It gets uglier if you are in the 2003 edition of the IBC. It literal says you can NOT use NFPA 13 for seismic design. 2003 IBC excludes the section of ACSE 7 that allows the use of NFPA 13 and ASCE 7 requires you to proof the calculated force (can be done) and displacement (here's the rub) is greater with 13. I did an article in the NFPA Journal in this issue. See:

http://www.firesprinkler.org/techservices/articles/nfpa0501seismic.pdf

After the TIA on 2002, the latest ASCE 7 now embraces 13.


Roland

On Mar 22, 2007, at 1:34 PM, Brooks, Bill wrote:

This answer is based on the 2003 IBC, and I've posted it previously here. It looks like the answer is in your list where the Seismic Design Category is listed as B. The code text and the referenced ASCE 7 has been rearranged
somewhat in the 2006 IBC.

My previous response follows:


In case you don't want to read all the way down to the bottom, the "answer"
is:
1.  Step 1 - Architect identifies Building Classification
2.  Step 2 - Structural engineer identifies Seismic Design Category
3. Step 3 - If both parties above do their jobs correctly, bracing is not
necessary for Seismic Design Categories A and B.

The sprinkler designer should NEVER attempt to perform Steps 1 and 2.

You might also note the reference to storage racks. You don't want to get into a situation where you are bracing your rack sprinkler system using
non-braced racks as your support points.

Now the longer explanation:

The difficulty with determining when bracing is required is compounded by the fact that the information comes from two documents (IBC 2003 and ASCE 7-02) and that there are multiple factors, use groups, etc, that must be defined. The need for bracing cannot be determined solely by the sprinkler designer. The project architect and structural engineer must play a role. In some cases you could have an MEP engineering firm create a spec that is in conflict with the architect's and structural engineer's determinations.

These are the steps required to determine if seismic bracing is necessary
for a sprinkler system:

1. Determine Building Classification (I, II, III, or IV) to identify its Seismic Importance Factor. To do this refer to IBC 2003, Table 1604.5. The
values are between 1.00 and 1.50.

THE SPRINKLER DESIGNER CAN MAKE A GUESS AT THIS ONE, BUT THE PROJECT
ARCHITECT WOULD BE THE RESPONSIBLE INDIVIDUAL TO MAKE THE BUILDING
CLASSIFICATION DETERMINATION

2. Look at Table 1604.5 footnote a to determine the Seismic Use Group.

ONCE THE BUILDING CLASSIFICATION IS IDENTIFIED, THE PROJECT ARCHITECT WOULD
PASS THIS INFORMATION ON TO THE STRUCTURAL ENGINEER.  THE STRUCTURAL
ENGINEER USES THE SEISMIC USE GROUP IN CONJUNCTION WITH STEP 3 BELOW.

3. Determine Seismic Design Category based on ground motion using Tables 1616.3(1) and 1616.3(2). Note ground motion factors on left and Seismic Use
Group on top.

THE STRUCTURAL ENGINEER MUST EVALUATE THE GROUND MOTION VALUES AND DETERMINE
THE SEISMIC DESIGN CATEGORY

4. Determine need for seismic bracing using ASCE 7-02. 9.6.1 establishes the need for bracing of Architectural, Mechanical, and Electrical Components and Systems. There are 6 exceptions to this paragraph, and these exceptions are related to the Seismic Design Category determined above. In order to come up with the "answer" one other piece of information is needed. This is
the Component Importance Factor from ASCE 7-02, 9.6.1.5.  Quoting:

"9.6.1.5 Component Importance Factor. The component importance factor (Ip)
shall be selected as follows:
Ip = 1.5 life safety component required to function after an earthquake
(e.g. fire protection sprinkler system)
Ip = 1.5 component that contains hazardous content
Ip = 1.5 storage racks in structures open to the public (e.g., warehouse
retails stores)
Ip = 1.0 all other components

In addition, for structures in Seismic Use Group III:

Ip = 1.5 all components needed for continued operation of the facility or
whose failure could impair the continued operation of the facility"

Once the Component Importance Factor is identified, the 6 exceptions to
9.6.1 can be reviewed to determine the need for seismic bracing.  Only
exceptions 1, 2, and 4 are applicable to the sprinkler system:

"Exception: The following components are exempt from the requirements of
this Section:
1.  All components in Seismic Design Category A
3.  Mechanical and electrical components in Seismic Design Category B.
4. Mechanical and electrical components in structures assigned to Seismic Design Category C provided the (component) importance factor Ip is equal to
1.0."

HERE IS WHERE THE ANSWER COMES IN. DURING THE DESIGN PROCESS THE ARCHITECT DETERMINES THE BUILDING CLASSIFICATION AND PASSES THIS INFORMATION ON TO THE
STRUCTURAL ENGINEER.  THE STRUCTURAL ENGINEER DETERMINES GROUND MOTION
FACTORS AND IDENTIFIES THE SEISMIC DESIGN CATEGORY. THEN, THE SPRINKLER CONTRACTOR USES ASCE 7-02, 9.6.1 TO DETERMINE THE NEED FOR BRACING. AS YOU CAN SEE, THE ANSWER IS GOING TO BE YES FOR DESIGN CATEGORIES C, D, E, AND F BECAUSE THE SPRINKLER SYSTEM COMPONENT IMPORTANCE FACTOR IS 1.5. THE ANSWER
WILL BE NO FOR DESIGN CATEGORIES A AND B.

Bill Brooks
412-365-3712
412-365-3350 FAX
412-400-6528 Cell

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Thom
McMahon
Sent: Thursday, March 22, 2007 11:53 AM
To: [email protected]
Subject: Re:Seismic and building codes


Probably you CA guys can answer this off the tops of your heads, but I'll
take help from anywhere.

Using the IBC 2003, chapters 16 and 18, "When is seismic bracing required?"
Here's the building info:

Assembly building over 300 occupancy
Type V construction (all wood)
a. Seismic importance factor IE = 1.25
b. Seismic Use Group = 3
c. Mapped Spectral Response acceleration (i. ss = 0.259 ii. si = 0.066
d. Site Class = B
e. Spectral Response Coefficients: (i. SDS = 0.18  ii. SDI = 0.04)
f. Seismic Design Category = B
g. Basic seismic Force Resisting System
h. Response Modification Factor(s) R=3
i. Seismic Response Coefficient(s) Cs=0.0429
j. Analysis Procedure used:
k. Seismic Base Shear:

The above is all the info given by the Arch & Structural engineer.
We've asked the building Dept. and they need to ask ICC. Our question to
them and to you all is the same.

"When do we need to provide seismic bracing on our fire sprinkler system? At

what Site Class or Seismic Design Category, or combination, do we need to
provide seismic protection?
NFPA 13, 2007 9.3 "Where water based fire protection systems are required to

be protected against damage from earthquakes, the requirements of 9.3 shall
apply, unless the requirements of 9.3.1.2 are met."

Lost in ICC Limbo!

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Roland Huggins" <[EMAIL PROTECTED]>
To: "SprinklerFORUM" <[email protected]>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to