and I am glad to pass it on to whoever it may help. Rod DiBona Rapid Fire Protection -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Charles Thurston Sent: Thursday, March 22, 2007 1:07 PM To: Cliff Whitfield Subject: Re[2]: Seismic and building codes Hello Cliff, I hope they figure it out before next week as that is where I'll be all week Intermediate design school..... Wish me luck Thursday, March 22, 2007, 11:37:22 AM, you wrote: > Roland, > We were taught in the intermediate design school (2005) that Category > A & B were exempt like Brian mentioned in an earlier post. Were we > taught incorrectly or has something changed since them? > Cliff > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Roland > Huggins > Sent: Thursday, March 22, 2007 11:30 AM > To: [email protected] > Subject: Re: Seismic and building codes > I don't think the CA boys know the answer since they always have to > provide seismic protection. > You have to protect ALL structures until proven otherwise is the > starting point. Go to IBC 1614.1 for that statement AND the > exceptions when protection is not required. We did a couple of > articles in Sprinkler Age about this matter. Significant break points > are Design Category A and a low spectral response (Ss of 0.15g or Sl > of 0.04g) > Roland > On Mar 22, 2007, at 8:53 AM, Thom McMahon wrote: >> Probably you CA guys can answer this off the tops of your heads, but >> I'll take help from anywhere. >> >> Using the IBC 2003, chapters 16 and 18, "When is seismic bracing >> required?" >> Here's the building info: >> >> Assembly building over 300 occupancy >> Type V construction (all wood) >> a. Seismic importance factor IE = 1.25 b. Seismic Use Group = 3 c. >> Mapped Spectral Response acceleration (i. ss = 0.259 ii. si = >> 0.066 >> d. Site Class = B >> e. Spectral Response Coefficients: (i. SDS = 0.18 ii. SDI = 0.04) f. >> Seismic Design Category = B g. Basic seismic Force Resisting System >> h. Response Modification Factor(s) R=3 i. Seismic Response >> Coefficient(s) Cs=0.0429 j. Analysis Procedure used: >> k. Seismic Base Shear: >> >> The above is all the info given by the Arch & Structural engineer. >> We've asked the building Dept. and they need to ask ICC. Our question >> to them and to you all is the same. >> >> "When do we need to provide seismic bracing on our fire sprinkler >> system? At what Site Class or Seismic Design Category, or >> combination, do we need to provide seismic protection? >> NFPA 13, 2007 9.3 "Where water based fire protection systems are >> required to be protected against damage from earthquakes, the >> requirements of 9.3 shall apply, unless the requirements of 9.3.1.2 >> are met." >> >> Lost in ICC Limbo! >> >> Thom McMahon >> Firetech, Inc. >> 2560 Copper Ridge Dr >> Steamboat Springs, CO 80488-2136 >> Tel: 970-879-7952 >> Fax: 970-879-7926 >> ----- Original Message ----- From: "Roland Huggins" >> <[EMAIL PROTECTED]> >> To: "SprinklerFORUM" <[email protected]> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum -- Best regards, Charles mailto:[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
